Foreign fitting (to me)
GM_73
Member Posts: 1
Hello all,
Attached is a photo of a fitting on a 2 pipe steam radiator. Most of the radiators in the house have the familiar (to me) return circular traps. Others have this "foreigner". Any help greatly appreciated.
Thank you
0
Comments
-
vapor system ball trap. Picture and description in lost art. See if I can find the picture.
0 -
They work splendidly and are simple.
Provided you keep your pressure down. Not more than 8 OUNCES (half a pound) per square inch shutoff. You'll need a vapourstat to make this system run right.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England3 -
This is an O-E Vapor system but someone replaced these original return fittings with standard traps.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0