High water feeder numbers no leaks that we can detect

hjw09
hjw09 Member Posts: 13
edited January 6 in Strictly Steam

We have a one pipe steam heat system w/ an oil fired boiler. On December 16 when arriving home we noticed what appeared to be steam or smoke coming out of our chimney which prompted us to check the boiler to make sure there was nothing weird going on. I noticed the water feeder number looked high so I took a picture of it. We kind of forgot about it and fast-forward to today we noticed the same steam/smoke coming out of the chimney so I we went downstairs to check the boiler the number on the water feeder is even higher. There are no leaks that we can detect we checked every pipe/valve/radiator & all around the boiler. our steam heat seems to be running fine. We do not hear any weird noises or notice anything unusual.

Water feeder was 153 on 12/16 and is now 243 on 1/6

What could the problem be?

What could be the issue?

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 25,624

    A leak in the boiler above the water line.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Long Beach EdethicalpaulSTEAM DOCTOR
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,637

    As Jamie suggests,a leak high in the boiler is allowing steam to escape up the chimney.

    ethicalpaul
  • jesmed1
    jesmed1 Member Posts: 1,042

    You may be in the same boat as this boiler owner:

    https://forum.heatinghelp.com/discussion/199558/how-to-avoid-this-again-rust-hole-above-water-line-burnham-in4/p2

  • skimmer
    skimmer Member Posts: 173

    how old is it??

  • hjw09
    hjw09 Member Posts: 13

    It is from 2004 and I finally got someone to come out and look at it. It’s cracked inside so that explains it !