Hey all,
I have been trying to tweak my steam system to get it running properly. I had adjusted the radiator vents and am now getting relatively even heat throughout the house however from the start of the boiler it is taking close to 25-30 mins before the radiators start to warm up. Is this a proble with the main vents? I have attached several images here. These are short runs coming up from the boiler. I have seen gorton 1 and 2's but am unsure what is needed. Any help would be greatly appreciated. Thanks.
Comments
-
They have venting capacity charts you can download for free. You can size your main vents according to length and size of pipe. Installing a Gorton #2 on each main would significantly improve system performance. Install the main vents on a 6 inch nipple or longer
ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
What you need is main vents at the ends or at least very near the ends of the steam mains.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
The pictured location is good. You said it's a short run, try a Maid o Mist #1 or Gorton #1 in each position
https://www.supplyhouse.com/Jacobus-Maid-O-Mist-J1-1-3-4-x-1-2-Main-Vent-Valve-3563000-p
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Thank you for the quick replies!
0 -
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements