boiler cycling for hot water loop - bad?

skimmer
skimmer Member Posts: 169

We all know short cycling is bad for steam boilers.

What about cycling for a basement hot water loop?

It seems on my steam boiler, it cycles off and on to 180 much more frequently and with shorter run times when calling for heat only on the hot water zone.

I can hear it off and on many many times in an hour before the basement tstat is satisified.

Does this shorten the life of the boiler? Contribute to holes above the water line?

Comments

  • LRCCBJ
    LRCCBJ Member Posts: 682

    The hot water zone is tiny. The boiler is huge.

    To limit the cycling you need an aquastat with an adjustable differential. If you allow the boiler to drop 30°F before it restarts, you'll cut the cycling by 2/3.

    Long Beach Ed
  • skimmer
    skimmer Member Posts: 169

    Would that affect the heating?

  • LRCCBJ
    LRCCBJ Member Posts: 682

    Presuming it IS a steam boiler, it would NOT affect the heating. The boiler operates for CH via, typically, the thermostat, which will allow the boiler to actually BOIL. The aquastat does not.

  • skimmer
    skimmer Member Posts: 169

    yes its steam with a hot water loop. honeywell aquastat with bulb inserted into boiler (not strap on) set to 180. any recommendations for the adjustable.. its wired into the 24 volt

  • LRCCBJ
    LRCCBJ Member Posts: 682

    This is a typical adjustable.

    https://www.supplyhouse.com/Resideo-L4006A2007-High-or-Low-Limit-Aquastat-100-240-DegreeF-range-5-30-DegreeF-Adj-Differential-L4006A2007

    The only question is whether the bulb will fit in the piping that you have. Cannot be sure without removing the existing aquastat. You can usually return it if it won't fit and you repackage it carefully as new.

  • LRCCBJ
    LRCCBJ Member Posts: 682

    You really should look carefully at the existing aquastat or get a model number. It might already have an adjustable differential!

    Long Beach Ed
  • skimmer
    skimmer Member Posts: 169

    I will!!! I looked at the one at supply house, where would the differential be? I dont see it? is it a setting on the inside?

  • Jamie Hall
    Jamie Hall Member Posts: 25,262

    As has been said, this is a control issue. It is unlikely in the winter that the boiler will be too cold for the loop to work, but in any event there should be an aquastat to turn it on it it is too cold. Say at around 140 F or thereabouts. And that one — or another — should remove the demand for hot water at around 180 — but that one should not be wired to prevent the boiler from steaming in response to the thermostat.

    Pretty simple really.

    And, by the way, we don't all accept that short cycling is bad for steam boilers. It depends on just how short the "on' cycle is — and more particularly, how short the "off' cycle is. But that's another topic.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    ethicalpaul
  • bburd
    bburd Member Posts: 1,093

    I think in this case that the cure in the form of spending money on a new aquastat is worse than the disease in the form of additional cycling. Some things just are not worth worrying about. If I owned it I would look to increase the differential if the existing aquastat is adjustable; the adjustment would be inside the cover.


    Bburd
  • skimmer
    skimmer Member Posts: 169

    Well right now its set for 180. Its the only one.

    It only cycles a lot when the basement loop calls for heat and the rest of the house (steam) doesnt. Which is usually on warmer days.

    On colder days, when its running for steam upstairs, there is a main that runs thru the basement and helps keep it warm. And also since the boiler is running for steam, the water is generally hotter then 180 anyway if the basement should call for heat after the steaming cycle

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,848

    Take the cover off the aqustat and look in the middle at the bottom under the wiring terminals. If it has the adj. differential you will see a white wheel with #s on it.

    Or post the model # and we can look it up.

    It will be a L4006A or a similar #

  • LRCCBJ
    LRCCBJ Member Posts: 682

    Here you go…………..

    https://www.ebay.com/itm/305931833935?_skw=L4006A2007&itmmeta=01JG85WC9SR16QWNSYHWJYX2MA&hash=item473af5524f:g:WKkAAOSwoARnQ9et&itmprp=enc%3AAQAJAAAA8HoV3kP08IDx%2BKZ9MfhVJKl9iurg5w1GLaC0lGhk%2F4NeLym4BksKuItFQ5j9akn%2B0ZxG35Gnp5MFbG7LA%2B6FVug%2Fj5T1E3lcOquz0W3o%2BqMMpHQZEsX6I1XL0wXaRYa3F7bZ%2FYvlXHRACcQf6Q4YkE8AckWV--Pj0IC7haeF928Fx5OvnpAfuCIQ08h95uYi2u4nz1qMXnFFshR8lm7V3CNKjzjjJWxknTbIA7%2BOZrkXZISOtTz%2BYYpd1VFAyDRwg9W7UyjL%2B4JpawDOkItnYnIBpC6DtKbjOT0Nc%2BoxJQkY%2Bz7aAv%2BsXdwJk9ifY1uwHA%3D%3D%7Ctkp%3ABk9SR5jF8YWCZQ

  • skimmer
    skimmer Member Posts: 169

    I dont see a differential wheel. Only a temp setting wheel??

  • LRCCBJ
    LRCCBJ Member Posts: 682

    The differential wheel is inside the housing. Need to take off the cover. What's the model number of yours? Should be inside the cover.

  • skimmer
    skimmer Member Posts: 169

    Hard to get to at the moment.. Will check soon and post back.. thanks for the advice and help!

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,848

    Honeywell L4006A2007 at Supply House.com is what you need.

    Or similar model with adjustable differential.

    Since it is not used as a safety high limit I would try E-Bay. Might be less $$$$ that Supply House.

  • skimmer
    skimmer Member Posts: 169

    do you think it will make a difference? I don’t want to over think this.

  • skimmer
    skimmer Member Posts: 169

    low and behold it does have a setback. It was set to 5 on the dial.

    So I changed it to 30


    so at the moment. It’s 180 with a differential of 30. That should cut back on the frequent off and on cycling for the basement loop.

    It was getting excessive

    bburd
  • Jamie Hall
    Jamie Hall Member Posts: 25,262

    That would have done it…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • LRCCBJ
    LRCCBJ Member Posts: 682

    That's a home run. Nothing to purchase……………two minutes of labor👍️

  • skimmer
    skimmer Member Posts: 169

    yeah really im glad i didnt jump the gun and purchase one..

    i wonder how much this save on wear and tear and efficiency