New old radiator steam vent hissing

Giovanni722
Giovanni722 Member Posts: 12

hi again, I just had a new old radiator installed on my first floor and the steam vent (purchased from Home Depot for $15) is hissiny uncontrollably with no signs of stopping. Do you guys think it’s the vent? Do I just need to get a new better one? Is there something wrong with the radiator? Is there too much pressure? By the way this is a single pipe system! Thanks!

Comments

  • delcrossv
    delcrossv Member Posts: 1,437

    Yep. Do NOT buy vents from Home Depot.

    Go to supplyhouse.com.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    Giovanni722ethicalpaul
  • bburd
    bburd Member Posts: 1,057

    Home Depot does not sell decent steam air vents. However, there may be more going on. What pressure do you see on your boiler gauge while this is happening? Can you post a photo of the pressure gauge and the pressuretrol, which is the square gray box on the boiler wired into the other electrical parts there.


    Bburd
    Giovanni722
  • Giovanni722
    Giovanni722 Member Posts: 12

    I had a professional come over and do the required maintenance on my boiler and he said everything looked good. It’s a 1700 square foot house and none of my other radiators hiss like the way this one did tonight (again newly installed)

  • Giovanni722
    Giovanni722 Member Posts: 12
  • Jamie Hall
    Jamie Hall Member Posts: 24,983

    It's the vent. Get a good one… it'll cost more, but you get what you pay for.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Giovanni722bburddelcrossvethicalpaul
  • Giovanni722
    Giovanni722 Member Posts: 12

    thanks @Jamie Hall, yeah makes sense. I was in a pinch and at Home Depot so I just picked one of those up hoping for the best.

  • bburd
    bburd Member Posts: 1,057

    I agree regarding the vent quality, but that pressuretrol is set a little bit high. You want a maximum of 2 psi cutout, and 1.5 is better. Try adjusting the main scale down just below 2 psi. Don't adjust it so low that the mechanism comes apart. The differential is set correctly.


    Bburd
    Giovanni722
  • Giovanni722
    Giovanni722 Member Posts: 12

    I have 9 radiators in the house and 2 are slightly bigger (living room and dining room). What would lowering it to under 2 do for me? Sorry first time I’m using this kind of system and the guy that was just here said it was ok so a little weary about touching those controls. Thanks! @bburd

  • bburd
    bburd Member Posts: 1,057

    The general rule for low pressure steam heating systems is to keep them under 2 psig. Pressures above 3 psig can damage vents, increase noise and at higher levels cause all kinds of other problems.

    That said, if the current settings were working well until you changed that one vent, there is probably no need to change them.


    Bburd
    delcrossv
  • Giovanni722
    Giovanni722 Member Posts: 12

    now that you say that a few radiators do hiss, I may knock it down to 2psi, it’s as simple as lowering down that lever on the right? Right? Just trying to make sure the boiler running as efficient as possible while also keeping noise and clanging down! I appreciate the responses! @bburd

  • bburd
    bburd Member Posts: 1,057

    Yes, the lever on the right. I believe it's controlled by a screw on top.


    Bburd
  • Giovanni722
    Giovanni722 Member Posts: 12

    just changed the valve and pressuretrol, here goes nothing!

    PC7060