I don’t think my single pipe steam system has a main

I just noticed that my single pipe steam system doesn’t seem to have a main. It looks like it has one long run with T’s going to the first floor and second floor radiators.
The radiators themselves seems to be getting hot quickly enough. The end of the main radiator is the kitchen radiator and there seems to be a gorton vent on it. All the other radiators have the cheapo maid o mist.
Here is photo of the piping off the boiler.
Thoughts? Also noticed my boiler seems to run for 5 mins then turnoff for 1 minute before running again. I’m assuming it’s short cycling due to the vents being garbage at the radiators.
Comments
-
-
-
@melo , how long is the main, and what pipe size?
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
cheapo maid o mist
I think you meant to say: proudly made in the USA, design possibly copied by Gorton who tripled the price, happily passing air and stopping steam silently on thousands of radiators
But get real Maid O Mist for $12 from Supplyhouse.com , not the copycat ones at the big box stores
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el2 -
you’re the first person to put it that way to be honest. I respect your opinion as you guys have been doing it for a while and would love to save money.
Why does maid o mist have bad reputation where I live? (Big eastern city).
Also, any issues with using the Hoffman adjustable vents?
0 -
You used to be able to buy buy a maid o mist kit that had the air valve and 5 orifices so you could select what size of vent for just a little more than the cost of the vent itself, made it easy to balance radiators. Now you have to buy the orifice kit (5 sizes) and the vent separately, still very handy for initial balancing of the system.
I've had MOM's on my system for over a decade with no failures.
Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge1 -
trade pros get very opinionated about stuff 😅
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
-
Maid-o-Mist doesn't have a #2- have to buy Gorton for that size.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Mad O Mist vents based in Illinois and Gorton based in New Jersey, which may explain the geographical preference mentioned by poster, delcrossv ,above. That doesn't mean some company products aren't also made in China
Regards,
RTW
0 -
I don’t know what company you mean, but MoM boxes say “Made in USA”
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements