Fan not running on heat

Scd
Scd Member Posts: 2

Thought it was frozen pipe on the attic, it appears not. 1 shared water heater in the basement, 1st floor heating comes from air handler in the basement, 2nd floor heating comes from air handler in the attic. 2nd floor heating has been working until 3 days ago. 1st floor has noissue. 

2nd floor room temp is at 64. 

Set T'Stat to 70 in heating mode - fan doesn't work. Confirmed it calls for hot water - because pipe runs hot at both the furnace and air handler.

Set T'Stat to 70 in heating mode and Fan ON - fan doesn't turn on .  Touch red and green fan runs .

Set T'Stat to 60 in heating mode and Fan ON - fan kicks on.

Set T'Stat to 60 in cooling mode - fan kicks on.

Fan motor speed selector is at Tap 3. Changing to Tap 1 or Tap 2 doesn't make a difference. 

Replaced 2nd floor T'Stat with the one from 1st floor, same problem. 

Any suggestion for next step diagnose? Thanks

Comments

  • pecmsg
    pecmsg Member Posts: 5,330

    What thermostat do you have?

  • Jamie Hall
    Jamie Hall Member Posts: 24,984

    I find it a bit odd that the fan runs when you are calling for a cooler temperature, but not when you are calling for heat. Miswiring problem somewhere?

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Scd
    Scd Member Posts: 2

    It has a nest, tried another nest, also the old Honeywell. It was working before for years so wires should be ok

    Saw a similar thread somewhere where they had issue with one particular tap, in my case tried all three got same behavior

  • pedmec
    pedmec Member Posts: 1,078

    in the nest programming you have to specify they you want the nest controlling the fan on heat.