Steam return line fails every year

The pipe that failed in the pictures is coming from the dry return of the system. It connects to the equalizer return tee where there shouldve been a hartford loop. System is one pipe steam. I repaired this section of pipe each of the last 3 years. This time I piped a proper Hartford loop. It seems to be failing at the weld of the nipple. My question is can this pipe be failing because there was no Hartford loop causing water hammer in that location? Thanks
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
Comments
-
How much stress is on that joint? And do the pipes vibrate? Can we see the full configuration? Looks much more like a fatigue failure from a lateral or up and down vibration and overlolad…
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
-
You might also try a different material like stainless steel or brass. I've seen nipples this size in stainless for sale at Menards. Stainless is actually cheaper than brass.
Please keep us posted on what you end up doing and how it works long term. I have a customer with similar problem. They keep replacing with schedule 40 black pipe and continue to have the same problem. I just hear about this, but I'm not the guy doing the pipe changes.
Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.2 -
-
-
How much MU water is being added to that system?
0 -
May seem like a silly question but where is your main vent located ? I ve seen dry returns that where un vented meaning right at the end of a main they would install a tee and vent and then properly reduce and run the return back to the boiler as a dry return w no vent at its end . I ve have seen this occur and upon repiping w a vent at the end of the dry return have not had the issue again . Make up water does play an issue but I believe that the unvent dry return may be helping form acidic condensate and be the root cause the issue .
i ve run across this where the wet returns are shot so being they have the height they run it back as dry returns and leave the old vents where they where and problem's solved .
peace and good luck clammyR.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating0 -
Too much make up, or poor air elimination. Install a digital feeder or water meter on the makeup. You might add some corrosion inhibitor or Squick the boiler.
There was an error rendering this rich post.
0 -
I agree with Jamie. Also, how tight are you getting this joint? Remember, residential steam is low pressure. With a good thread sealant, you don't need to get the joints that tight, and with the PTFE tape, it's really easy to overtighten things because it reduces friction.
Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
If this is at the boiler, is the boiler throwing a lot of water in to the header that is flowing through the equalizer and in to this nipple? The pitting would seem to indicate it is corrosion. Maybe install it with the weld to the side or up so it isn't sitting in the water.
0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 67 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements