The pipe that failed in the pictures is coming from the dry return of the system. It connects to the equalizer return tee where there shouldve been a hartford loop. System is one pipe steam. I repaired this section of pipe each of the last 3 years. This time I piped a proper Hartford loop. It seems to be failing at the weld of the nipple. My question is can this pipe be failing because there was no Hartford loop causing water hammer in that location? Thanks

ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 25,595

    How much stress is on that joint? And do the pipes vibrate? Can we see the full configuration? Looks much more like a fatigue failure from a lateral or up and down vibration and overlolad…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Hap_Hazzard
  • pecmsg
    pecmsg Member Posts: 5,705

    crap chinese pipe.
    that little damage shouldn’t cause a leak.
    Try Sch 80 nipples.

    delcrossv
  • Pumpguy
    Pumpguy Member Posts: 726

    You might also try a different material like stainless steel or brass. I've seen nipples this size in stainless for sale at Menards. Stainless is actually cheaper than brass.

    Please keep us posted on what you end up doing and how it works long term. I have a customer with similar problem. They keep replacing with schedule 40 black pipe and continue to have the same problem. I just hear about this, but I'm not the guy doing the pipe changes.

    Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
    Website: www.nashjenningspumps.com

    The first step in solving any problem is TO IDENTIFY THE PROBLEM.
    delcrossvPaul S_3
  • delcrossv
    delcrossv Member Posts: 1,897

    I'd re do with red brass pipe and bronze fittings. Make the transition to black far above the waterline.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    neilc
  • Jamie Hall
    Jamie Hall Member Posts: 25,595

    The guys above do have some useful comments on different components — but I'm not convinced this one is a corrosion problem. I still want to know what the loads on that fitting are.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    LRCCBJdelcrossvHap_Hazzard
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,175

    How much MU water is being added to that system?

  • clammy
    clammy Member Posts: 3,205

    May seem like a silly question but where is your main vent located ? I ve seen dry returns that where un vented meaning right at the end of a main they would install a tee and vent and then properly reduce and run the return back to the boiler as a dry return w no vent at its end . I ve have seen this occur and upon repiping w a vent at the end of the dry return have not had the issue again . Make up water does play an issue but I believe that the unvent dry return may be helping form acidic condensate and be the root cause the issue .
    i ve run across this where the wet returns are shot so being they have the height they run it back as dry returns and leave the old vents where they where and problem's solved .
    peace and good luck clammy

    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
    Specializing in steam and hydronic heating

  • Dennis
    Dennis Member Posts: 124

    Too much make up, or poor air elimination. Install a digital feeder or water meter on the makeup. You might add some corrosion inhibitor or Squick the boiler.

    There was an error rendering this rich post.

  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,871

    I agree with Jamie. Also, how tight are you getting this joint? Remember, residential steam is low pressure. With a good thread sealant, you don't need to get the joints that tight, and with the PTFE tape, it's really easy to overtighten things because it reduces friction.

    Just another DIYer | King of Prussia, PA
    1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
  • mattmia2
    mattmia2 Member Posts: 11,711
    edited 12:05AM

    If this is at the boiler, is the boiler throwing a lot of water in to the header that is flowing through the equalizer and in to this nipple? The pitting would seem to indicate it is corrosion. Maybe install it with the weld to the side or up so it isn't sitting in the water.