Help choosing a new boiler (Part 3 - the Results! and more questions :)
RandomLady
RandomLady Member Posts: 59
edited December 2024 in Gas Heating
Hello forum,
For anyone wishing to follow along, here is Part 1 (me stating my situation and asking for help figuring out what sort of boiler to buy) and Part 2 (narrowing down my options) and a bonus question (me trying to figure out where to put the exhaust).
Before picture
TL-DR; My 30-year-old cast iron boiler died, so I needed to pick some replacement in a hurry. My water heater tank was also 30-years old, but still working, so I had to decide to replace it or not, and if so, with what. I had been quoted for combi-boilers and decided to come here and get advice. I ended up choosing an IBC SL10-85 modulating boiler (output range: 10,100 BTU/h to 79,000 BTU/H) with a 40-gallon indirect water tank for a home with just under 50,000 BTU/H design heat load.
Behold:
Special requests: anti-vibration mounts (though this boiler is actually so quiet), mixing valve for the hot water tank so I can store the water at a high temperature (apparently this is standard), dirt screen with magnet (apparently also standard), and exhaust through the existing chimney instead of basement wall (on the other side of the wall from the boiler is a patio area).
I am very happy to have central heating after 3 weeks of space heaters! Just want to thank everyone for your help and thought you'd like to see the outcome! (Feedback or things to watch out for, are welcome).
As expected, though, it seems to need tweaking.
Issue: the hot water isn't hot. I am hoping this is something I can fix myself rather than having to wait until Monday and call the guys to come back.
DHW at the faucet is about 85 deg F on hottest setting. I would describe this as.. lukewarm. DHW tank is currently set at 140F so I am told; was planning on increasing to 160F after the house had a chance to warm up. Which brings me to my second point.
House heating takes FOREVER. I increased the thermostat from 19C (66.2F) to 21C (69.8F) two and a half hours ago, and so far we've only managed to get to 20C (68F). Is this.. normal? (I'm used to a one-setting boiler firing all 80,000 BTU at my baseboards for like 5 minutes and being done lol)
Yesterday when we kicked the system on for the first time, it took four hours to go from 19.5C to 21C, and the installer explained it was taking a while because it had to work out the air in the system. I did not bleed any radiators, but they all feel warm (well, lukewarm..) so I think they should be good by now? It's been 15 hours? There is also an automatic bleeder installed. So I'm thinking the boiler water just isn't hot enough, like the DHW.
I haven't read the encyclopedias that came with it yet, but just wondering if this is something in the settings that I can do, or if I have to call them to come back.
«1
  • Kaos
    Kaos Member Posts: 904
    " it took four hours to go from 19.5C to 21C, "
    That is actually what you want, means the system is running well and was set up correctly. The boiler should only be supplying hot enough water to match the heat load of the house. For night time setback, set it to start earlier so it will meet your target when you need it.
    The cold water is a mixing valve adjustment. These have a cap you can loosen and unlock which lets you turn to adjust the temperature. If this doesn't work sometimes the check valves inside the mixing valve can have crud in them which needs to be cleaned out.
    I would not crank the tank temperature more than 140F. Indirects have very quick recovery and your boiler has enough heat output to run about 1 shower continuously. I doubt you'll have issues with the temp as is.
  • RandomLady
    Oh no!!!! So when I wake up in the morning and turn the heat up, it will be nearly lunch time before my house is warm? That's… not good news to me. 😔 I guess I will need to keep the electric space heaters around forever
  • RandomLady
    Hot water should be stored above 140F, to avoid potential Legionella: CDC
    hot_rod Member Posts: 27,717
    your old boiler was probably running 180f all the time. They can adjust the ODR on this one to get a bit quicker response. A pic pic of your mixing valve, some of them have tamper proof caps that need to be removed to adjust them up higher
  • RandomLady
    So adjusting the ODR can make my house warm up faster? Is this something I can do? (also what is ODR)
    This is my mixing valve: Watts LF1170
  • RandomLady
    I just Googled it; the ODR means outdoor reset. The boiler supports outdoor reset but it was not installed. (I asked about it and they said they usually don't install them, and I was good with that.)
    Does that mean I am stuck with 4-5 hour wait for temperature increases? 😥
    They set heating to 131? I think it needs to be higher.
    if you want to take the time to read through the programming section of the manual it will tell you how to change the setting.
    Usually the installer will write the settings in the manual as to how they programmed it
    turn the red knob to hotter. It should supply 120f . If the tank is at 140? But it looks like they set your dhw to 133, it may need to be hotter for that mixing valve to regulate to 120
    RandomLady
  • RandomLady
    For the first part, are you referring to the space heating or the domestic water heating?
    I increased the DHW tank temperature setting to 155F. The boiler has heated it but the tap temperature is still not hot.. looks like it's maybe around 90F now or just under.
    The mixing valve's documentation says it's set at the factory for 120F and should only be set by a qualified installer 🤔
  • Ironman
    Ironman Member Posts: 7,918
    ODR is something that is beneficial to you. It can save about 15% on fuel and actually make the house more comfortable. All they have to do is install the outdoor sensor and properly adjust the reset curve.
    When using it, you don’t want to be setting the thermostat up and down because the response time will be much longer and it will probably use more fuel. It’s old technology vs. new. You now have a boiler which modulates to match the load when properly set up. The old one was just 100% on or 100% off.
    As mentioned, the mixing valve on the domestic needs to be adjusted to get hotter water.
    Bob Boan
    RandomLady
    EdTheHeaterMan Member Posts: 12,453
    The mixing valve may be set to 120°F at the factory, or it may be a little off. I have had that problems with other customers that like to take a shower with 125°F water. the standard Mixing valve has a stop at 120°F and if your valve is already set there and the temperature sensing spring is out of calibration, then you will never get the hot water that you want. You may need to get a different valve that has a different temperature range like this one
    https://www.supplyhouse.com/Caleffi-521616A-1-Press-MIXCAL-3-Way-Adjustable-Thermostatic-and-Pressure-Balanced-Mixing-Valve-w-Gauge?_br_psugg_q=mixing+valve
    EDIT: Have the valve you already have checked for the proper adjustment and to see if there is any debris lodged in the valve the is preventing the valve from closing the cold water off enough to get you the 120°F water you want.
    New systems often have junk inside the pipes that foul thing up and need to be cleaned out.
    RandomLady
  • RandomLady
    Oh, I see. Actually that probably explains why they didn't install the outdoor reset then. I wanted to be able to lower the home's temperature at night (or when I'm away) and then raise it during the day. Maybe I will get one of those programmable thermostats so the temperature can start increasing a couple of hours before I wake up :)
  • RandomLady
    Huh. Okay. I think I will call them on Monday then. I feel like I could try to set this myself, but with the wording in the manual that came with it, that it should only be adjusted by a qualified installer, I'm concerned about voiding any kind of warranty it may have, or they won't support it after I monkeyed around with it. Especially if, like you said, it needs to be replaced.
    At least the home is warm now!
    As far as adjusting the max temperature for space heating or central heating (CH) in order to get the most out of your equipment you want it to operate at the lowest possible temperature. In order to get your system to operate the way the old one did, you need to operate it at 180°F. You may want to try a temperature somewhere in the middle to split the difference. Like start at 140° to see if that is more to your liking. if not then go to 145°F a few days later. Eventually you will find a nice compromise.
    RandomLady
    I will add one thing about your boiler, or any boiler for that matter. You need the proper size boiler to be able to heat your home on the coldest day of the year (sometimes called the design temperature, but that is not always true, it sometimes gets colder than the stated "DESIGN" temperature for your area). That said, you don't need that much heat on any given Tuesday when the overnight low is only 2°C. That will only need about half the capacity of that new heater. The best way to keep that heater operating at the lower capacity is with a lower water temperature pumping through the radiators.
    Since those lower water temperatures in the radiators will keep your home comfortable, then there is no need to use hotter water in the radiators on the milder days of the heating season. The problem with that is the lower temperature water will not increase the room temperature as fast as you would like. In order to get you the result of a lower room temperature while sleeping and a higher room temperature while awake, you could use a learning thermostat that will consider the outdoor temperature when changing from the low setting to the high setting and start the process 4 hours before you want the higher room temperature on very cold days and only start the process an hour ahead of time before you want the higher room temperature on milder outdoor temperature days.
    Honeywell, Nest, and ecobee are three companies that make such a thermostat.
    RandomLady
  • Ironman
    That’s not the approach to use if you want the best efficiency and comfort. That’s the way it was done with the old technology boiler that you previously had.
    With the new boiler, that approach actually fights with how your new boiler is designed to operate. The new boiler modulates its firing rate and the water temperature (when the outdoor sensor is connected) to match the ACTUAL load on the house. Running the thermostat up and down is counterproductive to that.
    Get the installer to come back and connect the outdoor sensor and set the ODR curve to match the type of radiators that you have. Then, set the thermostat at one temperature at which you’re comfortable and leave it there.
    You paid for a boiler with ODR and that’s what you should have. That’s the most efficient way to run that boiler - and the most comfortable.
    Bob Boan
    SuperTechbburdworldclasshvacEdTheHeaterMan
  • LRCCBJ
    LRCCBJ Member Posts: 1,043
    Sadly, as you know, this is an exercise in futility and no contractor wants to even think about bothering to set it properly (and they generally cannot without more data and iteration). The H/O needs to understand and adjust it……………if the contractor would take the time to explain it.
    I takes weeks of small adjustments to dial it in properly, and even in that scenario, it could be slightly off at the extremes of OAT.
    SuperTechRandomLady
  • Ironman
    To get it perfectly adjusted, maybe; to get it reasonably close, no.
    Anything close is better than nothing.
    As I stated previously, it’s a function of the boiler that supposed to be used and the contractor sold it as such. He should be honest and competent enough to do it or else he should not be selling the boiler. It’s not rocket science.
    Bob Boan
    SuperTech
  • LRCCBJ
    Excuse me…………😅
  • nordic440
    nordic440 Member Posts: 11
    I have an IBC boiler, absolutely love it. I don't have have an Outdoor reset either but I run it at 158*F and when it gets really cold I bump it too 165*F. Get a degree an hour rise easily on the coldest days.
    DHW is set at 125*F and mixing valve kicks it down to 120*F endless showers
    You just gotta dial that thing in, you will love it!
    RandomLady
  • RandomLady
    This is exactly my experience with the Lochinvar Knight boiler I had installed (in another house) back in 2009. I had to tweak its program for months before it worked right. (And I may be misremembering, but I think I had them remove the outdoor reset eventually - maybe).
    Unfortunately as a human (especially a female one), I don't prefer one constant temperature for 6 months straight just because that's the ideal thing for my boiler's design. It would be great if boilers were actually designed for the comfort and convenience of the people in whose homes they were installed. Sometimes I want it cooler, sometimes I want it warmer. And humans evolved with cooler temperatures at night - cooling down helps us make melatonin for sleeping. But I hate freezing during the day, at which time I am not normally bundled up under covers.
    As for the boiler sales people.. well they can only sell what is being manufactured and what is dictated by local codes. For example, where I live, all new heating systems have to be high-efficiency (more than 90%), so a mod/con was my only option. If I had a choice, I probably would have bought another cast-iron on/off boiler - but I didn't. Our jurisdiction even gives out programmable thermostats to encourage people to turn it down at night or when out at work.
    As for my DHW/mixing valve question, I just went down and tried to see if I could do anything; it turns out there is a screw that you need to remove, using a specific size of Allen key I don't have. So my water will remain tepid until next week when the installers can come back. Sigh.
  • LRCCBJ
    You are completely accurate in your analysis.
    If you are an individual who wishes to adjust the temperature in various rooms YOURSELF and have it recover to your new set temperature in a REASONABLE amount of time, outdoor reset is NOT FOR YOU.
    However, you CAN and SHOULD learn how to change the boiler supply temperature. You might want it at 165F in the coldest month of the year but would be perfectly pleased with 145F in November and will will be perfectly pleased with 130F in October. You can make these changes YOURSELF in about one minute after 10 minutes of instruction by the installer. LEARN how to do it and save fuel and longevity for the boiler.
    Note that I am simply guessing at the temperatures. Yours might be a bit different and that requires experimentation.
    Or, you just leave it at 180F year round and burn extra fuel for no reason. But, the recovery after a 10F setback will be just like your old boiler………….FAST.
    RandomLady
    up for a learning experience ?
    NTI has videos on how to program their boilers . If the installer cannot or will not you could learn the settings and do it yourself. You need them to wire in the sensor however.
    Or call the NTI rep in your area, find the contact info at the NTI site. Tell them the installer doesn’t want to connect the ODR on you newly installed boiler
    Have the model and serial number ready
    Ill bet the local rep would be happy to help you get it adjusted
    IronmanRandomLadyEdTheHeaterMan
  • Kaos
    As others have said, you want outdoor reset.
    The typical dialed in curve is not for you though, but that can be easily adjusted to allow for faster recovery. The curve with faster recovery will still save you a significant amount of fuel in the shoulder season, this is free money in your pocket. There is no need for fixed setpoint. The best part is that once you have the curve selected that works for you, you don't have to do anything, it all happens automatically.
    Running a modcon in fixed temperature mode is throwing all that efficiency you paid for out the window.
    P.S. Once you get your mixing valve fixed, turn down the tank temperature. The only need for 160F water is if you keep running out.
    Ironman
    contacts, if you need to go this far
  • RandomLady
    Thank you, but I do not have an NTI boiler, so I don't think they would support me
  • RandomLady
    Yeah but… I don't like "happens automatically" - I want to be able to choose what temperature my house is based on what I am doing that day, or how I'm feeling, or what time it is, or whether the sun came out, etc.
    Since the temperature outside varies a lot.. for example yesterday when I woke up it was -10C, (14F) and today when I woke up it was -2C (28F) so in any case, the boiler would have to do a lot of adjusting throughout the day. I guess I don't get why the outdoor temperature varying is good for efficiency, but the indoor temperature varying, is not. The boiler still has to do work…?
    As for my water tank, turning up the temperature did not fix the chilly hot water at the tap. I turned it up because it's recommended to store water above 140F (as I stated above), and it was sitting at like 131F before 😬. So far, I don't know if I'll run out since I mostly get cold water right now anyway. 😓
  • RandomLady
    Yep, I read through all the manuals yesterday and I can surely figure out how to do it. I also noticed the supply and return temperatures are close together. (As in one of my screenshots above, they are only 4F apart). I believe this means the boiler is not condensing. So eventually I want to figure that part out, too.
    When the installers come back to fix the hot water, I will ask them about both of those things.
  • LRCCBJ
    Set the heating circulator to "LOW"…………it is currently on "HIGH". Very simple. This will slow the flow rate and raise the DT so the return water is cooler. You are looking for 15-20F for a difference between supply and return. Don't listen to them if they claim it won't work.
    (Leave the circulator for the indirect on "HIGH".)
    RandomLady
  • Kaos
    The only thing that happens is the unit automatically adjust how hot the water it produces. It doesn't change at all how hot your house is, that is set by the thermostat.
    For your example, between the two days, all that would have happened is the water temperature changed a bit, but the time to get the house back from night time setback would have been the same.
    People tend to overestimate how much fuel is saved by night time setback. Unless the setback is for a long period of time or you have a very leaky structure, the fuel you save during the night you need to use to get the house back up to temperature. I have a heat pump and for those night time setback is even worse, so I never use any setback as recovering from setback would use more electricity than keeping the house the same temperature.
    Unlike night time setback, outdoor reset and running your unit at the lowest temperature does actually save fuel and saves fuel the whole day and night as it increases the amount of condensation which bumps up the efficiency. This is why you want to use it.
    With modcon, recovering from night time setback is best done with a programmable thermostat. Just set it to start before you wake up and the house will be exactly where you want it.
    IronmanRandomLady
  • Ironman
    If you wanna sleep with it cooler, why not just turn off, or throttle down the radiator in your bedroom instead of cooling the entire house down?
    Bob Boan
  • RandomLady
    My baseboard, copper fin radiators don't have individual control settings. At least, none that I'm aware of. I have to take one end apart and there is a stem for bleeding, and that's it.
  • Grallert
    Grallert Member Posts: 1,142
    You might have mentioned it above? but the type of emitters you have is important here. If you have baseboard convectors the water you run through them will likely need to be hotter. Their designed for 180 degree water in order to deliver the 155 or so BTUs with a rapid temp rise. Because they have very little mass they radiate very little heat energy. They're really only convecting. That said you boiler with its ODR should be able to compensate and adjust for all that.
  • Ironman
    There should be an adjustable damper (louvre) on each baseboard that you can open or close to control the heat output.
    Bob Boan
    ethicalpaul Member Posts: 8,925
    Or if the dampers aren't cutting it, you can also place a folded blanked over some or all of the baseboard to reduce how much heat it emits into your room. Or place aluminum tape over the louvers.
  • RandomLady
    Can you clarify this please? Are you saying that with outdoor reset, I can still manually turn the thermostat down and up as desired?
  • RandomLady
    Maybe..? But even if it does, to be perfectly frank, I'm not about to move furniture and get out my tools every night and morning to adjust it. That will get old VERY fast. I would much rather just use my thermostat.
    WOW. This is really going off in an unusual direction. From what I understand from this discussion is that @RandomLady is experiencing a problem of not enough heat for a timely recovery from a night setback, …and now it is giving information on how to reduce the heat output of Baseboard radiator convectors and to call the wrong manufacturer's rep for help..  Where did we all go so wrong?
    1. Our friend wanted a simple on off cast iron boiler
    2. As a result of local regulations she is restricted to a high efficiency boiler only
    3. She ended up with Mod/Con boiler from IBC and a matching IBC indirect water Heater.
    4. Now she has 2 problems.
      1. Mixing valve from DHW is offering 90°F (~32°C) for showering
      2. Slow (4 hour) recover from manually set night setback takes too long
    5. Furthermore the installing company has not installed the outdoor sensor for the ODR to operate.
    So the advice was given to adjust the mixing valve however the instructions with the mixing valve states that only a professional should adjust the mixing valve. (She does not want to void any warranty) Also that particular valve has a Hex or Torx screw on the cap to prevent homeowner adjustment, and the homeowner does not have the correct size wrench to remove the cap.  So the homeowner is stuck with lukewarm showers until the installed can find time to return to make the needed adjustment.
    As far as the need for faster recovery is concerned, advise was given to increase the boiler temperature in order to allow for faster recovery.
    And other advise on matters other that getting the homeowner the comfort she wants may be off topic.
    Does that just about sum it up @RandomLady ?
    LRCCBJRandomLady
