Main Vent Type and location on Vent Tree

Wcurtis
Wcurtis Member Posts: 66

if a smaller main vent (Hoffman 75) is the first one that sees the air needing to be removed on a vent tree followed by two Big Mouths and one Gorton 2, does the location really matter?

Just placed the Hoffman last on this header and it didn’t even get hot (it was pulled off another header for this test and working), Bigmouths and Gorton worked as expected, have an extra Hoffman and experiementing with faster air removal time.

Comments

  • Steamhead
    Steamhead Member Posts: 17,358

    Shouldn't make a difference- what happens if you put the #75 first?

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    ethicalpaul
  • Wcurtis
    Wcurtis Member Posts: 66

    yeah that is what I’ll try tomorrow just for grins

  • Wcurtis
    Wcurtis Member Posts: 66

    Just wanted to see if others had any additional in-sight, it’s just fun (kinda of a kid at heart) experimenting with these details

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,364

    If it is a manifold it makes no difference which vent goes where.

    ethicalpaul
  • dabrakeman
    dabrakeman Member Posts: 627

    It should get hot if it is venting air to let steam in regardless of where on the tree it is unless there is a water block in the tree or the vent has gotten stuck closed.

  • Jamie Hall
    Jamie Hall Member Posts: 24,699

    It will only get hot when very hot air or steam reaches it. It's not uncommon for vents on dry returns (not on steam mains or steam main extensions) to never get hot — and never close. In fact, they shouldn't…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England