Pressuretrol settings
before:
after:
now I have to repack the nut on one of the radiator stems that’s leaking.
What do you think of the new settings?
Comments
-
Widen the differential to 1 psi.
What you want is the boiler to shut off at 1 1/2-2 psi. You want the boiler to restart at as low of a pressure as you can adjust it for ….just before the gauge needle hts 0 psi. Yo may need a 0-5 psi gauge to adjust for this as doing it with a 0-30 psi gauge will be difficult if not impossible.
2 -
There was a good tip in here about tightening the packing nut.
Tighten it while the heat is running, so you only tighten enough to silence it, and not more
0 -
yep I repacked it while cold and then had to tighten while the heat was coming up as it still leaked until it stopped
0 -
I am thinking of removing the pressuretrol and putting in a vaporstat.
What would be a good starting point for settings??
0 -
Right where that one is set.
However! Being absolutely level is critical with the mercury vapourstats. Even a tiny bit off can throw it several ounces out of calibration. Be sure that the pigtail on which it is mounted has the curl perpendicular to the body. I also recommend putting a quality low pressure gauge on the same pigtail to see what it really is doing, and adjusting the instrument to match the gauge.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 921 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements