Hello! We bought a house with a one-pipe steam system feeding 10 different steam radiators throughout our house. Initially, all of the radiators were setup with "C" or "D" vent valves (Maid-O-Mist and Gortons). There has been significant noise from the air vents on the radiators and they were all poorly balanced. I have most of them balanced a little better, changing certain vents to 4s, 5s, and 6s, like the diagrams show. Using a thermal gun they are all much closer to heating up at the same time. But the vents still make a whistling sounds as they heat up, even with brand new vents. It isn't consistent, they all whistle and then get quieter and then back to whistling (not very high pitched, more like someone learning how to whistle and struggling), like the pressure pushing out the air is varying. Is this an issue with the boiler or something else related to the venting setup?

The main has two vents, both Gorton #1. I have new ones but they are in difficult places to change so I haven't gotten to them. The mains heat up pretty quickly and I do hear some air coming out of the main vents. The mains aren't insulated, I am working on ordering insulation now. All of the radiators are angled properly as well, no water hammering. The thermal gun shows about 210 deg F on the main right off the boiler. Boiler was serviced a month ago, but it was really just a cleaning.

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,556

    Get the new main vents on there. That may make a useful difference — though it may not end the problem. Also get the mains insulated, and check very carefully along their whole length for any sags or even relatively flat stretches. The variation in sound makes me wonder if there aren't stretches where condensate tends to collect while the system is heating up. Not stopping the flow of steam, but momentarily slowing it down.

    Beyond that also check what pressure the boiler may be set to, although that is not likely to be a problem near the beginning of a heating cycle.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • ethicalpaul
    ethicalpaul Member Posts: 6,433
    edited November 19

    Insulating the mains is fine idea, it helps put the heat where you want it and keep it from where you don't, assuming you don't want your basement warmed.

    But it will not have a positive effect on your whistling, and may actually make it worse. Here me out @clammy and other friends 😅

    A. If the mains are COLD when the call for heat begins, a lot of steam will go toward warming the pipes (this is true regardless of insulation, I hope we agree). This makes the steam push a lot "slower" along the main because steam is condensing as it moves slowly along the main. This will make an undersized main vent perform just fine because the volume of air that has to be vented is spread out over a much longer time.

    B. If the mains are HOT when the call for heat begins, much less steam will go toward warming the pipes because they are already warm. The steam will move much faster along the main, and the job of the main vents will be much larger because the same volume of air that is in the main is going to be pushed in a shorter time period. This will in turn put more pressure on the radiator vents because the main vent will be overwhelmed, increasing the amount of air pushed through the radiator vents, and increasing hissing.

    And by insulating the mains, there will be many more times when the B situation occurs.

    So my advice would be don't bother with insulation until after get your main venting where it should be and/or get the hissing figured out. There are other threads that explain how to time your main to see when you have enough main venting, and I recommend that procedure rather than just trying to do the math. It eliminates all unknown variables by letting the actual behavior of your main dictate your venting.

    There are other variables that could be affecting your hissing as @Jamie Hall mentioned, including the question of "is your boiler oversized?".

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • IanMac227
    IanMac227 Member Posts: 5

    Thanks for the advice. I will try and change the two main vents and see if there is any difference. I don't think there are are sagging or low spots on the mains but I can double check that. I'll also look into timing the mains and confirm whether the main venting is an issue.

    What pressure should I be looking for off the boiler? Like mentioned, I do hear it pretty quickly as the lines fill with steam. The boiler is a Weil-McLain SGO-4 (144,000 Btu/hr capacity).

  • ethicalpaul
    ethicalpaul Member Posts: 6,433
    edited November 19

    If you have a low-pressure scale gauge (like 0-3psi) you would hope to see just a slight movement well under 1/4 psi.

    If you have a factory-installed 0-30 psi gauge you would hope to never see it move. But they are almost always broken anyway and never move, so that is a false sense of security there. If it is working, you might see it slowly rise up to 2-3psi once all your radiators are full of steam, to the point where your pressuretrol shuts off the boiler on pressure.

    If you see it go up quickly to 2psi or higher then your boiler is almost certainly oversized.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • IanMac227
    IanMac227 Member Posts: 5

    Okay thanks. I have a 0 - 30 psi gauge and haven't seen it move yet. Wasn't sure if it was working or not.

  • bburd
    bburd Member Posts: 1,011
    edited November 19

    @IanMac227 can you post pictures of your pressuretrol, with the cover on and off? We need to see the settings. Also, has the pigtail between the pressuretrol and the boiler been cleaned? Sometimes they clog up and prevent the pressuretrol from sensing the steam pressure.


    Bburd
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,157

    That's a good thing. Your home should be able to heat at less than 1 PSI. If that gauge is not moving, then you are operating at about 1/2 PSI or less. In order to diagnose your whistling issue, you may want to invest in a low pressure gauge. You need to leave the 0-30 gauge in place by code. This would be in addition to that gauge. https://www.supplyhouse.com/Winters-Instruments-PLP302-2-1-2-PLP-Steel-Low-Pressure-Gauge-1-4-Bottom-NPT-w-Brass-Internals-0-55WC. This gauge measures up to 2 PSI in ounces per square inch.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    delcrossv
  • IanMac227
    IanMac227 Member Posts: 5

    Here is a pic of the pressuretrol. Looks like it's set right around 1 psi. I pulled the gauge off and it does seem like there is gunk throughout the pigtail. Doesn't look completely plugged but obviously I can't see the whole thing.

    Also thanks for the link on the gauge. I can certainly look to add it.

  • bburd
    bburd Member Posts: 1,011

    That white wheel inside the pressuretrol should be set to "1". Pipe cleaners work well for cleaning out the pigtail; you should also be sure that the holes it fits into on both ends are clear.


    Bburd
  • IanMac227
    IanMac227 Member Posts: 5

    I did confirm that it is set to "1". For cleaning the pigtail, were you able to clean it with pipe cleaners without taking it off? Just wanted to avoid unwiring if I didn't have to.

  • Jamie Hall
    Jamie Hall Member Posts: 24,556

    I've had better luck cleaning things like pigtails using long heavy zip ties than pipe cleaners — but your mileage may vary. If you have access to compressed air, you may be able to blow them out.

    However… I think you may have to unwire things just to get access to the pigtail to work on it. Take pictures…