LWCO Blowdown....Under a Little Pressure?

AdmiralYoda
AdmiralYoda Member Posts: 662
edited October 8 in Strictly Steam

I have a 44 year old Peerless boiler and I test the float type LWCO weekly. I generally have two different methods.

  1. While the boiler is running, but not steaming I will open the drain on the LWCO and verify the boiler shuts down when the float drops. I'll let it drain until the water is clear and top the water back off, then let it boil to drive off any free oxygen.
  2. Open the LWCO valve while the boiler is making steam and under pressure, maybe 0.5-1psi. This doesn't shoot the water out of the LWCO drain but actually allows the water in the LWCO to boil and become turbulent. Kind of a LWCO steam cleaning. Since the boiler is really hot I'll let it cool a bit before toping it off, then fire it back up to drive off the free oxygen.

Any harm to the LWCO while doing the blowdown while under pressure? Seems to keep it clean. Thoughts?

And to be clear I'm not bypassing any safety controls when I do the blowdown under a little pressure. I just set the thermostat a couple degrees higher and let the system fill up with steam and build some pressure. My Vaporstat cuts out at 18 ounces with a 12 ounce differential. I have a Pressuretrol backup too. 2psi cut out with 1psi differential. I measure this with a 0-32oz gauge.

Comments

  • ethicalpaul
    ethicalpaul Member Posts: 6,144
    edited October 8

    It looks like they recommend flushing it during boiler operation:

    http://s3.supplyhouse.com/manuals/1350816480646/83711_PROD_FILE.pdf

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    AdmiralYodaEdTheHeaterMan
  • Jamie Hall
    Jamie Hall Member Posts: 24,242

    Whatever works. I see no particular problem with either of your methods. Main thing is to get that blowdown valve fully open. My own preference is to not just open it, but to open it, let it swoosh, close it, let the LWCO refill, open again, rinse and repeat until the swoosh is clean — then top off and go. Usually two or three swooshes will do… but as I say, whatever works.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    AdmiralYodaEdTheHeaterMan
  • ChrisJ
    ChrisJ Member Posts: 16,159

    For me, the main thing is to make sure the burner automatically shuts down while you're dumping the LWCO.

    If it doesn't, the LWCO doesn't work and that's bad.

    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    ethicalpaulEdTheHeaterManLong Beach Ed
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 8,794

    I told my customers that the LWCO flush is better done under pressure. And if the water feed is connected to the wet return before the HL, then you can add water right away.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    ethicalpaulRTW
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,128

    The above answers are fine with me. My only comment is to assure that the piping connecting the LWCO to the boiler is clear. It can be partially plugged and the LWCO will shut the burner off on a blowdown but if the boiler loses water and the connections are compromised the LWCO may not trip on low water.