Warren Webster..vacuum or not
Hi all, I generally work on one pipe systems and occasion come across two pip (generally vapor systems) but they are all gravity systems. I know that often most of the old vapor systems utilized natural induced vacuum to increase efficiency BUT……. I am working on an old warren Webster vapor two pipe system with boiler feed pump that the customer is insisting that the system is a vacuum system and has always had a vacuum pump. I have never worked on a pumped vacuum system and not sure how to identify one but im pretty sure that this is not suppose to be a pumped vacuum system as it looks like a typical gravity Webster vapor system that they are using the feeder reservoir to increase boiler water. Any assistance would be greatly appreciated as to what I should be looking out for.
  • Pumpguy
    Pumpguy Member Posts: 801
    The book, STEAM HEATING, A Manual of Practical Data compiled by THE GENERAL ENGINEERING COMMITTEE of WARREN WEBSTER COMPANY published in May, 1922 is available for viewing online if you do enough searching.
    Maybe your library can get you a copy.
    My original copy with 367 pages has a wealth of information, and on page 149 through 178 has information about the use of mechanical vacuum pumps.
    Sorry I can't be more helpful with your specific questions.
    Steamhead Member Posts: 18,526
    @Onepipe @Pumpguy we'd have to check the pipe sizes against the various capacity charts. In a system designed for pumped vacuum, the return lines would be smaller than for gravity return because the pump would increase the pressure differential between supply and return.
    Many Webster systems would use naturally-induced vacuum to allow the old coal boilers to keep making steam as the coal fire burned down. But this would still use gravity return.
    If the boiler-feed pump replaced an old Return Trap, this would still have been gravity return unless the boiler pressure got too high, then the Return Trap would kick in.
    This is all covered in @DanHolohan 's book "The Lost Art of Steam Heating Revisited", available in the Store on this site.
    Consulting
    Mad Dog_2
  • Onepipe
    Onepipe Member Posts: 84
    @Steamhead thanks for the info and i have owned Dans book for many years. My wife jokes with me that I never leave home with out it but here in the detroit area there is alot of old systems that can throw you a loop. I have been reading up on vacuum systems and am familiar with natural induced systems with modern boilers, but I do not work on very many feed pumps (most are gravity return systems) and never one this old that was converted from gravity. It has a feed pump that can pull vacuum also, It was set on the vacuum setting when I showed up but it is hammering like crazy, has failed traps just about every where, poor piping, air lock exc….. I am just trying to not step on a landmine…HA! So would I need to take a look at the return main condensate capacity? is that what you are referring to when you mention sizing the lines? Thanks for the help.
    edited September 2024
    Consulting
    delcrossv
  • Onepipe
    @Steamhead thanks for the article. I’ll get some pics next week and see what you guys think. The dry returns seem common in size, I would not call the “ undersized” same with the take offs and returns to the radiators……. I’m going to be surprised if this system truly is a vacuum system but I’ll keep reading up and get some pics. Thanks
  • Onepipe
    So, I finally got around to providing some updated info on the potential Webster vacuum system I am currently working on. What I have found out is:
    First, the building does have a warren Webster vapor system and use to be fed by a central coal fired boiler for the entire campus that some time in the 70’s the central plant was shut down and a boiler was installed and then another was installed which is the current boiler that is in the building today.
    Second, Most of tue thermostatic rad traps look like they have never been touched and have failed causing steam to enter the dry return. I have since ordered net cages and will be replacing all the traps throughout the building. About half of the supply valves have been replaced with what looks to be non vacuum rated angle valves so that will need to be addressed still.
    Third, there is a vacuum pump in the system but I’m 90% sure that the system was never designed for a pumped vacuum. When looking in “lost art” a 1-1/2” dry return can handle 326,000 btu of load and a 2” can handle 710,400btu of load. My boiler is rated at 587,000btu and I have two 1-1/2” condensate returns coming back to the pump that tie into a common 2” return before entering the vac feed pump. Why I am concerned about this is because currently the vac pump is shot (mostly from the steam in the returns) and there is no equalizer line piped back to the boiler which is 50’ away in another room. I hate to spend all that time and money to install a new vac pump, pipe an equalizer line and then find out I don’t really need it. I talked to the pump company ( skidmore) I can re pipe my tank vent to the lower receiver tank and run the system as a feed pump only. I’m had temped to temp try it out and see if my calculation's/thoughts are correct.
    Any thoughts would be appreciated especially on the vac pump. please see the photos below.
  • jumper
    jumper Member Posts: 2,541
    If open trap passes steam can one make the argument that too much steam is admitted to radiator?How many radiators are there? How about restricting inlets? Somebody buys or makes pierced plates.
    Orifice Plates are used in valves suitable for two-pipe steam. Different length tailpieces available. Radiator inlet orifices in sizes 1/2″, 3/4″, 1″ & 1-1/4″.
    Jamie Hall Member Posts: 27,395
    If no one has messed with the original valves on the radiators (yeah, right, I know) it's even easier. Free up the valves (patience, and don't be a gorilla) and then try closing a valve — pick a radiator, any radiator — until the radiator get hot 80 to 90 percent across. Then stop. Done. The original valves on almost all vapour systems were actually designed just for that purpose… some of them (Hoffman) actually have two elements inside — one on/off too hot/too cold, which a handle, and an inner element which you aren't supposed to mess with after initial adjustment (need to take the valve partly apart and use a wrench) which is adjusted to the size of the radiator — at the maximum 6 to 8 ounce working pressure differential of the system.
  • delcrossv
    delcrossv Member Posts: 2,204
    edited October 2024
    @Jamie Hall Mepco still makes them.
    https://www.mepcollc.com/product_category/regulating-valves/
    https://www.mepcollc.com/product/swrf-b-regulator/
    That's what I'd use, then — much less hassle than orifices…
    delcrossv
  • Onepipe
    So I have used oraphase plates on two jobs now with success and also I have been using the mepco modern replacement valves and they work great too. This system has been worked over by more than one (non cautious) mechanic so it’s not in great shape. I’m not too worried about the valves, traps or steam supply I can handle that but I have never worked on a vacuum pump system before. I’ll be honest I don’t even know what one should look like….. this system looks pretty normal for gravity return. That said this system has a vacuum pump….also two dead ones laying in the corner….but the math and piping layout is saying that it was originally a gravity return system based on load vs pipe size. The current vac pump is shot but the feeder pump still works. I’m tempted to try and run it without vacuum for a month and see how it goes once the other issues are solved. I would need to pipe in a temp tank vent of course. Am I crazy. I’m just wondering is when the last boiler was installed the mechanic did not understand the difference between naturally induced vacuum and pumped vacuum…..based off his piping he/she was not reading much.
    I'd say to go for it without the pump… the worst it can do is not work!
    mattmia2 Member Posts: 16,891
    The worst it can do is only not work when you aren't on site to see what is happening.
    delcrossvPRR
  • Pumpguy
    edited October 2024
    @Onepipe, I believe what @Jamie Hall was trying to say in his earlier post is to not totally close, but throttle the radiator's steam valve to limit the amount of incoming steam so the radiator gets hot across 80 or 90% of its surface.
    This has the same effect as an orifice except the flow rate of steam can be changed to more or less, where with an orifice you're stuck with just one flow rate.
    The nice thing about this arrangement is the radiator condenses all the steam it receives, so there's no steam left to get into the return lines.
    On the flip side, the bad thing is a set throttling valve or orifice can't modulate, so during colder weather that radiator can't put out more heat because now its not getting enough steam.
    Regarding your vacuum pumps, yours are not really vacuum pumps as such, but common centrifugal pumps that pump water through an eductor venturi nozzle to produce vacuum using an entrainment principle. Repairs to these pumps are usually quite simple, requiring just a new shaft seal and motor bearings. The impeller could have cavitation damage, and if so, a new impeller would also be needed.
    When fitting a new shaft seal, check what elastomer is used. Viton or Ethylene Propylene are more heat resistant than common Buna N.
    I thought I read in a post above an implication that vacuum in the return line affects the flow of returning condensate. Thats a common misconception. The condensate flows back to the receiver tank by gravity. The only case where return line vacuum affects the flow of condensate is where there is uphill piping in the return lines and then the vacuum lifts condensate to a higher level return line.
    Doesn't the vacuum reduce the size of the return needed to vent the emitter?
    Depends on how much vacuum you pull in the return line. At any reasonable level of vacuum, the effect is not relevant.
  • Onepipe
    @Pumpguy thanks for the info, I have been looking at the blow apart for the pump/tank set to and you are exactly right. It just looks like a condensate pump ( wired as a feed pump) with a feed pump/tank (now called a hurling tank) sitting on top of it. That said based on the number of non vac rated angle valves that have been replaced and the leaking steam valves throughout the system I’m pretty sure it could not hold a vac even if it wanted to. I’m going to try it out with feed pump only and pipe in a temporary vent and see if my theory works before I put any money into rebuilding those pumps.
  • jumper
    Regarding setting throttle valve; it would be nice if one can disable handle so that folks don't continuously mess you up. Regarding those DomesticPump units; ingenious fellows can improve set up by splitting system into separate vacuum receiver and pump receiver. Somebody at ITT may have schematics?
    The question of return pipe mystifies me. Pumpguy is correct that condensate moves by gravity. Even a wimpy eductor sucks air plenty.
    What's the question on the return pipe? I missed something…
  • Pumpguy
    Its really quite simple to measure the air removal (CFM) capacity of a vacuum pump. Just valve off your receiving tank and then connect an orifice that is open to atmosphere. Then operate your vacuum pump and see what vacuum level is showing on the gauge. For this test to be accurate, it is important that the only air entering the receiving tank is air that is flowing through the orifice.
    If you tell me the horsepower of the centrifugal pump that is used to produce the vacuum, I can give you a starting point for orifice size.
    The attached file goes into more detail.
    The typical air removal capacity of a water eductor type vacuum pump is in the range of 6 to 10 CFM per motor horsepower.
    Another type of vacuum pump commonly used on units like yours is a positive displacement liquid ring type vacuum pump. These are more efficient, moving between 12 to as much as 17 CFM per motor horsepower.
    Another issue with vacuum pumps is their sizing. In a new system that is air tight and all traps are working as they should, 1/3 of a CFM per thousand square feet EDR is adequate. As the system gets older, the load on the vacuum pump increases due to minute air leaks that develop and traps not holding as they should.
    Recognizing that today's vacuum pumps are almost always working on old systems, I recommend going with one (1) CFM per thousand square feet EDR.
    It is a very common problem for vacuum pumps to be sized too small for a given system and operating conditions, and when this is the case, the operator is never able to fully realize the benefits vacuum pumps can provide.
    Unlike condensate pumps, there is no hard and fast rule on sizing vacuum pumps; its largely a matter of experience and judgement. One thing is for sure; within reason, you can't go too big in sizing vacuum pumps for steam heating applications.
    reggi
  • The Steam Whisperer
    The Steam Whisperer Member Posts: 1,316
    edited October 2024
    When installing the temporary piping in the vent on the condensate tank, you can just add a couple unsprung teflon ball check valves to allow a natural vacuum to form. I use Apollo 610104-A1 valves. I have a system nearby in a large home that the owner says on boiler shut down (Peerless gas fired EC model), the system pulls down to about 8 inches vacuum, and on the next start is usually still around 3 to 5 inches….so you have vacuum nearly all the time in typical midwinter weather.
    Also, since you have already used orifice plates, one of the neat things you can do on most systems is run a modulating burner on direct outdoor temperature reset. Once you get above minimum fire rate, the burner runs nearly nonstop and the orifices distribute the heat evenly through the system. Some systems require a higher firing rate for start up to prime the system and can then drop back to outdoor reset.
    I used this same concept at my church where we stage fire 2 boilers as needed with 2 stage thermostats. Our energy usage for the building is at least in the bottom 20% nationally based on Energy Star data. We are in Chicago, so cold winters ( much colder than New York)
    Also, since pretty much any system installed after 1915 or so has radiators that are about 60% too large for the peak design load (SBI standard sized radiators seem to be more like 100% or more oversized), if the orifices are sized properly and pressure controlled properly, radiator traps are no longer needed….steam never reaches the traps.
  • Onepipe
    @Jamie Hall when talking about the return piping it had to do with my maths for pipe capacity compared to my boiler in an earlier post that I am pretty sure this system was never designed for a vac pump and some where along the way it was added….
    “1-1/2” dry return can handle 326,000 btu of load and a 2” can handle 710,400btu of load. My boiler is rated at 587,000btu and I have two 1-1/2” condensate returns coming back to the pump that tie into a common 2” return before entering the vac feed pump.”
  • Onepipe
    @The Steam Whisperer with putting that check on the pump tank do you ever end up with condensate flow issues? I have seen plenty of systems pull a vac on shut down (1 pipe for sure) but never any continue to naturally hold vacuum during a fire cycle.
  • Onepipe
    @Jamie Hall thanks for the response and that’s what the math is pointing to. Would there be some other reason why some one would have added that vac pump to the system that I’m missing? (Other than some crazy people do crazy things) on a different note Im going to try and run the system next week with feed pump only and fingers crossed it all works out.
    neilc
  • jumper
    »you can't go too big in sizing vacuum pumps for steam heating applications.«
    Dry vacuum pumps suck more air per horsepower than liquid ring. But you need a "knockout tank" to prevent liquid slugs. Another item to watch.
    Those hurled water package units are inefficient on account of low NPSH as well as on account of venturi eductor. Another issue is condensate temperature. Both liquid ring pumps and eductors have more capacity with cooler water.
    Miscellaneous comment — no vacuum pump can produce a vacuum below the vapour pressure of the condensate at the condensate temperature.
  • jumper
    I wonder if anyone measured steam flow resistances through hermetically air free pipe?
    Steam is a gas, and so long as it is not condensing actively the flow resistance will be very close to that of air at the same temperature and pressure.
    I haven't had any trouble…Nearly all of the two pipe systems we see in Chicago were originally naturally induced vacuuum, so historically that didn't seem to be a problem. How long the system will hold vacuum during a firing cycle obviously depends on its tightness and the length of the steam cycle. Just basic physics would tell us that if the system is quite tight, and the load is constant, then each heating cycle would just reach 0 psi at the end of the cycle. Most of the heating cycle time over a heating season should then operate in a vacuum. You would not get the performance of having a vacuum pump ( unless you are using a steam powered air evacuation unit like on Moline Systems), But starting a system at 8 inches vacuum on a typical cycle should give incredibly good distribution like a vacuum pump. Once the system is primed the vacuum created by condensing steam in the radiators should keep things moving very nicely.
    Again, in Chicago, I find extremely few straight two pipe steam systems… nearly everything was originally naturally induced vacuum or had vacuum pumps.