GW
GW Member Posts: 5,188
my guy missed the grounded 3 wire to a nest, smoked the trans as he was replacing the control. So now we have a new control with a dead trans. I called Taco to see if we can get another trans and was politely told “no”. Hmmmm OK. Anyone have a source ? Thanks
Gary Wilson
Wilson Services, Inc
Northampton, MA
gary@wilsonph.com
    mattmia2 Member Posts: 17,467
    I thought those were modular and you could put 1 or 2 transformers in them. Maybe look at the model that does have the modular xfmr and see if the xfmr for that is the same. Could always just buy an appropriate xfmr and wire nut it. If one of the leads is connected to ground then match that up.
  • Robertw
    Robertw Member Posts: 88
    BE130915GEK- York Controls 120V-Primary 24V-Secondary 15Va Transformer — NWF Supply
    save the pig tail and the connectors. this should work for you
    Robert W.
    Energy Kinetics
    HVACNUTkcopp
    Bigger than the one they used but should work if it physically fits
    https://www.supplyhouse.com/Taco-ZVCXFR-001RP-Replacement-Transformer-for-Valve-Controls
    Since they are both class 2 it shoudln't be an issue overcurrent wise substituting the larger xfmr.
  • GW
    OK yes I see various trans on amazon and such, I was trying hard to have the 'proper' leads, but scru it! Thanks all
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
    GGross
    I really thought there was an xfmr for the one that could have one or 2 xfmrs that had those connectors on it.
  • ratio
    ratio Member Posts: 4,264
    I've had some luck with buying housings & crimp pins (& usually another crimper!) to roll my own connectors when I can't source the connector/part.
    Unfortunately for me, the local electronics store where I found all these parts at closed it's local branch & consolidated operations about an hour's drive from here. I still may end up there from time to time.
    GW
  • GW
    Yes, same here, when the local Radio Shack closed, I gasped a small bit. But the Amazon machine comes through here and there. I get it——small mom-pop suppliers for our stuff are going away because we all buy stuff online. I think everyone is in survival mode. I'll do what I gotta do.
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
    HVACNUT Member Posts: 7,526
    That's why God invented wire nuts and crimp connectors.
    kcoppGW
  • GW
    @HVACNUT indeed, I’m a little OCD, want to have things original OEM. But if Taco says no, fine and dandy.
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
    You could use the 1/4" qc xfmr and put insulated 1/4" terminals on the original harness and it would look like it is supposed to be that way.
  • HomerJSmith
    HomerJSmith Member Posts: 2,794
    I've done that and the biggest trans VA is 30VA which I bought from Supplyhouse. com. A larger trans will not allow the cover to be properly put back on. I cut the wires from the old trans close to the bad trans and I did pop rivet the new trans on after drilling the old rivet out. I wire nutted the wire leads from the board to the new trans. walla!
  • Joe Mattiello
    Joe Mattiello Member Posts: 752
    any 40va transformer will work. Save the pigtail and wire nut connections
    Hopefully this helps
    Joe Mattiello
    Taco Comfort Solutions
  • GW
    Joe, yes, fitting inside the enclosure is the snag