High limits, flame rollout switches, spill switches…………never, although I've seen a few; usually on flame rollouts because tech's. are too lazy or too scared to further investigate clogged heat exchangers or insufficient flue draft.

But my resolve never to jump a safety was tested today on a Viessmann Atola with a bad sequencer which is not really a safety. In this case, it allows the inducer fan to power on before ignition. The owners had no DHW, so I jumpered the sequencer to heat the indirect. I wanted to leave the jumper in place until the new part arrives, but I knew I would never get to sleep tonight.

What could go wrong?

8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

Two btu per sq ft for degree difference for a slab
Mad Dog_2

Comments

  • mattmia2
    mattmia2 Member Posts: 10,920

    it could blow up a little if the combustion chamber contains the right amount of gas. couldn't you just have got a sequencer?

    Mad Dog_2
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,467

    Alan,

    if I understand you correctly only the inducer would not start so you jumped 4 & 5 on the sequencer?

    If you did that the inducer will probably run 24/7. All the safety's for the burner are still in the circuit. No harm done at all.

    Part of the wiring diagram is chopped off but if the burner cycles on thermostat and the inducer runs all the time so what you can leave it that way until you get the part.

    I don't see any issue with doing that

    Mad Dog_2mattmia2
  • pecmsg
    pecmsg Member Posts: 5,290
    edited May 7

    Was taught in the UA classes if you're going to jump a Safety you get to stay and be the safety!

    Mad Dog_2HomerJSmithCLamb
  • Jamie Hall
    Jamie Hall Member Posts: 24,839

    Technically, if you jumpered four to five on the sequencer, that's not a safety in the usual sense. Rest easy,

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • I jumpered 1 and 3 and figured the fan would be on long enough to satisfy the pressure switch to remove any gas. The pressure switch is between 3 and the ignition control module, so there would be a short pre-purge.
    I’ve had very little experience with sequencers and didn’t know you could buy one off the shelf. It’s arriving tomorrow from Viessmann.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • mattmia2
    mattmia2 Member Posts: 10,920

    there are thoughts of an emergency mode for my ac to run off of generator involving a sequencer that starts the condenser then starts the furnace blower 10 seconds or so later after the compressor has had a chance to start but before it noticed a lack of load on the evaporator. I suppose I could do the same with the condenser fan and a 240 v sequencer.

  • Teemok
    Teemok Member, Email Confirmation Posts: 677

    I think that sequencer is there to provide A: delay the ignition module initiation for inducer pre-purge time. And B: inducer on hold after the call drops for post purge. Jumping 1 and 3 leaves the pressure switch as the ignition operator and shortens/eliminates the pre-purge delay. That's the risk. If there's a small gas leak or any source of combustibles around that build up and the ignition module is started before it's cleared out by the correct per-purge time, then it combusts in an undesired way. In a critical must run pinch, bad 1 - 3 contacts could be replaced with a delay on make device but factory parts are always the way to go. I agree with all that's said above, leave no jumpers in place.