lift fittings for condensate returns?
LILJohn
Member Posts: 4
How exactly do these things work ? I'm having a hard time conceptualizing how they function
0
Comments
-
Lift fitting?0
-
In order for water to go uphill in a condensate return line through a lift fitting, there has to be a difference in pressure between the low side and the high side.
I've never seen a lift fitting in a simple gravity system, so this needs to be a vacuum return system.
Simply put, the vacuum pump pulls a vacuum on the downstream (upper) side of the lift fitting. The vacuum pressure needs to be lower than the height of the water column height of the lift.
The higher pressure in the low return line pushes the condensate through the lift fitting and up the lift pipe.
If the higher return line is more than 10' in length, the lift pipe will have a loop over where it allows the lifted condensate to drop down into the higher return line.
To keep the low return completely drained of condensate, the lift fitting has to have a loop down first so the upstream low return line can be completely drained of condensate.
At one time, cast iron lift fittings were available, but not anymore, at least as far as I know.
The attached file goes into details about lift fittings, and show how a constructed lift fitting is assembled. Kind of complicated and labor intensive I think. I don't see why a common plumbers P trap wouldn't work just as well.
And the reason the lift pipe is 1/2 the size of the return line it to increase the velocity and provide a
more reliable and constant lift.
Also, keep in mind that in order for the lift to work, there has to be a pressure differential. When the vacuum pumps turns off or stops working due to too hot condensate, the pressure differential is lost so condensate fills up the low return line and now the whole return has a water seal and can't vent.
A lift fitting should never be substituted for a proper Auxiliary Accumulator Tank with vacuum relief valve, pressure vent line with check valve, and a float switch to activate the vacuum pump.Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.2 -
Is what you describe also called a siphon, Dennis?0
-
-
thank you dennis , it seems simple now lol0
-
I don't think so. If I understand the siphon principle correctly, the weight of the falling column of water on the downstream side creates the pressure differential for atmospheric pressure to push (lift) water on the upstream side.jumper said:Is what you describe also called a siphon, Dennis?
In a condensate lift application, a vacuum pump, and not a falling water column, is what creates the pressure differential.
Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.0
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements