Nest wiring question - No heat pump wire
www999
Member Posts: 1
I have a heat pump and the HVAC technician mentioned that I'm missing an orange wire, so he routed the green wire to the OB slot instead.
The current wiring configuration is:
Y1 - yellow wire
W1 - white wire
C - blue wire
Rh - red wire
OB - green wire
Both the heating and cooling functionalities work. However, I am not able to turn on just the fan. I live in a pretty vertical townhome so the upper levels are much hotter than the lower levels. I'd like to turn on just the fan to circulate the air.
Is there a way to do that with my current wires? I'm happy to sacrifice the auxiliary heating wire. I don't live in a very cold location so the auxiliary heat is not needed.
If that still doesn't work, is there a way to configure the wires for fan/heat in the winter and fan/AC in the summer?
Y1 - yellow wire
W1 - white wire
C - blue wire
Rh - red wire
OB - green wire
You could use the white wire for that and loose the auxiliary heat, or they make modules that can create an additional wire.Bob Boan
What is on the other end of those wires?
or
What does the air handler wiring look like?
It is quite possible that you have only 5 conductors.
18/2 is usually red and white
13/3 is usually red white and green
18/4 is usually red white green and yellow
18/5 is usually red white green yellow and blue.
Since that is the colors you have showing there is a possibility that you have one thermostat wire that has 5 conductors.
You can check the other end of the wire at the air handler without messing with the thermostat at the wall. See if there are more wires like perhaps a brown or orange wire that will be incliuded in the more popular 18/7 or 18/8 wires for heat pump thermostats.Edward Young Retired