Outdoor reset sensor
cheftim_2
Member Posts: 29
Good Afternoon,
I have a Buderus furnace with the 2107 controller installed and outdoor reset.
A couple weeks back it got a bit cold in the house and checked the reading of the outside air as seen by the outdoor reset sensor and read 84F when it was in the low 30's.
The controller saw that as Spring time and the warm weather shutdown went into effect.
I switched the controller from auto to winter to get heat back and now need to figure out why the bogus sensor reading.
Thinking the first place might be to verify connections on the controller and then ring out the wires to see if something broke. If that isn't the case, is the best next step to just replace the sensor and wiring or might there be some other troubleshooting steps first?
Thank you for any and all responses.
I have a Buderus furnace with the 2107 controller installed and outdoor reset.
A couple weeks back it got a bit cold in the house and checked the reading of the outside air as seen by the outdoor reset sensor and read 84F when it was in the low 30's.
The controller saw that as Spring time and the warm weather shutdown went into effect.
I switched the controller from auto to winter to get heat back and now need to figure out why the bogus sensor reading.
Thinking the first place might be to verify connections on the controller and then ring out the wires to see if something broke. If that isn't the case, is the best next step to just replace the sensor and wiring or might there be some other troubleshooting steps first?
Thank you for any and all responses.
0
Comments
-
The controller saw that as Spring time and the warm weather shutdown went into effect.Does the controller have a day and time setting!0
-
Most likely a bad connection somewhere.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
-
I would blame the groundhog....
0 -
You need to replace the outdoor sensor and check the wiring ......
There was an error rendering this rich post.
0 -
You can switch to manual .........
Set the dial to 160* with your 30* outside .......
The indirect water temperature will also reach 160* so be aware ...There was an error rendering this rich post.
0 -
Ohm out the sensor. Compare the ohm reading to the chart in the manual0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements