Question about pressure gauge
wheel
Member Posts: 5
Hello I have a couple of questions. If I install a 0 - 5 lb pressure gauge after the pigtail that runs to pressuretrol, I'm going to install a tee on top of the pigtail, mount the pressuretrol with a close nipple and run a short piece of pipe for the new gauge, will this work? The gauge will read the pressure? I'm having some issues with the pressuretrol not shutting off at the low cut out, .5 and diff of 1. The 0 - 30 boiler gauge is running up to 5 or so lbs and pressuretrol is not shutting it down. I checked everything on the boiler 8for clogging, couldn't find anything major. My system is a one pipe vented by the radiators, new boiler put in 7 years ago. I put some new valves, maid o mist, on all of them. Radiators get nice and hot. I don't know if the pressuretrol is bad or the 0- 30 boiler gauge is bad. I want to have a second lower rated gauge to check and see if pressure is somewhat correct or the boiler gauge is bad. Aiso the 0- 30 gauge is taking 20 min minimum to zero out, is that ok? Sorry for the state of this post, it's all over the place. Thanks for any replies
0
Comments
-
Pressure controls for boilers are not the most accurate devices. The more accurate controls are called vaporstats. As far as pressure gauges are concerned, the 0 to 30 gauge is a code requirement. They are also not the most accurate measuring devices for boilers. That said, you can add a vaporstat and a more accurate pressure gauge in order to dial in the boiler pressure.
https://www.supplyhouse.com/Honeywell-L408J1017-Vaporstat-Controllers-0-psi-to-4-psi
https://www.supplyhouse.com/sh/control/productComparison
By the Way, Is this the same steam boiler that you were talking about 14 years ago?
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
-
-
Yes the new gauge will read the pressure it sees
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Thanks to all who answered. I will recheck all parts for any possible issues and repost what happens. Thank you0
-
ed the heaterman, I went back down and checked the paperwork with the servicing data on it, yes my mistake I read off of the wrong line. It is the same boiler. I guess time is going by way faster then I can remember. It has been a good working system, no pipe knocking since that post. I didn't realize that my posts were under my account name, nice feature not having to search.1
-
Boring sermon...if you install a low range pressure gauge, provide an isolation valve and do not leave the gauge in service when unattended.
A few years ago I checked into the structural capability of gauges and the general answer is that they are good for 130% of full range. That means if you have a pressure excursion in your boiler above 6.5psig (relief valve is set at 15 psig), there could be a leak or worse.
0
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements