NYC Boiler Room ceiling must be sheet metal lined ?
Someone told me that lining the ceiling of a boiler room with sheet metal is a NYC code requirement for fire prevention - is that true?
Boiler is gas, 300k btu, multifamily building.
Comments
-
The Code may not specifically state "SHEET METAL" but there is a fire rating that must be followed. The code may say that the wall or ceiling must have a "2 hour rating" meaning that a boiler room fire must be contained within the room for a minimum of 2 hours. The builder or building design engineer or the contractor that is making the renovations to the existing building, should know if double layer of sheetrock or 5/8" sheetrock or a metal barrier between the ceiling and the framing or framing then sheetrock then sheet metal will meet with the code requirements.
Check with the authority having jurisdiction for clarification, and get it in writing if you can.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
2 -
I would think that would be in the building code0
-
Usually drywall is used to construct fire rated ceilings. Type X is "fire code" drywall and may be required. The thickness and number of layers are selected to make up the required fire rating in hours. This is all described in the building code.—
Bburd0 -
50/50 chance that will result in someone telling you where to put something with a brooklyn accent.EdTheHeaterMan said:The Code may not specifically state "SHEET METAL" but there is a fire rating that must be followed. The code may say that the wall or ceiling must have a "2 hour rating" meaning that a boiler room fire must be contained within the room for a minimum of 2 hours. The builder or building design engineer or the contractor that is making the renovations to the existing building, should know if double layer of sheetrock or 5/8" sheetrock or a metal barrier between the ceiling and the framing or framing then sheetrock then sheet metal will meet with the code requirements.
Check with the authority having jurisdiction for clarification, and get it in writing if you can.2 -
@mattmia2 In Jouisey we are a little nicer... not much but a little. But If you practice the trade below the Trenton Dixon line. you are in the south where it is pronounced JEr*sy not Jouisey then we are a lot nicer.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
2 -
Maybe. I would hope, optimist that I am, that the code requirement would be a performance, not a material, requirement.EBEBRATT-Ed said:I would think that would be in the building code
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
-
EdTheHeaterMan said:
The Code may not specifically state "SHEET METAL" but there is a fire rating that must be followed. The code may say that the wall or ceiling must have a "2 hour rating" meaning that a boiler room fire must be contained within the room for a minimum of 2 hours. The builder or building design engineer or the contractor that is making the renovations to the existing building, should know if double layer of sheetrock or 5/8" sheetrock or a metal barrier between the ceiling and the framing or framing then sheetrock then sheet metal will meet with the code requirements. Check with the authority having jurisdiction for clarification, and get it in writing if you can.
Thanks for the advice.
Yes I saw in the code the requirement for fire rating that can be achieved by using 5/8 drywall but others are telling me “no for sure you need a layer of sheet metal regardless of what you have above it” but maybe it’s just a case of people talking out of their azz.
Anyone know what the fire rating of wonder/cement board is? Asking because there is a bathroom above the boiler room ceiling and in case of any leaks upstairs I know wonder/cement board deals with water better than drywall.
0 -
The code will give you the required fire rating. The designer or builder will determine how to meet that rating. Some jurisdictions will adopt a particular code, and then have an amendment package that goes with it, so be sure to ask. This is a good resource for fire and sound-rated assemblies. https://www.usg.com/content/dam/USG_Marketing_Communications/united_states/product_promotional_materials/finished_assets/usg-fire-resistant-assemblies-catalog-en-SA100.pdf"If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
-
-
Panheadsforever said:Ask the inspector1
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements