Radiator bottom colder than top
Comments
-
I would check the radiator shutoff and vent ...
There was an error rendering this rich post.
0 -
The shutoff is fully open is there something else to check on it? The vent is 3 years old, will confirm if it opens and closes as it should.0
-
It would be normal for the top to be warmer than the bottom -- but it should be a lot warmer than that. Somehow it isn't getting the steam it needs or wants. As well as the valve (are you really sure it's fully open? Sometimes they get cranky...) but it also could be a restriction in the pipe leading to the radiator.
How hot is the feed pipe?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Remove the vent and see if the radiator gets hot. The valve handle seems low from here , why I mentioned it..
There was an error rendering this rich post.
0 -
Here's another picture of the valve just in case it actually does seem low. I'll try removing the vent, but I do hear hissing from the vent.0
-
I'll double check the temperature of the feed pipe. Good ideaJamie Hall said:It would be normal for the top to be warmer than the bottom -- but it should be a lot warmer than that. Somehow it isn't getting the steam it needs or wants. As well as the valve (are you really sure it's fully open? Sometimes they get cranky...) but it also could be a restriction in the pipe leading to the radiator.
How hot is the feed pipe?0 -
TonKa said:1
-
where is the vent on the radiator? is it on the left and encrusted in filth?0
-
Yes, middle left.0
-
I think the orifice that sets the vent rate unscrews from the top of those, you might want to unscrew it and make sure it is clear.0
-
I haven't seen Gorton vents with removable orifices. I could be mistaken, will double check.0
-
Either way make sure it hasn't sucked up all that crud around it.0
-
Is this something new or has it been like this for a while ? Is the insulation on the wall laying against the Radiator ? What is above the Radiator and below it , it looks like there's contact with mess underneath it...If air can't move , and the heat is getting absorbed by the insulation before it could get the cast iron hot I'd say there's a good chance your problem is simple...
Housekeeping and make sure the radiator isn't loosing what heat it's getting to the Insulation..
Just my thoughts by what I can see..
Other than whatelse that has already been mentioned by others that isOne way to get familiar something you know nothing about is to ask a really smart person a really stupid question0 -
Some further observations made. The valve is fully open, and vents are working fine; however, they don't stop hissing. Once I removed the radiator cover, I discovered the radiator itself is actually heating evenly and is 190 degrees all around. However, with the radiator cover installed, the top is hot to the touch and 130 degrees the bottom is cold and about 100 degrees. Could this cover be the issue and not allowing proper heat distribution form the radiator? I removed the insulation under the radiator just in case, but no changes in temperature. I also noticed the main only has a vent on the furthest end from the boiler. Since the vents don't stop hissing, I'm assuming one Gorton #2 isn't enough to vent this main? Also I discovered a portion of the return is cold. Is it possible there's a clog?
0 -
If you're measuring the temperature of that grate, that's not a surprising result. I think if you took the grate off you'd see the whole radiator (top to bottom) is more or less the same temp.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
This also isn't surprising. That is one weird piping arrangement you have (with possibly the highest, shortest "header" ever), but this section of pipe that you are measuring here isn't going to get any steam (nor likely anything else) so I'd expect it not to get hot
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
ethicalpaul said:If you're measuring the temperature of that grate, that's not a surprising result. I think if you took the grate off you'd see the whole radiator (top to bottom) is more or less the same temp.0
-
Yes, that is a very restrictive grate for sure. You might want something that has larger openings on the bottom and the top to make a chimney effect where the cool air is drawn in at the bottom and gets warmed, rises, and exits the top
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Covers block A LOT of heat - something like 40% or more. Additionally, because your cover is unpainted, somewhat shiny, and with a gap between it and the radiator, it is reflecting a good deal of radiant heat in the wrong direction. Just painting the backside of the cover and cutting a slot of one inch or so at the top and at the floor to allow for better air convection and would increase output... assuming the room needs it.0
-
@iizbor3d So the issue was that you were taking Heat measurements through the grating and when you checked it W/O grating the temperature was normal ( Hot ) ... ? Just seeing what was missed.. Glad you found it !One way to get familiar something you know nothing about is to ask a really smart person a really stupid question1
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements