How to correct short cycling on a residential steam boiler

Nycjs99
Nycjs99 Member Posts: 8
Steam boiler short cycling, causes

Comments

  • Nycjs99
    Nycjs99 Member Posts: 8
    What problems can a defective preasurertrol cause on a steam residential boiler cause
  • KC_Jones
    KC_Jones Member Posts: 5,827
    The question is a bit vague, but I’ll give it a shot.

    It depends how it’s defective. Is it defective that it’s not stopping the boiler at the safety cutoff pressure? If so it’s a potential safety concern in that the boiler can run out of control. In reality the thermostat would probably cut it off before any real problems occurred, but it should still be fixed.

    Is it defective in that it cuts off, but not at the pressure it’s set it’s set to? For me, not really a huge deal as they are known to be wildly off and not much to be done about it, a new one could have the same issue.

    The only other failure mode I can think of is it won’t let the boiler run, but I’m doubting that’s what you have because that one would be obvious.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    ethicalpaul
  • bigbillynyc
    bigbillynyc Member Posts: 4
    Change the pigtail and retest. Could be dirty
  • Nycjs99
    Nycjs99 Member Posts: 8
    My Weil mc claim GE-40 Pi steam boiler is short cycling when the thermostat is calling for heat.
    the preasuretrol is set at .05 psi with a #1 differential . The boiler short cycles at least 5 or 6 times before the thermostat is satisfied.
  • Nycjs99
    Nycjs99 Member Posts: 8

    The boiler is natural gas
  • Jamie Hall
    Jamie Hall Member Posts: 24,727
    There are so many causes... the most likely one is that the boiler is simply oversized -- possibly by quite a lot -- for the system. Nothing to be done about that. If the cycling begins before all the radiators are warm, it's also likely that the system does not have adequate main venting -- if it has any at all.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Nycjs99
    Nycjs99 Member Posts: 8
    With the thermostat calling for heat, the boiler seam to cut off at around 4 lbs , then the pressures goes down to a little above zero and the boiler starts up again, goes up to 4 lbs and shuts down on pressure, the the pressure goes down at just above 0 lbs and the boiler stars up again, it does that about 5 or 6 times before the thermostat is satisfied and shuts down the boiler
  • KC_Jones
    KC_Jones Member Posts: 5,827
    If it's short cycling after the mains are hot and the radiators are heating, the boiler is most likely too big and short of downsizing it, nothing you can really do except live with it.

    Oversizing iss one of the most common problems in this industry.

    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • Nycjs99
    Nycjs99 Member Posts: 8
    The pressuretrol is set ot .05 pai with a #1 set on the differential wheel, it seems to cut out and back in at the approximate psi, but it seem to short cycles . It cycles like 5 or 6 times before the thermostat is satisfied. My question is this normal.
    the pressure could be off to it is an older boiler though. 
    Ok and thank you for you help !
    charlie
  • ethicalpaul
    ethicalpaul Member Posts: 6,568
    edited February 16
    It's normal for an oversized boiler, which is indeed very common.

    The house needs heat, so the boiler wants to run. But the pressure control says "you can't run for awhile". Repeat until call for heat satisfied.

    But having said that, you should either fix or replace your pressure control because 4psi is WAY more pressure than you want. You should consider a vaporstat which can be set to a much lower cutout pressure.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Jamie Hall
    Jamie Hall Member Posts: 24,727
    duplicate thread, I think
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    ethicalpaul
  • Nycjs99
    Nycjs99 Member Posts: 8
    Thank you both for your reply, it is appreciated.
    best regards 
    Charlie S
  • Nycjs99
    Nycjs99 Member Posts: 8
    Thank You Paul,
    I was thinking of adding a vaporstat, what is the ideal setting? I’m  thinking .05 psi cut in and 1.5 psi on the cut out. What are you thoughts?
    Best Regards,
    Charlie
  • ethicalpaul
    ethicalpaul Member Posts: 6,568
    edited February 16
    Personally I would go much lower than that. I think the vaporstat lets you go to the ounces

    Keep in mind, and lowering of the cutout will increase your cycling. If you have a gas atmospheric it's not a big deal. If you have oil it might be a bigger deal, I don't know much about oil.

    You can also set up a timer circuit that makes the boiler rest longer after it starts building pressure, that's what I have. It's good, but it does increase the number of atmospheric "inhales" into the system when the steam collapses.

    Make sure your main venting is good, you want to put off the pressure as long as you can.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,400
    @Nycjs99

    If the boiler is oversized some on this forum have been experimenting with various timers to limit the short cycling with some success

    The idea is when the rads start to heat the timer shuts the burner down while the rads are giving off heat but the thermostat has not, yet been satisfied hoping the stored heat in the rads will satisfy the thermostat

    When the timer remakes contact and the stat is still calling the boiler fires again. The timer lengthens the time between cycles and cuts down the short cycling
  • ethicalpaul
    ethicalpaul Member Posts: 6,568
    Yes, it works great. We don't really "hope" that the stored heat in the rads will satisfy the thermostat, but if it happens to, then the call for heat ends.

    If it doesn't, then the boiler starts back up to provide more BTU into the house.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,312
    If we could know more about your boiler , there may be more we can suggest to reduce the number of cycles per call for heat. The make and model number of the boiler will help in that regard.

    Oil or Gas?

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • guzzinerd
    guzzinerd Member Posts: 276
    Personally I would go much lower than that. I think the vaporstat lets you go to the ounces Keep in mind, and lowering of the cutout will increase your cycling. If you have a gas atmospheric it's not a big deal. If you have oil it might be a bigger deal, I don't know much about oil. You can also set up a timer circuit that makes the boiler rest longer after it starts building pressure, that's what I have. It's good, but it does increase the number of atmospheric "inhales" into the system when the steam collapses. Make sure your main venting is good, you want to put off the pressure as long as you can.
    How low would you go?  I replaced the trol with a vaporstat at the start of this season and it's set at 1.5 and 0.5 psi. 

    Right now it calls for heat once or twice an hour and shuts down with the t-stat (set @ 69° prime time and 67°overnight)  between 0 and 1 psi. 
    Bryant 245-8 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains.  26 radiators heating up 3800sqf.
  • ethicalpaul
    ethicalpaul Member Posts: 6,568
    He did say it was gas in the other similar thread

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,312
    If you could use this chart to determine how much Radiation EDR you have by looking uo what your radiator looks like and counting the number of sections. there is a little math involved but if we know the EDR of your system, and the size of the boiler, that will answer a lot of questions.




    Sometimes it is difficult for someone to select what type of radiator they have from that chart above. This chart is intended for the professional that has encountered all kinds of radiators form many homes, so at a glance they can select the proper match. I have noticed some DIY folks on this site select the wrong radiator from this chart. To give you a guide to selecting the radiator from the chart that most represents your radiator, hear are some photos to help.


    To be sure you are counting the EDR correctly, we can help if you post pictures of your radiators.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • Erin Holohan Haskell
    Erin Holohan Haskell Member, Moderator, Administrator Posts: 2,354

    duplicate thread, I think

    I've merged these duplicate threads into one. Thanks!

    President
    HeatingHelp.com

  • 109A_5
    109A_5 Member Posts: 1,589
    Hello @Nycjs99,
    If there is nothing else wrong with your system like a plugged up pigtail, etc. And your are just dealing with a boiler size to EDR mismatch (oversized boiler). Just add an inexpensive timer in series with the pressuretrol or vaporstat. Excessive cycling whether is it at 5 PSI or 5 Ounces is excessive and can be eliminated or significantly reduced.

    https://www.supplyhouse.com/ICM-Controls-ICM203FB-ICM203F-Delay-on-Break-Timer-6-Wire-Leads-03-10-Minute-Knob-Adjust-Delay




    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System