How to correct short cycling on a residential steam boiler
Comments
-
What problems can a defective preasurertrol cause on a steam residential boiler cause0
-
The question is a bit vague, but I’ll give it a shot.
It depends how it’s defective. Is it defective that it’s not stopping the boiler at the safety cutoff pressure? If so it’s a potential safety concern in that the boiler can run out of control. In reality the thermostat would probably cut it off before any real problems occurred, but it should still be fixed.Is it defective in that it cuts off, but not at the pressure it’s set it’s set to? For me, not really a huge deal as they are known to be wildly off and not much to be done about it, a new one could have the same issue.
The only other failure mode I can think of is it won’t let the boiler run, but I’m doubting that’s what you have because that one would be obvious.1 -
Change the pigtail and retest. Could be dirty0
-
My Weil mc claim GE-40 Pi steam boiler is short cycling when the thermostat is calling for heat.
the preasuretrol is set at .05 psi with a #1 differential . The boiler short cycles at least 5 or 6 times before the thermostat is satisfied.0 -
The boiler is natural gas0 -
There are so many causes... the most likely one is that the boiler is simply oversized -- possibly by quite a lot -- for the system. Nothing to be done about that. If the cycling begins before all the radiators are warm, it's also likely that the system does not have adequate main venting -- if it has any at all.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
With the thermostat calling for heat, the boiler seam to cut off at around 4 lbs , then the pressures goes down to a little above zero and the boiler starts up again, goes up to 4 lbs and shuts down on pressure, the the pressure goes down at just above 0 lbs and the boiler stars up again, it does that about 5 or 6 times before the thermostat is satisfied and shuts down the boiler0
-
If it's short cycling after the mains are hot and the radiators are heating, the boiler is most likely too big and short of downsizing it, nothing you can really do except live with it.
Oversizing iss one of the most common problems in this industry.
0 -
The pressuretrol is set ot .05 pai with a #1 set on the differential wheel, it seems to cut out and back in at the approximate psi, but it seem to short cycles . It cycles like 5 or 6 times before the thermostat is satisfied. My question is this normal.
the pressure could be off to it is an older boiler though.Ok and thank you for you help !
charlie0 -
It's normal for an oversized boiler, which is indeed very common.
The house needs heat, so the boiler wants to run. But the pressure control says "you can't run for awhile". Repeat until call for heat satisfied.
But having said that, you should either fix or replace your pressure control because 4psi is WAY more pressure than you want. You should consider a vaporstat which can be set to a much lower cutout pressure.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
Thank you both for your reply, it is appreciated.
best regards
Charlie S0 -
Thank You Paul,
I was thinking of adding a vaporstat, what is the ideal setting? I’m thinking .05 psi cut in and 1.5 psi on the cut out. What are you thoughts?
Best Regards,
Charlie0 -
Personally I would go much lower than that. I think the vaporstat lets you go to the ounces
Keep in mind, and lowering of the cutout will increase your cycling. If you have a gas atmospheric it's not a big deal. If you have oil it might be a bigger deal, I don't know much about oil.
You can also set up a timer circuit that makes the boiler rest longer after it starts building pressure, that's what I have. It's good, but it does increase the number of atmospheric "inhales" into the system when the steam collapses.
Make sure your main venting is good, you want to put off the pressure as long as you can.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
@Nycjs99
If the boiler is oversized some on this forum have been experimenting with various timers to limit the short cycling with some success
The idea is when the rads start to heat the timer shuts the burner down while the rads are giving off heat but the thermostat has not, yet been satisfied hoping the stored heat in the rads will satisfy the thermostat
When the timer remakes contact and the stat is still calling the boiler fires again. The timer lengthens the time between cycles and cuts down the short cycling0 -
Yes, it works great. We don't really "hope" that the stored heat in the rads will satisfy the thermostat, but if it happens to, then the call for heat ends.
If it doesn't, then the boiler starts back up to provide more BTU into the house.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
If we could know more about your boiler , there may be more we can suggest to reduce the number of cycles per call for heat. The make and model number of the boiler will help in that regard.
Oil or Gas?Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
ethicalpaul said:Personally I would go much lower than that. I think the vaporstat lets you go to the ounces Keep in mind, and lowering of the cutout will increase your cycling. If you have a gas atmospheric it's not a big deal. If you have oil it might be a bigger deal, I don't know much about oil. You can also set up a timer circuit that makes the boiler rest longer after it starts building pressure, that's what I have. It's good, but it does increase the number of atmospheric "inhales" into the system when the steam collapses. Make sure your main venting is good, you want to put off the pressure as long as you can.
Right now it calls for heat once or twice an hour and shuts down with the t-stat (set @ 69° prime time and 67°overnight) between 0 and 1 psi.Bryant 245-8 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators heating up 3800sqf.0 -
He did say it was gas in the other similar thread
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
If you could use this chart to determine how much Radiation EDR you have by looking uo what your radiator looks like and counting the number of sections. there is a little math involved but if we know the EDR of your system, and the size of the boiler, that will answer a lot of questions.
Sometimes it is difficult for someone to select what type of radiator they have from that chart above. This chart is intended for the professional that has encountered all kinds of radiators form many homes, so at a glance they can select the proper match. I have noticed some DIY folks on this site select the wrong radiator from this chart. To give you a guide to selecting the radiator from the chart that most represents your radiator, hear are some photos to help.
To be sure you are counting the EDR correctly, we can help if you post pictures of your radiators.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
I've merged these duplicate threads into one. Thanks!Jamie Hall said:duplicate thread, I think
President
HeatingHelp.com0 -
Hello @Nycjs99,
If there is nothing else wrong with your system like a plugged up pigtail, etc. And your are just dealing with a boiler size to EDR mismatch (oversized boiler). Just add an inexpensive timer in series with the pressuretrol or vaporstat. Excessive cycling whether is it at 5 PSI or 5 Ounces is excessive and can be eliminated or significantly reduced.
https://www.supplyhouse.com/ICM-Controls-ICM203FB-ICM203F-Delay-on-Break-Timer-6-Wire-Leads-03-10-Minute-Knob-Adjust-Delay
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements