Steam Air vent
Options
mmc239
Member Posts: 81
What size steam air vent should I put on a steam baseboard located right above the boiler. The baseboard bangs a lot on start up. Should I use a valve with a bigger whole to get the air out of baseboard?
0
Comments
-
Smaller hole. The vent isn't the cause of the banging. It's much more likel to be that the baseboard isn't pitched properly -- it needs a really good pitch (I'd want at least an inch, even for a short baseboard, and maybe more) to the drain, or the pipe feeding it isn't pitched properly (half an inch per foot isn't excessive).Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
I have pitched it. Shut off valve is open completely. I have tried everything. It bangs on startup, then quiets down. I have tried Varivalve, water just shoots out of them. Hoffman, some water spits out, sometimes air would not bleed out of it and radiator would be cool. Right now I have Maid o mist, it seems to be the best for not spitting water.0
-
It's not the vent. It's as Jamie says, there's something about your system that is putting that water there.
One or more of:
- pitch of the convector/baseboard
- pitch of the supply pipe to the convector/baseboard
- near boiler piping being all fouled up, causing surging
- water quality being poor (dirty or oily), causing surging
NJ Steam Homeowner. See my sight glass boiler videos: https://bit.ly/3sZW1el0
Categories
- All Categories
- 85.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 49 Biomass
- 424 Carbon Monoxide Awareness
- 72 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 848 Plumbing
- 5.8K Radiant Heating
- 372 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 50 Water Quality
- 48 Industry Classes
- 47 Job Opportunities
- 15 Recall Announcements