New Steam Radiator Causing Water Hammer
The radiator I had replaced was cracked and the supply valve was closed for at least 4 years, would it be possible because the valve was closed for so long it is causing this issue?
If I drain the boiler and then run the heat, the water hammer disappears, but will return in the after about three heating cycles.
The rest of the radiators in the house heat up fine and so does the new radiator, which is pitched plenty. The supply valve is fully open but it sounds like the water is having issues trying to leave the new radiator. When I close the supply valve to the new radiator, the water hammer does not happen.
Any suggestions or advice will be greatly appreciated.
Comments
-
-
Yes, I even checked it with a level, it’s definitely pitched correctly. Possibly could try to get a few more shims under. The plumber originally had a varivalve adjustable vent but I went to Home Depot as I wanted to change it asap and picked up their standard angle #4.0
-
-
EBEBRATT-Ed said:What do you mean by "If I drain the boiler the water hammer disappears but returns after a few cycles"??? How is the water level in the boiler? Is it surging or bouncing more than 1"?The water level is fine, not surging0
-
Was a new supply valve and spud installed with the new radiator? If the old valve was reused with a new spud that could be the problem. Can you take a picture of the valve? If it was replaced it may be that a hot water supply valve was installed instead of steam and the valve body isn’t wide enough to allow condensate to drain beneath incoming steam. Could also be too small of a supply valve and spud into the radiator causing the same condensate traffic jamb.1
-
New spud and valve0
-
You have a pipe somewhere that is pitched incorrectly, and holding water. That's what's causing the hammer. That incorrectly pitched pipe could be why the valve was close in the first place, to stop the hammer. What floor is this radiator on?Miss Hall's School service mechanic, greenhouse manager,teacher and dog walker1
-
Grallert said:You have a pipe somewhere that is pitched incorrectly, and holding water. That's what's causing the hammer. That incorrectly pitched pipe could be why the valve was close in the first place, to stop the hammer. What floor is this radiator on?0
-
Grallert said:You have a pipe somewhere that is pitched incorrectly, and holding water. That's what's causing the hammer. That incorrectly pitched pipe could be why the valve was close in the first place, to stop the hammer. What floor is this radiator on?Is there anyway I can fix the pitched pipe myself?0
-
Assuming the takeoff to the radiator is counterflow then raising the entire radiator (while maintaining proper pitch) is your easiest means of impacting the pitch in a positive manner.0
-
dabrakeman said:Assuming the takeoff to the radiator is counterflow then raising the entire radiator (while maintaining proper pitch) is your easiest means of impacting the pitch in a positive manner.0
-
The pipe up through the floor into the shut off valve either was pulled up or sagged down creating a ponding of water in the main. You’re going to have to keep the radiator pitched to drain to the valve while trying to raise or lower the entire radiator with along with the valve to adjust the height of the main below to have the proper pitch. Or find the sag in the main and put a clevis hanger on it to pull the pipe up to the correct pitch.1
-
Here are some pics of the line that run to new radiator. Does anything stand out?0
-
Make sure all the pipes on the basement have the right pitch first, the new work might have shifted the piping.
The fact your problem comes back a while after draining the boiler tells me you may have oil in tour boiler water and that means it needs to be skimmed. The new work probably introduced oil into the system.
It's free to try if your boiler has a skim port installed.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge1 -
BobC said:Make sure all the pipes on the basement have the right pitch first, the new work might have shifted the piping. The fact your problem comes back a while after draining the boiler tells me you may have oil in tour boiler water and that means it needs to be skimmed. The new work probably introduced oil into the system. It's free to try if your boiler has a skim port installed. Bob0
-
That appears to be a counteflow main. Is that main vent the end of all the piping? If so it's definitely a counerflow and I'd be inclined to verify the pitch of the main to make sure that isn't the issue here.
If it is a counterflow, that vent location should be the highest point on that entire pipe run all the way back to the boiler.0 -
KC_Jones said:That appears to be a counteflow main. Is that main vent the end of all the piping? If so it's definitely a counerflow and I'd be inclined to verify the pitch of the main to make sure that isn't the issue here. If it is a counterflow, that vent location should be the highest point on that entire pipe run all the way back to the boiler.0
-
If you close the valve steam will not enter that radiator or much of the pipe that feeds it. If the slope is not very good on the piping that deeds that radiator it would be more likely to hammer.
If you try skimming and it helps your going the right direction, if it doesn't work you have crossed a possibility off the list and cost yourself nothing.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge1 -
BobC said:If you close the valve steam will not enter that radiator or much of the pipe that feeds it. If the slope is not very good on the piping that deeds that radiator it would be more likely to hammer. If you try skimming and it helps your going the right direction, if it doesn't work you have crossed a possibility off the list and cost yourself nothing. Bob0
-
We have skipped the most important step. I think. You need to check the pitch of every single pipe leading to that radiator.0
-
STEAM DOCTOR said:We have skipped the most important step. I think. You need to check the pitch of every single pipe leading to that radiator.1
-
I open the new radiator yesterday morning after the heat had already started and it worked all day yesterday perfectly fine, no water hammer. This morning the water hammer returned about 15 minutes after the heat turned on after being off for about 8 hours. Could this do with the lines being cold? Would insulating the lines help at all?NewJerseyHeatHelp said:BobC said:If you close the valve steam will not enter that radiator or much of the pipe that feeds it. If the slope is not very good on the piping that deeds that radiator it would be more likely to hammer.
If you try skimming and it helps your going the right direction, if it doesn't work you have crossed a possibility off the list and cost yourself nothing.
Bob
What was off for 8 hours? The heating system as a whole, or did you turn that one radiator off with the inlet valve?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Jamie Hall said:
What was off for 8 hours? The heating system as a whole, or did you turn that one radiator off with the inlet valve?BobC said:If you close the valve steam will not enter that radiator or much of the pipe that feeds it. If the slope is not very good on the piping that deeds that radiator it would be more likely to hammer. If you try skimming and it helps your going the right direction, if it doesn't work you have crossed a possibility off the list and cost yourself nothing. BobMy gut feeling says it has to do something with the supply line. It seems to be pitched correct, I can only access about 3 out of the 10 feet of it since the majority of the pipe runs behind a wall.This supply line is probably double the length of any of the other lines that run to the other radiators, not sure if that means I have to do anything differently to the new radiator (different vent (slower/faster?), more/less pitch?)0 -
-
Jamie Hall said:It may be that the supply line is either too small for the size of the radiator, or has inadequate pitch. How big (EDR) is this radiator?0
-
Why is the vent in the hot water bleed valve location?Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0
-
delcrossv said:Why is the vent in the hot water bleed valve location?0
-
Other have said vent in wrong location . If a plumber did this then he does not know much about steam systems being he installed the vent in the wrong location . There should be an Allen key screw about 2/3 of the way up . Remove the vent and re locate and install the Allen set screw where your vent is currently . The banging issue your having may have to do w one of two things the set back on the thermostat and possibly the supply pipe size to the edr of the radiator . If the radiator is over sized for the riser then you could be under feeding the rad which will cause more condensate to form then the radiator will drain . If this is a replacement radiator was it sized larger then the original one which was there ? What size vent is one the radiator possibly over venting the radiator . I also see there s no insulation on your steam piping for a counter flow system dry steam is extremely important and if your boiler is poorly piped and uninsulated steam mains well it does not help things . Possible see if you can raise the whole radiator and also pitch it back to the supply valve . Start off by putting that vent in the correct place . Vents installed on the top side of a radiator does not speed the heating only lets about 1/2 the rad get hot before the vent closes .
Peace and good luck clammyR.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating0 -
I've seem to strip the lower allen key head this morning before work (i should have waited until i was fully awake), after I get it out, would I be able to use a 1/8 in. MIP Plug Fitting in the higher vent since i wont be able to relocate it?clammy said:Other have said vent in wrong location . If a plumber did this then he does not know much about steam systems being he installed the vent in the wrong location . There should be an Allen key screw about 2/3 of the way up . Remove the vent and re locate and install the Allen set screw where your vent is currently . The banging issue your having may have to do w one of two things the set back on the thermostat and possibly the supply pipe size to the edr of the radiator . If the radiator is over sized for the riser then you could be under feeding the rad which will cause more condensate to form then the radiator will drain . If this is a replacement radiator was it sized larger then the original one which was there ? What size vent is one the radiator possibly over venting the radiator . I also see there s no insulation on your steam piping for a counter flow system dry steam is extremely important and if your boiler is poorly piped and uninsulated steam mains well it does not help things . Possible see if you can raise the whole radiator and also pitch it back to the supply valve . Start off by putting that vent in the correct place . Vents installed on the top side of a radiator does not speed the heating only lets about 1/2 the rad get hot before the vent closes .
Peace and good luck clammy
The new radiator is about 6 inches taller than the previous one but the same length and width.
The issues only seem to happen on a "cold" start, when the boiler starts up in the morning at 6 am after being off from about 10 am? Could it be since the supply lines are warming so quickly and the pipes being cold its producing extra condensate? i'm assume insulating could help with that? When the supply valve is closed at this radiator, the system works perfectly normal.0 -
"I've seem to strip the lower allen key head this morning before work (i should have waited until i was fully awake), after I get it out, would I be able to use a 1/8 in. MIP Plug Fitting in the higher vent since i wont be able to relocate it?"
Correct.
"The issues only seem to happen on a "cold" start, when the boiler starts up in the morning at 6 am after being off from about 10 am? Could it be since the supply lines are warming so quickly and the pipes being cold its producing extra condensate? i'm assume insulating could help with that? When the supply valve is closed at this radiator, the system works perfectly normal."
Insulation and correct pitch. Cold start leads one to think there's not sufficient pitch to get the condensate out of the pipe.Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
Looking at your radiator picture I’ll suggest instead of all the shims stacked how about this .
First disconnect the radiator from the supply valve and slide the radiator over alittle . See if the supply valve can be lifted up if so figure out about how height it can go to keep the valve lifted .Instead of stacking shims go get a piece of wood say a 2 x4 cut a few inches wider then your radiator and use that to get the radiator at the correct height maintaining and possibly increasing the pitch on that supply line . Aside from the air vent in the wrong location I would think the hammering really has to due w the difference in the replacement radiator height to the original rad.
Peace and good luck clammy
R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating0 -
If steam condensate too rapidly in the riser, what about venting that radiator more slowly?0
-
Sylvain said:If steam condensate too rapidly in the riser, what about venting that radiator more slowly?0
-
Back to basics. Water hammer in a steam system can only occur where sufficient water can build up in a near horizontal pipe to be pushed into a wave shape by the steam or air going by, and then that wave can be propelled along the pipe to where it hits a bend (either horizontal or vertical) and stops. Bang.
So the three necessary ingredients are enough condensate, enough velocity, and a stretch where the condensate can pool enough to form into a wave.
So... is the pipe big enough to handle the steam flow at a reasonable velocity? That's why runouts are sized based on the EDR they feed. Is the pipe slope constant -- no flatter stretches, never mind sags -- and adequate to allow the condensate to flow in a very shallow stream?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Back to basics. Water hammer in a steam system can only occur where sufficient water can build up in a near horizontal pipe to be pushed into a wave shape by the steam or air going by, and then that wave can be propelled along the pipe to where it hits a bend (either horizontal or vertical) and stops. Bang.
It's not the sudden collapse of steam coming into contact with cool water causing a vacuum that then causes an inrush of air that propels the water? I don't think the velocity of normal flowing steam from a boiler would cause water to slam into a pipe to cause a bang but I've been wrong before.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Honestly the mathematics is more than I want to mess with at the moment. However... let's consider a conservative velocity for steam (or air) moving in a pipe. 20 feet per second. That's about 12 miles per hour -- a stiff breeze. Have you ever observed the waves on a pond at that wind speed? They can build up to a pretty good sized ripple. Put that ripple in a pipe, and it can block a good fraction of the pipe -- and be pushed along by our friendly breeze. That's what's happening.
But... but.. even a well vented system doesn't heat 20 feet of main or runout that fast? No, it doesn't, and the reason is that the advancing steam front has to heat the pipe first, and that takes time (and builds up condensate which, we hope, can drain away...). So eventually the pipe is hot, the steam is whipping along, and -- if the condensate didn't drain away in time, we get waves. If we are lucky, we get one. If we are less lucky, we get successive waves until all the condensate has managed to drain away and the banging stops. If we are really less lucky and have a counterflow situation, that doesn't happen -- and the banging just keeps right on going until the boiler shuts off.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Thanks Jamie I'm with you on all of what you wrote except how a breeze can slam water into a pipe that sounds like a hammer hitting it.
that's why I'm in the "steam collapse vacuum" campNJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
I think you're both correct.. as there is more than one way to create water hammer. One is just more powerful than the other.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements