Heat is Off - Goodman MES80
SlowYourRoll
Member Posts: 187
in Gas Heating
Hello friends, the heat is off at my girlfriend's house. Gas fired furnace. Goodman brand, model MES80. The control board has an LED that flashes to indicate the error, and it's flashing 4 times, so I took a pic of the manual's description (see below), but basically it sounds like it's related to an insufficient amount of air blowing over the heat exchanger, which it determines by temperature limit switches. The burners aren't turning on, but I'm guessing that's because it is running and failing this check prior to ignition.
I replaced the air filter attached to the furnace and the two air filters on the return vents on the first and second floor. I couldn't find a return vent in the basement (it's a finished basement with heat vents). I thought there'd be a return vent for the basement but I'm not a pro, so maybe that's normal? Anyway, the house has brand new filters and still no heat.
My girlfriend mentioned that a previous tech said the blower was improperly sized for the vents in the house, and so the blower speed had to be adjusted to keep something from overheating (I'm guessing the heat exchanger?).
It's also really dirty inside the furnace (she hadn't changed the air filters in the 2 years she's lived here), so I'm wondering if maybe a coating of dust is interfering with the temp sensors that the limit switch uses.
I'm pretty handy in general but not an HVAC pro. We've got a few calls out to pros in the area to see if anyone can fix it tonight. In the meantime I wanted to see if there's anything I didn't think of that's worth a try.
I replaced the air filter attached to the furnace and the two air filters on the return vents on the first and second floor. I couldn't find a return vent in the basement (it's a finished basement with heat vents). I thought there'd be a return vent for the basement but I'm not a pro, so maybe that's normal? Anyway, the house has brand new filters and still no heat.
My girlfriend mentioned that a previous tech said the blower was improperly sized for the vents in the house, and so the blower speed had to be adjusted to keep something from overheating (I'm guessing the heat exchanger?).
It's also really dirty inside the furnace (she hadn't changed the air filters in the 2 years she's lived here), so I'm wondering if maybe a coating of dust is interfering with the temp sensors that the limit switch uses.
I'm pretty handy in general but not an HVAC pro. We've got a few calls out to pros in the area to see if anyone can fix it tonight. In the meantime I wanted to see if there's anything I didn't think of that's worth a try.
0
Comments
-
CORRECTION: my girlfriend read the post and wants everyone to know she's only lived here one year0
-
-
-
-
Thanks Jamie! I think they are automatic reset. Here's what the manual says...0
-
0 -
pecmsg said:That system is filthy!
the blower wheel is cacked in dust.It needs to be taken out and throughly cleaned.0 -
You can do a lot on the cleaning yourself. I'd use a shopvac, but even your normal vacuum will do.
On the limits -- if it is telling you that one or the other is open -- but since they are automatic reset, that tells you that one or the other of them is lying to you. It may just be a bad connection -- they happen -- or it could be that it may need replacement.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
-
@SlowYourRoll
It sounds like a limit is open. Get a piece of scrap wire and look at the wiring diagram trace the wires and try jumping the limits one at a time.
You may be able to find which limit is open. Then you will know what to replace. Do not leave it jumped or run it that way you could have a fire. The furnace needs service asap.1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements