Simplest way to test a rad

Tommi68
Tommi68 Member Posts: 46
Before I swap in a used rad from my storage, how do you all pressure test yours? I have no documentation on the replacement rad in question, so I am not certain why it was removed from service. It probably became surplus during a renovation but I would like some certainty. It is a 6 element, two pipe rad with no bleed, so I don't think I can water test it.
What do you do?

Comments

  • Jells
    Jells Member Posts: 576
    Never done it, but I'd test it like a gas line, air pressure with a gauge and ball valve to lock it off. Put in 60psi and see if it leaks out.
  • TomS
    TomS Member Posts: 66
    A hydrostatic test with water would be the safest way to do this. Testing an unknown vessel with air could be very dangerous if a section were to break away.
  • Big Ed_4
    Big Ed_4 Member Posts: 3,019
    It would be best to replace with New , cheaper then surplus ....

    There was an error rendering this rich post.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,477
    There is no reason you can't test with water. I would not go over 30psi.

    If you can't vent the air out due to no bleeder turn the rad upside down.
    Tommi68
  • Steamhead
    Steamhead Member Posts: 17,380
    TomS said:

    A hydrostatic test with water would be the safest way to do this. Testing an unknown vessel with air could be very dangerous if a section were to break away.

    This.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    Tommi68
  • Jamie Hall
    Jamie Hall Member Posts: 24,856
    If it has openings, you can get water into it. And out of it. Use water, as said at not over 30 if it's to be a hot water radiator, 15 psi for steam.

    Do NOT use compressed air! Do you have any idea how far the shrapnel would go if it broke at 60 psi?
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    ethicalpaul
  • Jells
    Jells Member Posts: 576
    TomS said:

    A hydrostatic test with water would be the safest way to do this. Testing an unknown vessel with air could be very dangerous if a section were to break away.

    You're right, I wasn't thinking.
  • Tommi68
    Tommi68 Member Posts: 46
    Thanks for the advice. The rad is small enough to lay on its side to vent trapped air. 
    I am presuming that I will fill it with water then add a small volume of compressed air to reduce the capacity for a catastrophic failure.