running circulator pump independently of electric boiler

lauriel
lauriel Member Posts: 3
It's a 4 lop system with a 4.5 kw thermo 2000 unit. I want to run the pump to even out the temperature in the slab. I only need the boiler when I am away. The solar input from the south window plus the cooking woodstove are keeping the house at the right temperature . I would like to run the pump to even out the heat gain through the slab from these 2 sources. What device could make it that the input from the boiler to the pump can activate the pump while disabling the manual or intermittent activator to the pump so that there is only 1 power source at a time at the pump? Also is it better to run the pump on constantly or intermittently?

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,954
    edited January 2024
    Interesting concept. The easiest thing I can think of is to disconnect the wire that goes to the pump. Place a female 120V receptacle (for repairing extension cords) on that wire. Get an extension cord and cut off the female end. Wire the cut off end to the circulator. Then just plug the circulator into a wall receptacle. The pump will run as long as it is plugged in to the wall. If you ever want to go back to automatic operation, just plug it into the wire from the boiler that now has the female receptacle.

    Easy Pezzy!

    Or we could design you a $1000+ control system with a relay and a switch, that can talk to the internet so you can do it from your smart phone, that will do the same thing with the push of a button. Just Ask @Jamie Hall

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    WMno57
  • Jamie Hall
    Jamie Hall Member Posts: 25,457
    Power the pump independently in parallel with the boiler. I presume that the present arrangement has the boiler turn on the pump when the boiler turns on? The safest way to wire this will be to have the pump wired with a manual switch and, in parallel with that, a relay. The present control from the boiler to the pump would activate the relay, which in turn would activate the pump with no risk of an electrical connection between the two, and then the pump would run when either the manual switch was on or the boiler was on.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • hot_rod
    hot_rod Member Posts: 24,212
    4 loops in a single zone?
    This is a simple, true, constant circ option. Zone pump runs constantly throughout the heating season.
    When the thermostat calls for heat the 3 way opens to the boiler and fires it on.

    An ECM as the zone pump reduces power consumption, Mine runs 24W all season.

    This works good in homes with radiant floor slabs that get a a lot of solar gain, moves that warm temperature throughout the zone.

    Outdoor reset can get you close to constant circulation also.

    You would have the boiler in place of the sep in this pic.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • lauriel
    lauriel Member Posts: 3
    Thanks a lot Ed Jamie and Hot rod, three very good ways.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,065
    Why not just put a 3 way switch or a relay with a single pole switch to bypass the boiler control. Flip the switch back to "boiler" when you go away.
  • jumper
    jumper Member Posts: 2,404
    I believe that motor and pump last longer if they stop/start less. That is worth electric cost for me.