Boiler losing water
Kjmass1
Member Posts: 266
I have a 1970’s Penco steam boiler that was serviced and running at 82.5% last year. Never has any issues. Seems like I’m losing about 2” of water from the sight glass each week…seems like a lot? Doing about 15 cycles of 25 minutes each per day. Anything to be concerned with?
0
Comments
-
Yes indeed. While that is not outrageous, you really shouldn't be losing much if any. That water is going somewhere, and that's not good. There are many possible sources of a leak, and you should start looking for them. Likely culprits are wet returns -- but at that age, unhappily the boiler itself is also a likely culprit. Equally unhappily, so long as it is cold outside, finding a boiler leak can be difficult -- since the water tends to evaporate.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Either the boiler is leaking, a vent somewhere is leaking, or a return is leaking. Have you noticed any water damage or moisture anywhere in your home?0
-
Jamie Hall said:Yes indeed. While that is not outrageous, you really shouldn't be losing much if any. That water is going somewhere, and that's not good. There are many possible sources of a leak, and you should start looking for them. Likely culprits are wet returns -- but at that age, unhappily the boiler itself is also a likely culprit. Equally unhappily, so long as it is cold outside, finding a boiler leak can be difficult -- since the water tends to evaporate.Don’t see anything around the radiators or the valves either.Only change from last year was I turned in my attic radiator- it’s finished and partially used, but the extra edr helps the boiler recover from small setbacks without hissing. I’m going to shut that one off for this week and see if that helps.0
-
Hello, @Kjmass1,
Any excessive white looking exhaust out of the chimney ?
You could let the boiler cool down and then flood just the boiler and see if it leaks. Then return the water level to normal before use.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
109A_5 said:Hello, @Kjmass1, Any excessive white looking exhaust out of the chimney ? You could let the boiler cool down and then flood just the boiler and see if it leaks. Then return the water level to normal before use.0
-
helps the boiler recover from small setbacks without hissing
Regardless of the EDR, your boiler shouldn't be hissing. Depending on where and when you are hearing this hissing, this could be the source of your water lossNJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Just looked at the start of this cycle and there is white coming out of the chimney…not sure if it is excessive. It’s 28F outside and snowy.Kjmass1 said:
This is not good. It can be difficult to gauge what is or is not excessive, but an oil fired boiler should have very little, and rather wispy, smoke which dissipates quickly, even in humid air. I'm thinking leak in the boiler... but I'd also check that radiator you just turned on.
One thing about leaks. If it is a steam leak, say from a vent not sealing all the way or leaks around a valve stem, you won't see it. The steam will evaporate very rapidly. A cold mirror near the possible location may, however, show moisture. And you re not looking at a lovely puddle. One drip every ten seconds is a gallon or so per day -- and will, in most cases, dry out without showing much.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Jamie Hall said:
This is not good. It can be difficult to gauge what is or is not excessive, but an oil fired boiler should have very little, and rather wispy, smoke which dissipates quickly, even in humid air. I'm thinking leak in the boiler... but I'd also check that radiator you just turned on. One thing about leaks. If it is a steam leak, say from a vent not sealing all the way or leaks around a valve stem, you won't see it. The steam will evaporate very rapidly. A cold mirror near the possible location may, however, show moisture. And you re not looking at a lovely puddle. One drip every ten seconds is a gallon or so per day -- and will, in most cases, dry out without showing much.109A_5 said:Hello, @Kjmass1, Any excessive white looking exhaust out of the chimney ? You could let the boiler cool down and then flood just the boiler and see if it leaks. Then return the water level to normal before use.
I mentioned the extra radiator and EDR as my boiler is very oversized compared to the connected radiation. It’s perfectly silent and even unless coming out of a setback of a degree or two. What’s the significance of the white smoke- poorly burning? Same for nat gas?0 -
ethicalpaul said:helps the boiler recover from small setbacks without hissingRegardless of the EDR, your boiler shouldn't be hissing. Depending on where and when you are hearing this hissing, this could be the source of your water loss0
-
Normally there is some moisture in the exhaust gas. If the boiler's heat exchanger is compromised above the water line some of the steam goes up the chimney instead of heating your home.Kjmass1 said:What’s the significance of the white smoke- poorly burning? Same for nat gas?
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Looks like I’m losing about the same amount of water with that radiator shut off…sounds like I need to call someone in.0
-
Does any of the return piping run underground or the supply run through a crawl space? If so, that is should be investigated.0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 51 Biomass
- 419 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 922 Plumbing
- 6.1K Radiant Heating
- 375 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 16 Recall Announcements