Issue with conquest 80

Hi i have conquest 80 furnace    whenever the unit is turned on  even with the thermostat wiring disconnected   after a minute or so the draft inducer powers on and 10 to 30 seconds later the main blower starts and both remain running until you kill power to the furnace    


On the control pcb the ok and power leds are in continuously 

The flame led is off to start  then the draft inducer then after a delay it starts slow flashing  for about 6 seconds when it then starts fast flashing with the indoor blower starting

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,878
    and so what is the problem?
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Ironman
    Ironman Member Posts: 7,555
    Sounds like you have an open limit or flame rollout switch.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.