Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Steam Boiler not turning on
Dolphino
Member Posts: 5
Hello everyone, so I cleared out the dirty water from my steam boiler. 10 minutes later, the boiler just turned off with no single. I tried to turn it off and on after a few minutes and no single at all. Any suggestions for fixing it?
It's a Weil mclain eg/peg50pidn s5
It's a Weil mclain eg/peg50pidn s5
0
Comments
-
10 minutes, the sort of sounds like the safeguard low water cut off. Did it come back on?0
-
Where is the water level in the sight glass?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
yeah, but, why is the VXT dark?
Is the power on ?
any other lights lit up on the boiler?
jiggle the service switch?
or the breaker?
give us a picture of what you have there besides the water feeder.known to beat dead horses0 -
neilc said:yeah, but, why is the VXT dark? Is the power on ? any other lights lit up on the boiler? jiggle the service switch? or the breaker? give us a picture of what you have there besides the water feeder.0
-
-
ok, he didn't "Jump" anything to make it work?, did he?known to beat dead horses0
-
Probably the “switch at the top of the stairs”
An oldie but goodie1
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements