Took these images from the front of my boiler. Not sure if the images help. I don't have equipment to check the Amp draw. I read that for steam boilers, the anticipator should always be set to 1.2 (see image attached). My bills seem unusually high and I want to make sure it's running in the most efficient manner. Using old round thermostat. Thanks
0
Comments
-
Hello @abcaldwell,
Back many decades ago when steam heat was going from Coal to Natural Gas the Gas Valve drew a lot more current which would burn up the heat anticipator in a T87 Thermostat. So the recommendation was 1.2 which effectively disabled the anticipator resistor. I would set it for the current draw of your actual Gas Valve 0.23 Amps.
However if you have other control equipment between the Thermostat and the Gas Valve the actual current through the Thermostat really should be measured to be correct and accurate and not cause damage to the anticipator resistor.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Setting the anticipator by the current draw of the control system does not account for the difference in lag time in various methods of heating.
For steam heat with cast iron radiators you want a relatively long cycle. It needs to be long enough so that steam reaches all rooms before the burner shuts down. You may have to experiment a bit, but a higher amp draw setting giving less anticipation is probably what you need.—
Bburd0 -
-
But don't worry too much about "inefficiency". The BTUs are going into your house regardless.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Thank you for the responses. I appreciate it.0
-
@abcaldwell
One other note.
If you have an older Honeywell T87 thermostat which I believe you do.
You can get new thermostats that have choices for your heating system that you can select from, heat anticipators, showing in the directions.
There's a Honeywell 87 series that has this choice. I'm sure there are others.
Years ago it was ten wraps around an Amprobe with t-stat wire and doing the math.
1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements