Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

The case of Ray versus the A dimension

2»

Comments

  • ethicalpaul
    ethicalpaul Member Posts: 6,678
    We are in agreement, Jamie, isn't that cool?

    You are saying that a dry return open to atmosphere won't spew steam if the pressure is correct.

    I'm saying a dry return open to atmosphere if the pressure is correct will have no need of an A dimension.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • ethicalpaul
    ethicalpaul Member Posts: 6,678
    edited November 2023
    Gsmith said:

    same concept on the A dimension, might not be needed in most cases, but doesn't hurt or cost much as a "standard" way of designing/installing most systems.

    I am not saying don't have an A Dimension. It makes sense to have the main high and the wet return low.

    I'm saying that the concern about the water level rising at the A dimension is overblown, by a long shot. (for example, like the concern about getting the main venting above the main)

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Jamie Hall
    Jamie Hall Member Posts: 24,881
    Perhaps it is, as so often, a matter of using the same words to mean different things? However one wants to call it, though, the water will rise in a pipe connected to a wet return at one end and a dry return -- or open to the atmosphere -- at the other end 28 inches above the boiler water line for each psi gauge in the boiler... has to, to balance the steam pressure.

    It will rise very little, if at all, in a similar pipe, but connected to the steam main at the top end...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,502
    Don't forget we are talking here about a perfectly installed system installed and working the way it should.

    But:

    Traps fail and are neglected. There are probably more defective traps in use than there are working traps

    Pipe hangers fall off and wreck pitch

    oversized boiler are a common occurrence

    Radiation gets disconnected

    @ethicalpaul

    Think of a two-pipe system with steam traps from all the radiation and drips from the steam mains. Lets say they are dry returns and the boiler is operating at 1.5 psi.

    The traps are all working and have 1.5psi- (steam main pressure drop) at the trap inlet. The dry returns run back to the boiler and drops down into the boiler. There is a main vent on the dry return to vent the air so there is basically 0 pressure in the return main because it is vented

    The water in the return drop will rise up "stack" about 3' in that return drop to overcome the boiler pressure of 1.5 psi. Otherwise the water will not go into the boiler.

    To prove this raise the boiler pressure to 4 or 5 psi like my example posted above and watch what happens.

    The vent will close because it is waterlogged, the water will back up into the horizontal dry returns and hammer and bang when the traps cycle because traps are not perfect and pass a little steam. The radiators and traps will waterlog and gurgle and bang and they will have no heat.

    We have now turned a steam system into a noisy hot water system without a circulator
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,405
    How did I know this would go to 2 pages when Ray said "Dimension A"

    Will definitely go to 3 pages or even 4 if EthicalPaul has anything to say. And he usually does! LOL

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    ethicalpaul
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,502
    @EdTheHeaterMan

    We could start some other popular discussions such as "what pipe dope should I use", or "does my Nest need a C wire". or the one that always lights up the board "dry returns" versus "steam main extensions"

    We can save those for when things slow down
    ethicalpaulEdTheHeaterMan
  • ethicalpaul
    ethicalpaul Member Posts: 6,678
    Thanks @EBEBRATT-Ed I’d love to try it but I have one too few pipes! But thank you for sharing the scenario, it helps me understand 

    @EdTheHeaterMan I like the joke but it takes two to tango…I don’t reply to myself 😂

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    EdTheHeaterMan
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,405

    Thanks @EBEBRATT-Ed I’d love to try it but I have one too few pipes! But thank you for sharing the scenario, it helps me understand 

    @EdTheHeaterMan I like the joke but it takes two to tango…I don’t reply to myself 😂

    Oh hell... I always talk to myself, sometimes it is the only time I get to have an intelligent conversation.

    Otherwise it is like having a battle of wits with unarmed opponents

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    ethicalpaulEBEBRATT-Ed