Hot water heat system pump not running
blargendarg
Member Posts: 5
Hello all- I've done quite a bit of troubleshooting on this and just want to make certain I have my bases covered. Here's the scenario:
Standard Taco circulator pump doesn't run. I disconnected this and connected it directly to 120v and it runs fine.
Looking at the aquastat(L8148E 1257) there was obvious blackening on the board at the base of the relay, so I replaced it with one my father had in storage- it *looks* fine, but can't confirm it *is* with certainty.
Relay wasn't clicking over on the new one so I jumpered T to TV and the relay itself works(looks like I also need a new thermostat), I have 120v at Line but not anything at C1/C2. I wanted to test the thermostat wire, so I jumpered the ends upstairs- relay clicked over as soon as I gave it power again, but nothing from the pump. I read that the pump should cycle on with the boiler around 145F, but it makes it all the way to 180 and boiler turns off and nothing. Boiler and damper cycle just fine and so I'm still getting heat from passive circulation. It's just the one zone- no valves.
As far as I can tell, there must be something wrong with this aquastat as well. Is there anything I've missed here as to why the pump might not be running apart from that? I'm accustomed to this kind of stuff but these systems are complex- just want to be sure before I drop several hundred on a new part. Thanks for any guidance you can provide.
Standard Taco circulator pump doesn't run. I disconnected this and connected it directly to 120v and it runs fine.
Looking at the aquastat(L8148E 1257) there was obvious blackening on the board at the base of the relay, so I replaced it with one my father had in storage- it *looks* fine, but can't confirm it *is* with certainty.
Relay wasn't clicking over on the new one so I jumpered T to TV and the relay itself works(looks like I also need a new thermostat), I have 120v at Line but not anything at C1/C2. I wanted to test the thermostat wire, so I jumpered the ends upstairs- relay clicked over as soon as I gave it power again, but nothing from the pump. I read that the pump should cycle on with the boiler around 145F, but it makes it all the way to 180 and boiler turns off and nothing. Boiler and damper cycle just fine and so I'm still getting heat from passive circulation. It's just the one zone- no valves.
As far as I can tell, there must be something wrong with this aquastat as well. Is there anything I've missed here as to why the pump might not be running apart from that? I'm accustomed to this kind of stuff but these systems are complex- just want to be sure before I drop several hundred on a new part. Thanks for any guidance you can provide.
0
Comments
-
-
how's this? and yes, have & can use multimeter
0 -
Adding photo of connections for replacement thermostat, connected as the previous one was. Blue wire connected to R which connects to terminal TV in aquastat, White wire connected to W which connects to terminal T in aquastat and that's it. Red wire is not connected at either end. Can confirm this causes the relay to 'click over' with thermostat setting above ambient temp
0 -
It seems the basement bargain has issues . I like the roll of BX )
There was an error rendering this rich post.
0 -
Just in case the pump needs relocating, haha. Not my doing, but it aint broke- so there it stays!
Fair enough- it's unlike my pop have a perfectly good backup just sitting around so it kinda makes sense.0 -
When the relay clicks and you see it pull in is there 120v on the pump?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Good thought. I tested this several times both at the pump connection at the board and at the pump itself. There is often, not always, voltage there briefly. Generally anywhere from 1-20v for a fraction of a second before dropping back to 00
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements