You don't need no equalizer line & Hartford with our boiler
tim smith
Member Posts: 2,813
Comment from a scotch firetube mfr tech support. He referenced that that's old school thinking from the early 1900s when boilers were exploding. He commented that with all the redundant low waters & safeties etc that it is not needed on their boiler. I was questioning this as this boiler was installed by another company and not how I would have piped it. This is strictly pumped return with all returns coming back to feed tank.
Any comments ? I think there might be!
Tim
Any comments ? I think there might be!
Tim
0
Comments
-
Can we see photos of the install and/or the installation manual? He's probably right.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
-
I have seen a few scotch marine boiler in my day and it's true most of them do not have an equalizer or a Hartford loop, especially with a pumped return.0
-
A Hartford Loop is replaced by a check valve when a condensate return pump is used.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes2 -
I am not sure I have ever seen a Hartford Loop on a scotch marine boiler.0
-
Thanks guys it's not normally what we see here. Appreciate it.
Tim0 -
Here's one from Burnham that does show an equalizer with a pumped return. See Pg. #141
-
Even though the manufacturer says these are not needed, an inspector might still require them. Check with your local Code officials.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
-
I'm with The Steamer & Ed, maybe no H Loop, but an Eqaulizer is advised AND Most inspectors are looking for that...If nothing else, an equalizer allows natural flow and thermal turnover when the boiler is firing. All am advantage. You don't have to like it, but butting heads with the inspector is alot like arguing with the Cop that pulls you over: Big attitude = more tickets $$$. Mad Dog 🐕-1
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements