3 zone system, one zone doesn't turn on boiler
TJack303
Member Posts: 10
Hello,
For some background, I have a 3 zone hydronic heating system with a natural gas boiler. Each zone has a honeywell zone valve. 2 zones are in-floor heat, 1 for the basement and 1 for the garage. The 3rd zone, and the one that is causing issues, is upstairs and controls hydronic baseboard heaters.
When I turn up the thermostat upstairs the boiler doesn't turn on, I even bypassed the thermostat and spliced the 2 wires together. Still nothing. If one of the other 2 zones are on I will get heat upstairs, so the zone valve is working but for some reason it's not sending the signal to the boiler to fire up. I rewired the entire control circuit and still same issue. I even swapped the zone valve heads for the upstairs and the garage, thinking maybe it was a bad end switch, still same issue.
Any thoughts on what else I can try before calling a heating company to come take a look at it? I'm an electrician by trade so I thought I'd be able to figure it out but I'm stumped.
For some background, I have a 3 zone hydronic heating system with a natural gas boiler. Each zone has a honeywell zone valve. 2 zones are in-floor heat, 1 for the basement and 1 for the garage. The 3rd zone, and the one that is causing issues, is upstairs and controls hydronic baseboard heaters.
When I turn up the thermostat upstairs the boiler doesn't turn on, I even bypassed the thermostat and spliced the 2 wires together. Still nothing. If one of the other 2 zones are on I will get heat upstairs, so the zone valve is working but for some reason it's not sending the signal to the boiler to fire up. I rewired the entire control circuit and still same issue. I even swapped the zone valve heads for the upstairs and the garage, thinking maybe it was a bad end switch, still same issue.
Any thoughts on what else I can try before calling a heating company to come take a look at it? I'm an electrician by trade so I thought I'd be able to figure it out but I'm stumped.
0
Comments
-
Short the end switch wires and see if the boiler fires. I bet it won't. Find out where they are broken or fell out of a connection.0
-
mattmia2 said:Short the end switch wires and see if the boiler fires. I bet it won't. Find out where they are broken or fell out of a connection.0
-
I also did a continuity test on the thermostat wires to verify it was a complete circuit to the valve head and the wires are good.0
-
The motor and/or end switch on those valves wear out over time and fail to prove.
I would just replace the whole power head. https://www.supplyhouse.com/Honeywell-Home-40003916-026-Replacement-Head-for-V8043E-Zone-Valves"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Zman said:The motor and/or end switch on those valves wear out over time and fail to prove. I would just replace the whole power head. https://www.supplyhouse.com/Honeywell-Home-40003916-026-Replacement-Head-for-V8043E-Zone-Valves0
-
No. If swapping the valve heads doesn't fix the problem, they are not the problem. The problem is, as @mattmia2 said, somewhere in the wiring from the end switch to the boiler. Bad connection, broken wire... a variety of possibilities.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Jamie Hall said:No. If swapping the valve heads doesn't fix the problem, they are not the problem. The problem is, as @mattmia2 said, somewhere in the wiring from the end switch to the boiler. Bad connection, broken wire... a variety of possibilities.0
-
Its wired exactly like this, only with 3 zones instead of 5. Also the fact that I can jumper the end switch on the valve and the boiler fires up rules that out.
0 -
-
The valve is binding so the motor doesn't open all the way and close the end switch if switching actuators doesn't fix it but shorting the wires does. Try it with the actuator disconnected from the valve body.
EDIT: Or the valve isn't getting powered because of a problem in the thermostat circuit. Is the valve opening at all like @Alan (California Radiant) Forbes asked?0 -
Did you ever say that the zone valve opens when the thermostat calls for heat?
0 -
mattmia2 said:The valve is binding so the motor doesn't open all the way and close the end switch if switching actuators doesn't fix it but shorting the wires does. Try it with the actuator disconnected from the valve body.2
-
Honeywell makes a repair kit for the valve body- I believe the part number is 40003918-006. It's also a conversion kit for older models, and may be described that way.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements