Primary Loop - 1 1/4" vs 1"
A Laars Combi Boiler (MFTCW140) calls for 1 1/4" pipes on the primary loop. The manual reads:
CH pipe minimum size : 1 1/4 ̋
And the diagram shows:
The inlet and outlet on the unit are 1". And I'm planning on using 1" pipe on the secondary.
In a separate thread hot_rod wrote
I'd much prefer to use 1" pipe. Not just for the cost savings, but also because I could use a manual press tool instead of sweating. I'm a big believer in following a manufacturer's instructions. But, I'm a bigger believer in real world experience - of which I have none. Is the manual wrong and hot_rod right?hot_rod said:The 1-1/4 between boiler and hydro sep is overkill and the 1-1/4 sep is more $$
Dunno if it's relevant, but I'm running eight loops, each ≈250', to two zones. Is there some sort of calculation I should be doing to determine if 1" pipe on the primary is sufficient. I want hot_rod to be correct. Anyone else care to chime in?
Comments
-
I’m sure there’s a reason they call for 1 1/4” primary. My guess is to maintain minimum GPM through the heat exchanger.0
-
You’ve got a scenario which is not ideal: namely, your primary loop requires more flow than the total of your secondaries. A buffer tank is the best solution, but a hydro-sep will help.
A 1-1/4” line is good for about 14-16 gpm; a 1” is good for 8-10.
The connection size at the unit is not relevant to pipe sizing.
A 140k btu boiler needs a 1-1/4” line to maintain 14 gpm at a 20* delta T. However, your secondary is only gonna carry about 6 gpm if your loops are 1/2”.
Your boiler is more than twice the size needed for space heating because it’s sized for domestic output.
You could get by with 1” if you limit the firing rate for space heating to 80k or less.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.2 -
But if that were the case, would the inlet and outlet on the boiler itself also be 1 1/4"?pecmsg said:I’m sure there’s a reason they call for 1 1/4” primary. My guess is to maintain minimum GPM through the heat exchanger.
Boiler 1" <-> Primary 1 1/4" <--> Secondary 1"
To my layman's eye, that seems like you're restricting flow before and after the primary.
0 -
er0
-
Got it.Ironman said:The connection size at the unit is not relevant to pipe sizing.
Interesting…Ironman said:A 140k btu boiler needs a 1-1/4” line to maintain 14 gpm at a 20* delta T. However, your secondary is only gonna carry about 6 gpm if your loops are 1/2”. Your boiler is more than twice the size needed for space heating because it’s sized for domestic output. You could get by with 1” if you limit the firing rate for space heating to 80k or less.
I think I'd rarely go above 80K (never?) for space heating. Before I decided on a combi, I was looking at 80K boilers. Out of curiosity, would something catastrophic happen if I went, say, 100k on very cold day with 1" on the primary.
Given what you wrote, it seems better stick with 1" on primary to avoid the mismatch with the secondary.
0 -
How did you size this?0
-
That's a long story. Succinctly, consensus between a couple different HVAC pros. Supposedly, I need a boiler of around 54K BTUs (at most). Eighty was essentially the next size up, with turn down expected to keep it around what I need. Then I decided to go combi, so 140K.pecmsg said:How did you size this?
0 -
Required flow thru the boiler is based on the delta t also. The manual may show an example at different delta t
Many if the boilers allow you to downrate the firing rate for heating loads also. That fire tube boiler probably has a low flow requirement if you plan on locking it down to 80 k or soBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Do does that mean stick with manual specified 1 1/4" or take a chance on the 1"?hot_rod said:That fire tube boiler probably has a low flow requirement if you plan on locking it down to 80 k or so
0 -
It would not be the first time.MikeAmann said:To me, this sounds like you made a poor decision.
Isn't that the whole point of Combi unit with a 10:1 turndown ratio - to deal with the mismatch?MikeAmann said:I think your heat and hot water needs to be separate systems. You have a very large mismatch.
Somebody's taking a shower, 140K BTUs to the DHW. But most of the time, the unit is churning out 30K BTUs for CH. Am I not understanding correctly?
0 -
First, as I mentioned, you can run 1” if you limit the firing rate to 80k btus in space heating.
Second, the primary purpose of modulation is to match the firing as closely as possible to the actual load as outdoor temperature changes. It’s not to compensate for oversizing.
Your situation is the major drawback with a combi: in order to heat domestic instantaneously, the boiler is almost always oversized for space heating.
Unless it’s just recently been changed, the 140k btu model has a 5 to 1 turndown; the 199k is 10 to 1.
If you haven’t installed the boiler yet, I’d highly recommend that you go with a heating only boiler and an indirect tank. The combi may be cheaper up front, but it requires a lot more maintenance and service and has a shorter life expectancy.
Have you done a heat loss calculation?
Do you know what your domestic demand is?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.2 -
Good. Because I really want to use 1".Ironman said:First, as I mentioned, you can run 1” if you limit the firing rate to 80k btus in space heating.
You had me really worried. I've looked at so many boilers that I could have easily gotten confused. I double checked. Both are 10:1Ironman said:Unless it’s just recently been changed, the 140k btu model has a 5 to 1 turndown; the 199k is 10 to 1.
Sure. But in practice, potato/potatoh? As long as the boiler can turndown to adequately match the various heating loads and then fire up to match DHW draw I'm not seeing the conflict. At 10:1, that means 14K, 28K, 42K and 56K are my lowest settings. It seems highly unlikely that my domestic heating loads will fall outside that range.Ironman said:Second, the primary purpose of modulation is to match the firing as closely as possible to the actual load as outdoor temperature changes. It’s not to compensate for oversizing.
I have not installed the boiler. But when I first started researching, the math on a combi vs condensing + indirect didn't really work in the latter's favor. Off the top of my head, the heat-only condensing boiler plus indirect tank route was 1.75x more expensive. And it seems doubtful I'll get 1.75x more life out of it. But on your advice, I'll revisit.Ironman said:If you haven’t installed the boiler yet, I’d highly recommend that you go with a heating only boiler and an indirect tank. The combi may be cheaper up front, but it requires a lot more maintenance and service and has a shorter life expectancy.
I have. Twice. Once from a guy trying to sell me a boiler and another from a guy who was supposedly RESNET and BPI certified. They differed, so I split the difference.Ironman said:Have you done a heat loss calculation?
I do. The Laars 140 is more than sufficient.Ironman said:Do you know what your domestic demand is?
0 -
It’s not just life expectancy: the combi has a plate heat exchanger for the domestic; they scale up very quickly - especially with hard water. That requires descaling on regular basis. There’s a 3way diverter which switches between space and domestic heat. There’s also a modulating valve which tempers the domestic. Both of these have very high failure rates. Then there’s the repeated starting and stopping for domestic calls. It all takes its toll.
I’m in the field every day and see all this on a regular basis. We’ve reached the point where we don’t offer combi’s even if it means losing the job.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
I would just pipe it in 1 1/4 for the boiler loop. Sweating the small amount of fitting vs pro pressing them as far as time goes is negligible, and the fittings themselves are cheaper. More btus= more better in this case. Your secondary piping wants to pull as many btus as it needs at any given time anyway, might as well make it happy and remove problems down the road.Experienced Boiler Mechanic In Summit County, Colorado.0
-
I would install any/ all tankless with valves like these. It makes the delime process a quick easy task
The amount of scale build up is related to the hardness of your water, any idea of the hardness?
The indirect will see the same scaling, just spread over a larger surface so it is less noticeable. Minerals come out if the water when it is heated, regardless of the heater design
with good flow through a plate hx they do self scour, but low faucet gpm does them no goodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
This is like buying a hummer because a blazer is a little bumpy on dirt roads. Scale and hard water should be reduced before they even make it to the boiler. Space for parts is the main reason why you go with a combi and they 100% can be installed correctly requiring the same amount of maintenance a traditional Boiler/side arm does. I mainly install the later, but there are situations where a combi is absolutely the best option.Ironman said:It’s not just life expectancy: the combi has a plate heat exchanger for the domestic; they scale up very quickly - especially with hard water. That requires descaling on regular basis. There’s a 3way diverter which switches between space and domestic heat. There’s also a modulating valve which tempers the domestic. Both of these have very high failure rates. Then there’s the repeated starting and stopping for domestic calls. It all takes its toll.
I’m in the field every day and see all this on a regular basis. We’ve reached the point where we don’t offer combi’s even if it means losing the job.Experienced Boiler Mechanic In Summit County, Colorado.0 -
Could you elaborate on this? I just don't see any situation where I'll need more BTUs than a 1" primary can provide. I get that Laars specs the primary at 1 1/4" in case CH demand really is 140K, but that's definitely not my use case.SummitMechanic said:Your secondary piping wants to pull as many btus as it needs at any given time anyway, might as well make it happy and remove problems down the road.
So far we have SummitMechanic and the Laars manual on the 1 1/4" side.SummitMechanic said:I would just pipe it in 1 1/4 for the boiler loop.
Ironman and hot_rod on the 1" side.
1 -
My only elaboration is that 1: it will not hurt anything and 2: If for some unknown reason Laars has to get involved at some point for warranty reasons it could be a sticking point for them.SteamtoHotWater said:
Could you elaborate on this? I just don't see any situation where I'll need more BTUs than a 1" primary can provide. I get that Laars specs the primary at 1 1/4" in case CH demand really is 140K, but that's definitely not my use case.SummitMechanic said:Your secondary piping wants to pull as many btus as it needs at any given time anyway, might as well make it happy and remove problems down the road.
I guess i can also add the that the time/cost dynamic for 1" pro press and 1" 1/4 sweat might even land on the side of sweat for such a small section of your piping. Boiler efficiency and gas cost to heat the piping will not increase running costs with a 1" secondary piping because the amount of btu's carried vs the amount being produced will balance themselves out by the boilers actual fire rate.
And on an opinion basis, i would rather have my boiler loop make a bit more than i need instead of making the exact amount or in worse case scenario, less then i need.
The other upside would be the added available BTU's for additions to the central heat at some point or addition of snowmelt down the line. I would rather overbuild for a slight cost increase than save a bit of time and money for a headache down the road.
Experienced Boiler Mechanic In Summit County, Colorado.0 -
The way I'm reading what Ironman wrote, a 1 1/4", instead of a 1", primary actually could cause a problem. Am I misunderstanding?SummitMechanic said:My only elaboration is that 1: it will not hurt anything
Ironman said:You’ve got a scenario which is not ideal: namely, your primary loop requires more flow than the total of your secondaries.
A 1-1/4” line is good for about 14-16 gpm; a 1” is good for 8-10.
A 140k btu boiler needs a 1-1/4” line to maintain 14 gpm at a 20* delta T. However, your secondary is only gonna carry about 6 gpm if your loops are 1/2”.
This is a very fair point.SummitMechanic said:and 2: If for some unknown reason Laars has to get involved at some point for warranty reasons it could be a sticking point for them.
0 -
The SEP will negate any of the oversizing that @Ironman is referring to. Also a pipe that is larger than the minimum required has rarely been a problem in this industry. Just because you CAN pump 14 GPM thru a 1-1/4" pipe, does not mean that you WILL pump 14 GPM thru that pipe. A 1-1/4" pipe can allow less than 1 GPM flow with no problem. Ask anyone that has designed a gravity hot water boiler system.... Oops, they are probably all dead by now.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
SteamtoHotWater said:
The way I'm reading what Ironman wrote, a 1 1/4", instead of a 1", primary actually could cause a problem. Am I misunderstanding?SummitMechanic said:My only elaboration is that 1: it will not hurt anything
Your primary is going to flow based off of its own pump. The secondary is going to pull off of that a percentage of the btus depending on pipe size and pump flow rate. The boiler loop will maintain its set heat point and the secondary will pill off of that accordingly. Primary Flow rate will not effect secondary flow rate. Especially if it is piped 1 size larger as the primary piping will have the least amount of resistance and that is where the water is going to want to go anyway.Ironman said:You’ve got a scenario which is not ideal: namely, your primary loop requires more flow than the total of your secondaries.
A 1-1/4” line is good for about 14-16 gpm; a 1” is good for 8-10.
A 140k btu boiler needs a 1-1/4” line to maintain 14 gpm at a 20* delta T. However, your secondary is only gonna carry about 6 gpm if your loops are 1/2”.Experienced Boiler Mechanic In Summit County, Colorado.0 -
Got it.EdTheHeaterMan said:The SEP will negate any of the oversizing that @Ironman is referring to. Also a pipe that is larger than the minimum required has rarely been a problem in this industry. Just because you CAN pump 14 GPM thru a 1-1/4" pipe, does not mean that you WILL pump 14 GPM thru that pipe.
To be clear, you would favor the installing the 1 1/4" over the 1"?
0 -
I would use 1-1/4 to be sure on warranty issues.SteamtoHotWater said:
Got it.EdTheHeaterMan said:The SEP will negate any of the oversizing that @Ironman is referring to. Also a pipe that is larger than the minimum required has rarely been a problem in this industry. Just because you CAN pump 14 GPM thru a 1-1/4" pipe, does not mean that you WILL pump 14 GPM thru that pipe.
To be clear, you would favor the installing the 1 1/4" over the 1"?
I would use 1" in my own home because I know it will work.
So the score is 2.5 to 1-1/4" and 2.5 to 1"Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Well that makes my decision really easy ; )EdTheHeaterMan said:So the score is 2.5 to 1-1/4" and 2.5 to 1"
0 -
you could also size the boiler pump so it cannot flow more than 10 gpm. Either with a pump selection or adding a balance valve
Ill bet the boiler has a way to lock it in to a max modulation rate, most do now It basically limits the fan inducer to a not to exceed rpm
so lower flow and lower fire rate, protects the hx
yet in dhw the boiler can still high fire to provide maximum domestic production
Any number if ways to make this a safe installation
Or the additional $$ to go 1-1/4Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements