Possible e x v not opening
Snowmelt
Member Posts: 1,454
I have a Fijitsu unit with 4 heads , every day for like 6 hours, usually when sun is strong on the condenser the air isn’t working. Let me explain …….
I have 2 - 1 ton air handlers and a 7,000 btu air handler……. Every day in afternoon the rooms get to 72 although I have the remotes set at 68.
When it was 72 last it in house ad it was 78 outside the remote was set to 68 there was no sweating on 3 of the 4 line sets outside. To throw a monkey wrench in the mix, the insulation on the line set rotted away, I’ll put some insulation on Monday or Tuesday.
The questions are can the EXV valves fail, or do you think the line set not being covered for 12 inches give the pressure some odd reading where they’re not opening?
Well, yes EXVs can fail; and no, a foot of missing insulation isn't going to noticable effect operation. However, there should be one EXV per port on the condenser. The odds of them all having synchronized individual failures is …not probable. More diagnostics are needed. I might start with a manifold on the service teats during the transition from a working period to a non-working period.
Are any error codes displayed/blinked?
1 -
No codes on indoor unit, outdoor I didn’t take cover off. Only possible leak is threw the copper ……..
the tricky thing was it was on all day, it was fine till 4 pm temp was 68 in house. At 10 pm it climbed up to 72. I went outside to see if unit was frozen. Three lines were outdoor temp no frost or sweat. I felt the lines for 5 minutes I swear I heard the fan ramp at different speeds, I went inside 1/2 hour later it was comming out cooler and within three hours the whole house was do2n to 680 -
It's low on refrigerant. Repair the leak(s).
And you said 4 heads but only mentioned 2- 12's and a 7.0 -
K I’ll check for leaks again. The 4th unit is a 9,000 btu ceiling cassette , which is operating fine0
Thanks Pec , I do have a statement , also asking for your thought. The 4th head is a ceiling mount which has no ducts . I just called my wife she’s home right now . She told me she gave the unit a rest for 2 hours , it reached 75 in the house . The one room which is a ceiling cassette (no ducts) cooled the room to 70 degrees in 2 hours. Which in just blowing my mind. Now my attic is very hot. I’m thinking the little bit of duct work is not insulated enough , I’m going to have to get a temp at the inside coil also, I thik0
No sweating on which lines, specifically?
If there's four heads that's 8 lines. On a minisplit all 8 of those lines should be cold if the heads are running, four of them extremely cold as they're coming out from the EXV's, no?
If both lines going to a specific head aren't sweating, I'd say there's a big issue there and it's not the lack of insulation.
Thanks all, I’m on top of it , I’ll let you know all what happens0
- 129 Chimneys & Flues
