Fujitsu Evaporator Freezing when turned off
I don't use the one upstairs at this point.
When I turn on the lower one and it's running for about a day or so, the upstairs one freezes up and drips all over the floor. I've tried to get some pros out to take a look at it but no so easy where I live here on Cape Cod.
I explain the situation to them and they all say the same thing: It most likely needs refrigerant because units can freeze without enough refrigerant. I then question that logic based on the fact the upstairs unit is freezing but it's turned off so do they still think it's a refrigerant issue. Not much said at that point and I don't hear back from them again.
I would imagine there's a valve involved at the condenser side that is allowing refrigerant to flow to the unit that's off and that's somehow contributing.
Any and all feedback appreciated. Just trying to get looking in the right location to find the source of the problem.
Comments
-
Oh, and if there's anyone on the Cape or nearby that could be recommended, I'd rather have a pro look at it.0
-
-
-
Seems like to me , two wires power the inside unit and the third is the communication to the condenser . Maybe it was wired wrong from the factory if not wired wrong on your part . Seems like the control wire terminals are switched . I would be calling tech support to verified . Mistakes are made
There was an error rendering this rich post.
0 -
Yes, just set it to cooling to 85°or something, just to see what happens
I had a multi-split (4 heads) freeze up when the heads were wired one port off. (wired to A, B, C; & piped to B, C, & D) It just so happened that one of the heads had a small load & didn't need to run often, but the others basically ran all the time.
0 -
Raise the upper and see if the lower gets cold , then you will know....
There was an error rendering this rich post.
0 -
Is there maybe some minimum flow thing that opens that zone too when only 2 zones are calling?0
-
Generally multi split outdoor units have a minimum operating range, and that minimum changes depending on the number, size, and type (ducted, ductless etc) of indoor units connected. This is not always clearly stated in the machines spec sheet, they will usually show the rated minimum which is the lowest possible that the unit can run at, based on the minimum connected units.mattmia2 said:Is there maybe some minimum flow thing that opens that zone too when only 2 zones are calling?
LG has engineering manuals for their multi head units, and design software, that when used properly can identify these issues before installation. The issue I see is that almost nobody uses these tools, they just see the minimum on the spec sheet and base the design off of this number.
If needed the ODU will force indoor units that are not calling to do something to dump the extra load
1 -
I meant one zone calling, but you got the idea.0
-
-
Multi head systems, when sized and matched correctly can absolutely operate with just one head running. Refrigerant will flow through the other heads even if they're off, but the coils shouldn't freeze. Agree with @pecmsg. One of those 3.
Do you know if the total line set length exceeds the factory charge, and of so, was X oz. added per ft.?0 -
I appreciate all of the feedback. Managed to come down with Covid a second time but I will try and get out and look at some of the suggestions including electrical lines issue and minimum heads running in a multi zone unit.0
-
You could also check if the 4-way reversing valve is working.
0 -
Got out to the workshop where both systems are off. Set upstairs to high temp downstairs to low
Upstairs
Initial temp 79
Set Temp: 80
4 hours later: 66
Temp of evaporator air measure with Fluke IR 52
Downstairs
Initial temp 74
Set Temp 66
4 hours later: 72
Temp of evaporator air measure with Fluke IR 74
Sounds like the control wires are crossed maybe?
As simple as just flipping them at the condenser connections and see what happens?
0 -
Where's the installing contractor?cheftim_2 said:Got out to the workshop where both systems are off. Set upstairs to high temp downstairs to low
Upstairs
Initial temp 79
Set Temp: 80
4 hours later: 66
Temp of evaporator air measure with Fluke IR 52
Downstairs
Initial temp 74
Set Temp 66
4 hours later: 72
Temp of evaporator air measure with Fluke IR 74
Sounds like the control wires are crossed maybe?
As simple as just flipping them at the condenser connections and see what happens?0 -
That's another story
There was an error rendering this rich post.
0 -
Your outdoor unit has electronic thermal expansion valves to meter how much refrigerant each room unit gets. Seems like it is not shutting off flow to the upstairs unit. That could be a wiring mistake or a EEV problem.
0 -
rsilvers said:Your outdoor unit has electronic thermal expansion valves to meter how much refrigerant each room unit gets. Seems like it is not shutting off flow to the upstairs unit. That could be a wiring mistake or a EEV problem.1
-
Maybe a trouble code is being generated. Or maybe it is wired wrong. Mostly I was saying that I do think this unit can control the flow of refrigerant to each head unit and that the flow doesn't normally go through units not calling for cold.pecmsg said:
If that was the case a trouble code would be generated!
0 -
I'm going to retrace the wiring this morning to further check my assumption the controller wiring is wrong. The system hasn't really worked correctly since the installer, yours truly, installed it a few years back. I'm not in the workshop a lot and when I am it's not for long periods of time and will often turn on upper and lower heads.
Seeing the heads go to the set point of the other remote feels like it's the controller wiring. I'll report back. And as usual, thank you to all of you for taking the time to respond.0 -
It certainly seems like the wiring is crossed. That's why they make ohm meters.0
-
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements