Can this blower motor be fixed?
Comments
-
If you look at your 3rd picture you posted, you can see a wheel balancing weight.
It looks like a push on "Pal Nut". Don't move it, that is how little weight difference can throw a wheel out of balance. If out of balance it will wear out the motor bearings...existing or new. So your repair has to end up with a balanced wheel.
Your plan sounds like what my FIL used to do on the farm during the 1930's depression. When everyone had more time than money.0 -
mattmia2 said:I'm not seeing hundreds of watts in difference between motors but the way motors are rated is a bit dubious, it is sort of like we have these parts we use for many motors, let's test them under this very specific condition and publish a rating that doesn't reflect the real world conditions.0
-
Check to see if there are any rebates available for changing to ECM. In Michigan we had them for at least a few years and while it was not a ton it definitely offset the cost difference if you were changing one out anyway0
-
-
-
The payback period is not that hard to calculate. The savings per year is:
((hours_per_day*watts)/1000)*dollars_per-kwh*365
For me, the motor is used for heat and AC. Let's say 5 hours a day average. For a 3/4 HP, about 250 watts savings. My cost per KwH is about 0.45.
That is $205 a year savings but the motor only costs $100 more. So for $100 more, it saves about $2000 over 10 years. That is an easy decision.
Let's say I am wrong and it only runs 2 hours a day. Then it is $82 a year savings. It will still pay for itself in the first 1.5 seasons and turn a profit after that.
0 -
-
Does the new motor take the same frame?
Does a wiring harness and a relay board come with?
I see it's an R22 system. What brand and how old is the condenser?0 -
I've heard this argument and I've seen it countered with another.SuperTech said:One thing you might want to consider is how ECM motors are more prone to issues with restrictive ductwork and high static pressure. Has anyone else measured total external static pressure of your system?
The ECM motor only does what it's designed to do. If they overheat or die early from doing exactly what they're designed / programmed to do, that's pretty sad and it's a badly designed part.
Whether or not the rumors are true I have no idea. There's plenty of badly designed parts out there.
@rsilvers You forgot to add that you're paying more to remove the extra heat from A/C that you paid to put there with the PSC motor. So it's actually costing even more than you calculated.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
I think it's actually the case that most systems have overly restrictive ductwork & are operating outside mfgrs specs, which would indicate that PSC motors are more forgiving or at least conservatively rated.ChrisJ said:
I've heard this argument and I've seen it countered with another.SuperTech said:One thing you might want to consider is how ECM motors are more prone to issues with restrictive ductwork and high static pressure. Has anyone else measured total external static pressure of your system?
The ECM motor only does what it's designed to do. If they overheat or die early from doing exactly what they're designed / programmed to do, that's pretty sad and it's a badly designed part.
Whether or not the rumors are true I have no idea. There's plenty of badly designed parts out there.
@rsilvers You forgot to add that you're paying more to remove the extra heat from A/C that you paid to put there with the PSC motor. So it's actually costing even more than you calculated.That fits with other observations made regarding newer, high efficiency, products.
0 -
High static kills ECM motors.ChrisJ said:
I've heard this argument and I've seen it countered with another.SuperTech said:One thing you might want to consider is how ECM motors are more prone to issues with restrictive ductwork and high static pressure. Has anyone else measured total external static pressure of your system?
The ECM motor only does what it's designed to do. If they overheat or die early from doing exactly what they're designed / programmed to do, that's pretty sad and it's a badly designed part.
Whether or not the rumors are true I have no idea. There's plenty of badly designed parts out there.
@rsilvers You forgot to add that you're paying more to remove the extra heat from A/C that you paid to put there with the PSC motor. So it's actually costing even more than you calculated.1 -
ratio said:
I think it's actually the case that most systems have overly restrictive ductwork & are operating outside mfgrs specs, which would indicate that PSC motors are more forgiving or at least conservatively rated.ChrisJ said:
I've heard this argument and I've seen it countered with another.SuperTech said:One thing you might want to consider is how ECM motors are more prone to issues with restrictive ductwork and high static pressure. Has anyone else measured total external static pressure of your system?
The ECM motor only does what it's designed to do. If they overheat or die early from doing exactly what they're designed / programmed to do, that's pretty sad and it's a badly designed part.
Whether or not the rumors are true I have no idea. There's plenty of badly designed parts out there.
@rsilvers You forgot to add that you're paying more to remove the extra heat from A/C that you paid to put there with the PSC motor. So it's actually costing even more than you calculated.That fits with other observations made regarding newer, high efficiency, products.
How can a motor which is designed to control it self possibly work outside of it's specifications?
There's literally a motor controller. It should be impossible to cause it to operate outside of it's specifications. If it somehow is running outside of it's ability, it's literally because it's own controller is forcing it to which seems absurd, doesn't it?
As far as I know, ESC stands for Electronic Speed Control. So, the motor is being controlled, it's not some erratic behavior. If high static kills them, it's a bad design.
A PSC cannot operate outside of it's specifications unless you physically stall it. If you restrict either side of a centrifugal blower it causes less load on the motor. This is why you hear it speed up.
If high static really does kill ESC blowers (and it very well might), we need to be complaining about it.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
ECM, not ESC.0
-
Yes the motor has a 5.6" mount. The same.HVACNUT said:Does the new motor take the same frame?
Does a wiring harness and a relay board come with?
I see it's an R22 system. What brand and how old is the condenser?
RHEEM from 2005. Which is weird as the air handler is from 1999. Not sure why they would have changed the condenser after 6 years.0 -
You're right. That's a oops on my part.rsilvers said:ECM, not ESC.
It's electronically commutated motor in this case but it still uses a special controller and does exactly what the manufacturer programs it to do.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Excessive surging!ChrisJ said:ratio said:
I think it's actually the case that most systems have overly restrictive ductwork & are operating outside mfgrs specs, which would indicate that PSC motors are more forgiving or at least conservatively rated.ChrisJ said:
I've heard this argument and I've seen it countered with another.SuperTech said:One thing you might want to consider is how ECM motors are more prone to issues with restrictive ductwork and high static pressure. Has anyone else measured total external static pressure of your system?
The ECM motor only does what it's designed to do. If they overheat or die early from doing exactly what they're designed / programmed to do, that's pretty sad and it's a badly designed part.
Whether or not the rumors are true I have no idea. There's plenty of badly designed parts out there.
@rsilvers You forgot to add that you're paying more to remove the extra heat from A/C that you paid to put there with the PSC motor. So it's actually costing even more than you calculated.That fits with other observations made regarding newer, high efficiency, products.
How can a motor which is designed to control it self possibly work outside of it's specifications?
There's literally a motor controller. It should be impossible to cause it to operate outside of it's specifications. If it somehow is running outside of it's ability, it's literally because it's own controller is forcing it to which seems absurd, doesn't it?
As far as I know, ESC stands for Electronic Speed Control. So, the motor is being controlled, it's not some erratic behavior. If high static kills them, it's a bad design.
A PSC cannot operate outside of it's specifications unless you physically stall it. If you restrict either side of a centrifugal blower it causes less load on the motor. This is why you hear it speed up.
If high static really does kill ESC blowers (and it very well might), we need to be complaining about it.
Once the wheel cant overcome the static pressure it free spins for a sec than catches air again. the control notices this drop in amperage and tries and compensate than the as it grabs air the amperage increase and tries to compensate for that.
There's a listed range there designed for.0 -
0
-
So you're saying they can't make a motor who's electronics protect both the motor and the control from failing?pecmsg said:
Excessive surging!ChrisJ said:ratio said:
I think it's actually the case that most systems have overly restrictive ductwork & are operating outside mfgrs specs, which would indicate that PSC motors are more forgiving or at least conservatively rated.ChrisJ said:
I've heard this argument and I've seen it countered with another.SuperTech said:One thing you might want to consider is how ECM motors are more prone to issues with restrictive ductwork and high static pressure. Has anyone else measured total external static pressure of your system?
The ECM motor only does what it's designed to do. If they overheat or die early from doing exactly what they're designed / programmed to do, that's pretty sad and it's a badly designed part.
Whether or not the rumors are true I have no idea. There's plenty of badly designed parts out there.
@rsilvers You forgot to add that you're paying more to remove the extra heat from A/C that you paid to put there with the PSC motor. So it's actually costing even more than you calculated.That fits with other observations made regarding newer, high efficiency, products.
How can a motor which is designed to control it self possibly work outside of it's specifications?
There's literally a motor controller. It should be impossible to cause it to operate outside of it's specifications. If it somehow is running outside of it's ability, it's literally because it's own controller is forcing it to which seems absurd, doesn't it?
As far as I know, ESC stands for Electronic Speed Control. So, the motor is being controlled, it's not some erratic behavior. If high static kills them, it's a bad design.
A PSC cannot operate outside of it's specifications unless you physically stall it. If you restrict either side of a centrifugal blower it causes less load on the motor. This is why you hear it speed up.
If high static really does kill ESC blowers (and it very well might), we need to be complaining about it.
Once the wheel cant overcome the static pressure it free spins for a sec than catches air again. the control notices this drop in amperage and tries and compensate than the as it grabs air the amperage increase and tries to compensate for that.
There's a listed range there designed for.
I know you don't believe that.
I'm not saying they don't fail.
I'm saying it's unacceptable especially at the price they're sold for.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
I'm sure there has been a long line of designs that shut down for benign things and got destroyed in the field since it was first deployed in the 70's. There is a balance between protecting the equipment and nuisance shut downs along with all sorts of unexpected field conditions the needed to be worked out to get to something reliable. They also need management that is interested in fixing those problems.0
-
ChrisJ said:
So you're saying they can't make a motor whose electronics protect both the motor and the control from failing? I know you don't believe that. I'm not saying they don't fail. I'm saying it's unacceptable especially at the price they're sold for.
Excessive surging! Once the wheel cant overcome the static pressure it free spins for a sec than catches air again. the control notices this drop in amperage and tries and compensate than the as it grabs air the amperage increase and tries to compensate for that. There's a listed range there designed for.
How can a motor which is designed to control it self possibly work outside of it's specifications? There's literally a motor controller. It should be impossible to cause it to operate outside of it's specifications. If it somehow is running outside of it's ability, it's literally because it's own controller is forcing it to which seems absurd, doesn't it? As far as I know, ESC stands for Electronic Speed Control. So, the motor is being controlled, it's not some erratic behavior. If high static kills them, it's a bad design. A PSC cannot operate outside of it's specifications unless you physically stall it. If you restrict either side of a centrifugal blower it causes less load on the motor. This is why you hear it speed up. If high static really does kill ESC blowers (and it very well might), we need to be complaining about it.
I think it's actually the case that most systems have overly restrictive ductwork & are operating outside mfgrs specs, which would indicate that PSC motors are more forgiving or at least conservatively rated.One thing you might want to consider is how ECM motors are more prone to issues with restrictive ductwork and high static pressure. Has anyone else measured total external static pressure of your system?
I've heard this argument and I've seen it countered with another. The ECM motor only does what it's designed to do. If they overheat or die early from doing exactly what they're designed / programmed to do, that's pretty sad and it's a badly designed part. Whether or not the rumors are true I have no idea. There's plenty of badly designed parts out there. @rsilvers You forgot to add that you're paying more to remove the extra heat from A/C that you paid to put there with the PSC motor. So it's actually costing even more than you calculated.That fits with other observations made regarding newer, high efficiency, products.
do you want to pay for it?
do you want an heater that’s troublefree for 30’years? Breakout the check book0 -
pecmsg said:ChrisJ said:
So you're saying they can't make a motor whose electronics protect both the motor and the control from failing? I know you don't believe that. I'm not saying they don't fail. I'm saying it's unacceptable especially at the price they're sold for.
Excessive surging! Once the wheel cant overcome the static pressure it free spins for a sec than catches air again. the control notices this drop in amperage and tries and compensate than the as it grabs air the amperage increase and tries to compensate for that. There's a listed range there designed for.
How can a motor which is designed to control it self possibly work outside of it's specifications? There's literally a motor controller. It should be impossible to cause it to operate outside of it's specifications. If it somehow is running outside of it's ability, it's literally because it's own controller is forcing it to which seems absurd, doesn't it? As far as I know, ESC stands for Electronic Speed Control. So, the motor is being controlled, it's not some erratic behavior. If high static kills them, it's a bad design. A PSC cannot operate outside of it's specifications unless you physically stall it. If you restrict either side of a centrifugal blower it causes less load on the motor. This is why you hear it speed up. If high static really does kill ESC blowers (and it very well might), we need to be complaining about it.
I think it's actually the case that most systems have overly restrictive ductwork & are operating outside mfgrs specs, which would indicate that PSC motors are more forgiving or at least conservatively rated.One thing you might want to consider is how ECM motors are more prone to issues with restrictive ductwork and high static pressure. Has anyone else measured total external static pressure of your system?
I've heard this argument and I've seen it countered with another. The ECM motor only does what it's designed to do. If they overheat or die early from doing exactly what they're designed / programmed to do, that's pretty sad and it's a badly designed part. Whether or not the rumors are true I have no idea. There's plenty of badly designed parts out there. @rsilvers You forgot to add that you're paying more to remove the extra heat from A/C that you paid to put there with the PSC motor. So it's actually costing even more than you calculated.That fits with other observations made regarding newer, high efficiency, products.
do you want to pay for it?
do you want an heater that’s troublefree for 30’years? Breakout the check bookSingle pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Can this quoted reply get any longer?ChrisJ said:
Sure they canpecmsg said:ChrisJ said:
So you're saying they can't make a motor whose electronics protect both the motor and the control from failing?pecmsg said:
Excessive surging!ChrisJ said:ratio said:
I think it's actually the case that most systems have overly restrictive ductwork & are operating outside mfgrs specs, which would indicate that PSC motors are more forgiving or at least conservatively rated.ChrisJ said:
I've heard this argument and I've seen it countered with another.SuperTech said:One thing you might want to consider is how ECM motors are more prone to issues with restrictive ductwork and high static pressure. Has anyone else measured total external static pressure of your system?
The ECM motor only does what it's designed to do. If they overheat or die early from doing exactly what they're designed / programmed to do, that's pretty sad and it's a badly designed part.
Whether or not the rumors are true I have no idea. There's plenty of badly designed parts out there.
@rsilvers You forgot to add that you're paying more to remove the extra heat from A/C that you paid to put there with the PSC motor. So it's actually costing even more than you calculated.That fits with other observations made regarding newer, high efficiency, products.
How can a motor which is designed to control it self possibly work outside of it's specifications?
There's literally a motor controller. It should be impossible to cause it to operate outside of it's specifications. If it somehow is running outside of it's ability, it's literally because it's own controller is forcing it to which seems absurd, doesn't it?
As far as I know, ESC stands for Electronic Speed Control. So, the motor is being controlled, it's not some erratic behavior. If high static kills them, it's a bad design.
A PSC cannot operate outside of it's specifications unless you physically stall it. If you restrict either side of a centrifugal blower it causes less load on the motor. This is why you hear it speed up.
If high static really does kill ESC blowers (and it very well might), we need to be complaining about it.
Once the wheel cant overcome the static pressure it free spins for a sec than catches air again. the control notices this drop in amperage and tries and compensate than the as it grabs air the amperage increase and tries to compensate for that.
There's a listed range there designed for.
I know you don't believe that.
I'm not saying they don't fail.
I'm saying it's unacceptable especially at the price they're sold for.
do you want to pay for it?
do you want an heater that’s troublefree for 30’years? Breakout the check book
It would seem no?0 -
-
I have the parts now to fix it but holding off because the $1200 per ton rebate for a heat pump is tempting. Exploring those options.0
-
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements