R to g
johnjohn89
Member Posts: 114
Guys what should u reading voltage between r to g during the heating mode? 28v or ov? Some unit I work on when during the heating mode I do get voltage readings between r and g, other I don’t , but I do believe that g get power by other , doesn’t power same time
0
Comments
-
-
-
There's so many different ways to wire the fan for heat mode. Some will use G, and some won't.
A PSC motor could get direct line volt power from an aquastat, or an internal time delay relay.
A variable speed could get voltage on W1 and start the fan. Voltage at W2 will increase fan speed.
The wiring you see where G is powered for fan in heat mode is usually done at the thermostat. There will be a "gas/electric" switch, or it will ask during installer setup "equipment or thermostat controls fan in heat mode".1 -
ratio said:Depends on how the control board is built. Some may back feed the G terminal when the limit turns the fan on, some may not.pecmsg said:If a switch is closed you get 0 voltage
if a switch is open you get voltage0 -
HVACNUT said:There's so many different ways to wire the fan for heat mode. Some will use G, and some won't.
A PSC motor could get direct line volt power from an aquastat, or an internal time delay relay.
A variable speed could get voltage on W1 and start the fan. Voltage at W2 will increase fan speed.
The wiring you see where G is powered for fan in heat mode is usually done at the thermostat. There will be a "gas/electric" switch, or it will ask during installer setup "equipment or thermostat controls fan in heat mode".0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements