Steam boiler of off, losing water

dra
dra Member Posts: 2
edited July 2023 in Strictly Steam

my steam boiler is power off , pilot still on , i see no leaks , but the water level still drops in glass tube every few days a little , where is water goin,?

Comments

  • pecmsg
    pecmsg Member Posts: 5,294
    Return line underground?
    mattmia2
  • Jamie Hall
    Jamie Hall Member Posts: 24,857
    Any number of places. Is the water level still above the Hartford Loop? If so, wet returns are likely candidates. If not... hmm... check that boiler very carefully. It may be that the pilot light is generating just enough heat to conceal a small leak in the boiler...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    exqheat
  • dra
    dra Member Posts: 2
    no , return line is above ground
  • Jamie Hall
    Jamie Hall Member Posts: 24,857
    dra said:

    no , return line is above ground

    Above ground doesn't mean it can't leak. Is it below the boiler water line? Then it can...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • HVACNUT
    HVACNUT Member Posts: 6,332
    Is it auto feed? Is it getting low enough where it's adding water?  
    Like Jamie said, especially if it has a flue damper, the block could get warm enough to at least contribute to evaporation with a crack above the water line.

    Start it up and watch for white smoke out of the chimney. It's not an ironclad diagnosis but it's a start.
    exqheat
  • BobC
    BobC Member Posts: 5,502
    Lay some newspaper under the edge of the boiler and any return lines that are near the floor. that should find any slow leaks .

    If it doesn't find any I'd start to think it's linking into the firebox or directly onto the gas tubes of an atmospheric boiler. I would then sut the piulot off and lay newspaper under the burner tubes to see if you pick up a leak.
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
    exqheat