The case of the disappearing water treatment chemicals, this Friday's case
What would cause this? As usual, I will answer this on Friday at 6am EST
Boiler Lessons
Comments
-
Wild guess: The wye filter is dirty/restricted. The boiler calls for makeup water, diluting the oxygen scavenger in it. But I am too ignorant to even guess why his treatment usage would have risen. Except maybe the treatment pump was wired up to activate when the LWCO called for water.
But it would seem they would have noticed the condensate tank overfilling...but maybe it had an overfill drain that wasn't easy to monitor.
It took longer to brew because the boiler was having to heat up a lot more cold water than it should have had to.
Very nice drawing by the wayNJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
Boiler leaking above the water line was my thought as well.0
-
But the chemical levels in the boiler were reported as low...JUGHNE said:Hole in boiler, losing steam up chimney, auto feeder for make up water, in boiler feeder pump tank, activated which activates chem pump.
More fresh cold water, slower steam, ....more chemicals with each water addition.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
The oxygen combines with the scavenger and reduces the level. My guess is the test tests for the active scavenger, not the combined scavenger and oxygen.ethicalpaul said:
But the chemical levels in the boiler were reported as low...JUGHNE said:Hole in boiler, losing steam up chimney, auto feeder for make up water, in boiler feeder pump tank, activated which activates chem pump.
More fresh cold water, slower steam, ....more chemicals with each water addition.1 -
Thanks! What a cool topic!!
https://www.watertechnologies.com/products/boiler-water/steam-condensate-treatmentNJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
My guess: steam trap failed shut so boiler is running strictly on makeup (which may be tied in with chemical pump). Constant makeup would lead to less efficient brewing due to lack of preheated water. As for boiler tripping on low water, guessing a clog in the FW pump strainer.Look forward to answer! This was fun..0
-
@mattmia2 You got it right. The customer had removed the vacuum breaker on the kettle and when the steam condensed, it pulled the piping into a vacuum. When the valve for the kettle opened, the steam zoomed out of the boiler at a high velocity taking water with it. The air in the system consumed the oxygen scavenger so the maintenance tech would add more chemical treatment. The other parts of the treatment would not be consumed as quickly and appear as solids in the water. The high solids caused bouncing water and made the carryover worse.
https://youtube.com/watch?v=tok7cZytYTsRay Wohlfarth
Boiler Lessons0 -
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements