Mitsubishi Heat Pump question
Currently working on a MXZ-8C48NAHZ hyper heat untit attached to 2 branch boxes with 7 heads ranging in size from 6k to 18k.
When turning a 6k head on for heating, it takes roughly 20 minutes for the head to start producing any noticible heat and for the fan on the indoor unit to start ramping up. The outdoor unit is the same with a slow ramp up of the fan speed.
I've found that the indoor unit in heating mode will not ramp up the fan until the coil gets hot enough to blow warm air however I though that the outdoor unit would initially work harder to meet demand and then ramp down.
Anyone have any ideas or thoughts?
Thanks,
Gary
Comments
-
It's a 'feature' to keep the IDF off until the coil is warmed up. It may be adjustable, but that'd be a call to tech support. Dunno about the slow to ramp up, 20 minutes seems a little excessive.<p><p>FWIW, Mitsubishi tech support has been very helpful, AFAIK they'll talk to anyone, homeowner or otherwise.
0 -
the fan should be on within minutes.
How old is this system?
What service has been performed.
0 -
The system is coming up on 3 years old. There have been quite a large number of calls on this system since it was installed. The latest call was to run a new lineset to an 18k unit that previously had a 3/8" instead of a 1/2" and move it from the 3 port branch to the 5 port using the 1/2" port.
After the move, the addressing on the branches boxes wasn't updated and comm failures everywhere. Tech comes out and updates the addressing on the 5 to reflect the additional unit connected but didn't update the address ranges on the box. So they had to come back and try again, they attempted something from the outside unit instead of the branch boxes with no luck (obviously). So they came back a 3rd time and brought a tech from Peirce Phelps, he fixed the address range issues but at the end of the visit after observing the extremely long ramp up time said it appeared to be working correctly.
So on a system that was previously heating that room in 5-7 minutes it now takes 20 to even start moving the temp and another 20+ for the indoor fan to ramp up to full speed.
Something changed and I'm guessing it was the inexperienced techs at the outdoor box.
2 things that I found that could cause this issue,
- System thinks that its running on DC current.
- System is running in silent mode (special operations page from the install manual)
0 -
get a more qualified tech.
-1 -
No, the fan comes on when it's nice and warm
0 -
I remember the first time I had to address these dips on a Branch Box system, I wasn't thrilled at all. The Japanese to English isn't very good. The rep walked me through it. If too much time passes, i need to look at my notes. But normally I can set the dips with basic memory.
0 -
that coil should be above room temperature within a minute. 2 at the most. Now it might be slow but still moving air.
0 -
no—-have you worked on (residential) larger multi-zone units? From a dead start, 5 minutes seems normal. I've agonized even longer on some jobs. The computers do their thing at their own pace. IF other zones are already firing, then yes, a minute or two
0 -
gary7770 just one unit is slow, or all of them? if just one, need to check the dc signals. If allof them, you have some real issues.
0 -
I've done a few and admit never really timed it. Energize heat and a few minutes the fans running.
0 -
Good Luck ,
There was an error rendering this rich post.
0 -
right on, the big Double Fan units are kinda slow. But 20 minutes, something is wrong
0 -
if the original installers ran 3/8 to an 18k head, i can only imagine what other installation errors that there are. i wonder if they split the lineset correctly to each branch box?
0 -
I'll check some other units today.
Its been an adventure for sure, adventure of the nightmare kind.
Thanks,
Gary
0 -
Tested a second unit (9k) on the other branch box and still slow heating. The indoor fan didn't ramp up until roughly the 24 minute mark
Thanks,
Gary
0 -
I'd be afraid to know if they added the correct refrigerant levels. With these branch box systems, you really do need to read. There are so many variables, impossible to arm-chair-opinionate this type of thing. I agree, they "ran a 3/8 to an 18000", that's a little scary
1 -
So, last changes that were made were running the 1/2 line to the 18k unit, moving it to the other branch box and then re-addressing the branch boxes.
For the outside unit, it says that SW2-2 is the Connection Information Clear Switch that you flip with the power off when "When relocating units or connecting additional units." which is basically what was done. I'm assuming that information gets stored in non-volitile memory and thats the necessity for that switch.
So my question is, after flipping that switch how long should I power up the system for before shutting it down and putting the switch back to the default position?
Thanks,
Gary0 -
Re: "I'd be afraid to know if they added the correct refrigerant levels"
This system ran for close to 3 years with the wrong charge. After the initial install, they came back no less than 3 times to add more not knowing that they needed to calculate the correct charge which was ultimately a total of 22.65 as reported by the Diamond System builder software that they needed someone at Peirce Phelps to run for them.
Thanks,
Gary0 -
you might want to contact a different Diamond dealer to review the entire install.
0 -
When i make an error in the settings, then correct the settings, there is not any 'killing the power and waiting". I turn the system on, and that's it. Yes, it may take a few extra minutes for the computer to think about things, but no 'shut it off and wait"
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements