Steam heat hammer
Cgl73
Member Posts: 2
in Gas Heating
Looking for some help on a hammer issue happening at the end of the cycle ONLY, about 5-10 seconds after boiler shuts down. It seems like it’s coming from right around the Hartford loop area. A close nipple for the Hartford loop was not used on the installation of this boiler. Instead there is about a 8-10 inch nipple. I believe this is the issue but wanted to get more opinion before pulling apart and redoing. Would like to repair with confidence that nothing else is the issue. Ty for any and all help
1
No guarantees with a hammer -- but it could well be that Hartford loop -- or it could also be that horizontal in the equalizer line. Or both. Depends a lot on exactly where the operating water level is.Br. Jamie, osb
The water level is def within 2 inches of water line. BUT, waterline could be dropping below that near end of cycle. Does that help at all for further opinion? Thank you0
I don't LIKE the Bushes down equalizer nor the extra long Hartford loop. Change both mad Dog1
That almost looks like 3/4" in to Bushing then to 1" and then to either 1.25" or 1.5 "
Also you should make those low copper elbows, tees w boiler drains fir flushing mX1 -
Those bushings in the black iron will trap water in that ell. either use a reducing ell or reduce it in the vertical.0
If your installer did not get some thing as simply as piping the equilizer and hartford correctly then I would assume the rest of the piping is crap also . I hope they will return for a second attempt to get it right but I would not put to much faith in that . Usually one who can not get it right the first time is clueless . Any one who knows what they are doing would never make a simple mistake as that clearly a novice at steam boiler installation . Personally I would second guess anything they did if they could not get that right . I mean it’s in the manual so it not just made up crap .
I lose faith very easy when I see things that are so basic that it makes sure you wonder ,what the heck peace and good luck clammyR.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
As said, there are at least 2 things wrong in that picture. If you desire a full evaluation post a picture or two from further back so we can see all the piping.
What size is that boiler? The piping varies depending on boiler size. Looks like one of the bigger ones in that series, but do need to verify.0