Eco pump using too much electricity.

kathya70
Member Posts: 1
in Gas Heating
New 20-18 Ecocirc pump triples energy use of b&g series 100 pump is this normal? I just replaced my circulating pump for my small single family residence. On top of the energy usage which I can track on my Enphase system, my radiator whistles when the pump is on, I’m guessing that means the pressure is too high. Any help would be appreciated.
0
Comments
-
How did you choose the new pump? Pumps vary widely in the relationship between the flow they create and the pressures they create it at -- you can't just swap one in for another one, even if they physically fit. It does sound as though you have much more flow and pressure than you did before -- and than you probably need.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
The ECO is a maximum 70W, the series 100 was
at least 210W, depending on the motor size.
What setting do you have the ECO running on? Is it a zone pump, or supplying zone valves.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements