Expansion tank and back flow preventer on an indirect water heater
Rickoo
Member Posts: 54
Hello!
I'm replacing my Peerless boiler tankless coil water heater with an HTP Superstor Ultra 45. My home has no back flow prevention in the water service line. No pressure reducing valve. Just a water meter with ball valves on either side.
The boiler has appropriate back prevention. I'm wondering if I should install an expansion tank and back flow prevention in the domestic cold water line to the indirect. Pretty sure its not required in my situation, but I'm wondering if its a good idea anyway?
Is a simple swing check valve appropriate here?
https://www.supplyhouse.com/Bluefin-SCS075-3-4-Solder-Ends-Swing-Check-Valve-Lead-Free
Any reason why I wouldn't want the expansion tank and back flow prevention?
Thanks!
I'm replacing my Peerless boiler tankless coil water heater with an HTP Superstor Ultra 45. My home has no back flow prevention in the water service line. No pressure reducing valve. Just a water meter with ball valves on either side.
The boiler has appropriate back prevention. I'm wondering if I should install an expansion tank and back flow prevention in the domestic cold water line to the indirect. Pretty sure its not required in my situation, but I'm wondering if its a good idea anyway?
Is a simple swing check valve appropriate here?
https://www.supplyhouse.com/Bluefin-SCS075-3-4-Solder-Ends-Swing-Check-Valve-Lead-Free
Any reason why I wouldn't want the expansion tank and back flow prevention?
Thanks!
0
Comments
-
-
Install a back flow protection on the water heater or the incoming water line?0
-
Hi, @Rickoo , I don't see what benefit you would get from making this change. You would have a bit more complexity and things to fail. Simple is good.
Yours, Larry2 -
Did you read my post? The boiler HAS A PROPER back flow preventer in its water supply line. I'm talking about the domestic water supply to the indirect.0
-
-
Thanks Larry!
My understanding the reason expansion tanks are installed in water heater domestic cold water supply is to prevent expansion of hot water from the water heater from possibly causing the water heater relief valve to drip. Or possibly causing damage to fixtures or appliances due to increased pressure. If the house has a check valve in the main water feed (like in a pressure reducing valve) I believe they are required. I don't have that and the expanded pressure from the tank will generally be absorbed back into the municipal feed line coming into the house.
At least that's the way I understand it. Does this make sense?1 -
This is what I'm speaking about....
0 -
I wouldn't bother installing anything that isn't necessary. If you are not experiencing any problems, do not add anything.
If you like, look into what a closed domestic water supply is as apposed to a open system.
You can find this information by down loading the direction on a "domestic cold water expansion tank."
As to your boilers "appropriate" back flow prevention. If you truly do have the proper device installed then you should be covered.
The swing check you showed in your first post is not appropriate in any area that I have worked.
A appropriate "BFP" would be a RPZ-----Reduced pressure zone device.
This type of BFP is considered a high hazard device installed on boilers and is required by most plumbing/heating codes as well as most department of public health agencies.0 -
Hi @Rickoo , We're on the same page. Because you don't have anything in the supply line that prevents backflow, thermal expansion cannot raise water pressure. You can make sure of this by putting a pressure gauge on any hose bibb, or water heater drain valve and see if pressure increases at all when the tank is being heated. I like the gauge that has a red indicator that shows the highest pressure reached. That way to don't have to stare at the gauge for a long time
Yours, Larry0 -
Thanks. This is a new install of an indirect on an existing boiler. I haven't plumbed it yet and was debating the installation of an expansion tank. The link to the swing check valve I posted wasn't intended to prevent contamination in any way. The boiler feed has a Watts 9D-M3. The swing check was to prevent hot water from migrating back into the cold.0
-
Are you on a public water supply? If so there may be a BFD on the meter or elsewhere
if you are on a private well, no need for a BFD
public water suppliers do not want water back after it has entered your property, that is the reason for the BFD requirementsBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I'm on public water. Just a water meter between the utility and my home. Is it possible for a water meter itself to incorporate back flow prevention? I've never heard of that?
Maybe I'll skip the expansion tank and see if I have issues with thermal expansion. If so, I'll put it in then.
Just trying to do the right thing here.0 -
All the plumbing codes require BFDs of different types. If you have a water meter in a pit outside, it could have a BFD in the yoke.
Hose bibs need BFDs to protect your homes water. Kitchen faucets with spray hoses have protection also, as should any lawn sprinkler system.
So some are intended to protect your plumbing regardless of the city connection. The BFD in or at the meter protects the rest of the water users.
Backflows of various listings are also required on boiler connections to potable water.
Check with your water provider for a clear answer. Many cities require BFD and yearly inspection, as their insurance carriers get involved also.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements