Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Speaking of safe chimneys...

JohnNY
JohnNY Member Posts: 3,285
Is this good? A 400,000 BTU boiler vents into this.
Very hard to capture between two buildings but it's a single wall flue run on the exterior of the building. Flue gases condense immediately and pour out the bottom at every cycle. It's also got huge holes in it from base to cap, through which most of the flue gases escape before they reach the top of the run. The guy won't change it because "My carbon dioxide detectors never go off".

I can't. I just can't.




Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes
Wahergmcinnes

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,183
    You do hit some winners, don't you!
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Canucker
  • Steamhead
    Steamhead Member Posts: 17,238
    Run, don't walk! If you haven't already, that is. This job will be nothing but trouble.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    mattmia2
  • Steamhead
    Steamhead Member Posts: 17,238
    JohnNY said:

    Steamhead said:

    Run, don't walk! If you haven't already, that is. This job will be nothing but trouble.

    You've lost your sense of adventure, Steamhead.
    If they won't spend the money to do the job right, I'm not getting involved. Lawyers are way too expensive.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    Hap_Hazzard
  • JimP
    JimP Member Posts: 90
    That looks like a single wall pipe. Do you think it would
  • JimP
    JimP Member Posts: 90
    Do you think it would work better if it was D Vent?
  • mattmia2
    mattmia2 Member Posts: 10,443
    I'm sure there is both a building official and a utility that would be more than happy to shut that down until it is fixed.
  • ChrisJ
    ChrisJ Member Posts: 16,146
    I swear I've seen you post this before and I said "Looks good from my house!".

    Am I losing my mind?
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • JohnNY
    JohnNY Member Posts: 3,285
    ChrisJ said:

    I swear I've seen you post this before and I said "Looks good from my house!".

    Am I losing my mind?

    You're correct!

    I told this client last year that we weren't going to work on the boiler anymore until he had a functional chimney installed. I can't put my guys in the mechanical room with this boiler running. It's below ground and has no active ventilation. I went back in there this week because he asked me to check his Heat-Timer settings. No change was made to the flue.

    @mattmia2 That's always a tough call, isn't it. Do I want to advise the client and take them at their word that they'll take corrective measures or do I want to jam them up mercilessly with the NYC Dept of Buildings? It's a case-by-case thing. This guy will fix this but first I have to jump up and down. Keep in mind this is a West Village 4-story townhouse.
    Here's a clip from the Zillow listing:

    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
    ChrisJPC7060
  • KC_Jones
    KC_Jones Member Posts: 5,769
    Wait...hold on...I need to clarify.

    What's in the picture is on a house that's estimated to be worth over 7 million dollars?
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • RayWohlfarth
    RayWohlfarth Member Posts: 1,619
    wow that's really scary
    Ray Wohlfarth
    Boiler Lessons
  • ChrisJ
    ChrisJ Member Posts: 16,146
    I assumed it was the back of an industrial building
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • ScottSecor
    ScottSecor Member Posts: 878
    @JohnNY we have some similar customers, thankfully not too many. Amazing what they will and won't spend money on.

    I find it odd that they think nothing of dropping big money on that antique couch that no one will ever sit on, or that high end kitchen that gets used a few times a year. But when it comes to that old (essential) heating system in the basement/dungeon, as long as it heats the space - leave it alone!
    Mad Dog_2
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,247
    Only in New York will a guy live in squalid conditions but drive a $180,000 car.
    GGrossMad Dog_2NYtimebomb
  • mattmia2
    mattmia2 Member Posts: 10,443

    Only in New York will a guy live in squalid conditions but drive a $180,000 car.

    Because the squalid conditions still cost more than the car.
    Long Beach EdEdTheHeaterManMad Dog_2NYtimebomb
  • KC_Jones
    KC_Jones Member Posts: 5,769

    Got to love this one. Customer is having work done on his house. Nothing to do with me. In the course of conversation he mentioned that they had extended the roof up. Turns out the contractor had raised the roof about two feet and now the top of chimney was actually inside the structure. I was there to get the boiler up and running. I told him no way no how. Chimney terminates inside the house. He told me he would have the contractor extend. They sent me this picture of the extension. Still no way and still no how. Wild stuff out there.

    So they had no inspections obviously. The homeowner may need to contact and attorney, I'd also be contacting the local AHJ to see what they have to say.

    That's absolutely insane.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    WaherMad Dog_2
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,247
    edited February 2023
    Nice new chimney, but where's the Karnak flashing cement?
    gmcinnesMad Dog_2
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,247
    edited February 2023
    @JohnNY That's what Karnak is for. Patch those holes. Good for the sand holes in those Chinese gas fittings too!
    And do somethin' about that leak in the bottom. A drain in that bucket maybe.


    Mad Dog_2
  • mattmia2
    mattmia2 Member Posts: 10,443

    Nice new chimney, but where's the Karnak flashing cement?

    is that the new york equivalent of dewitt's?
    Long Beach EdMad Dog_2
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 8,676
    The summer home I lived in for years (Flat Roof) needed a new roof and the Contractor (my brother-in-law) sold my father a new asphalt shingle pitched roof that created a 12 foot high attic space. Soon after construction was completed the insulators were in the attic getting sick. That is the week my brother-in-law learned that you can't vent oil burner fumes into a work space. But he is a well respected builder in the community. Of course I was tasked with the vacuum cleaning on the oil boiler the following weekend. We had an indirect for DHW.

    The house is no longer standing, But I still have the 8"x8"x 12' stainless steel chimney extension in the back yard that my brother-in-law came up with to resolve the problem.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    gmcinnesMad Dog_2
  • HVACNUT
    HVACNUT Member Posts: 6,081
    If the chimney is the pig, then the black paint must be the lipstick. 
    Also the crimps on the vertical pipe are pointing down. I guess it's to be expected. 
    JohnNYMad Dog_2
  • Bob Harper
    Bob Harper Member Posts: 1,071
    Ask him if his CO alarms ever alert. You can't fix stupid. An NDA is not slavery. You still have an obligation to mankind. I'd send certified letters return receipt to him, the gas utility, building department and fire marshal. Let him sue. He'll get cremated in court. He's endangering anyone who enters that building, attached neighbors and anyone who might have cause to stand outside. The IRC states these concerned people include building officials who enter to inspect, cops, fire, EMS, the plumber, etc. He is knowingly endangering you. You probably have legal recourse against him. He's a public hazard. I would do all this then walk away.
    Mad Dog_2
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,247
    edited February 2023

    Ask him if his CO alarms ever alert. You can't fix stupid. An NDA is not slavery. You still have an obligation to mankind. I'd send certified letters return receipt to him, the gas utility, building department and fire marshal. Let him sue. He'll get cremated in court. He's endangering anyone who enters that building, attached neighbors and anyone who might have cause to stand outside. The IRC states these concerned people include building officials who enter to inspect, cops, fire, EMS, the plumber, etc. He is knowingly endangering you. You probably have legal recourse against him. He's a public hazard. I would do all this then walk away.

    You'd do this to anyone with an unlined chimney?
    JohnNYCLambrealliveplumber
  • HVACNUT
    HVACNUT Member Posts: 6,081
    You'd do this to anyone with an unlined chimney?
    I didn't see that part. For this specific chimney I think @Bob Harper makes some valid points. The owner should be embarrassed with himself. 
    Mad Dog_2
  • Bob Harper
    Bob Harper Member Posts: 1,071
    There is no justification for an unlined chimney in use. An owner's options are to line it or decomission it. Period. No amount of mumbo-jumbo from a mfr, code inspector, etc. can soften or remove that burden. The case in point has been reported with active venting failure. This is a direct hazard to people. Therefore, there is a burden to alert the authorities since the owner has clearly indicated his indifference to the welfare of others. This move protects the public as well as the contractor. Also, the contractor should not touch the system, not attempt to service it but walk away. To work on it implies consent and approval.
    Now, what about an unlined chimney you encounter? Is it a hazard to the public? Yes. Is it a hazard specifically identified in the code that must be corrected? Yes. Is it a liability to any contractor who works on it or any attached equipment? Yes. Is it an impediment to the sale or transfer of the property? Yes.
    Someone please explain the justification for not relining a chimney that has been deemed unsafe by the evidence uncovered during an NFPA 211 level II inspection. Bueler?

    If the flue is undersized to where a properly sized liner cannot be installed into the chimney then that chimney cannot be used for the intended equipment. Contractors stuff anything they want into chimneys and try to will it up the stack. No. When you approach a chimney vented installation, your first question should be, "can this chimney adequately exhaust and contain the flue gases?" If unlined or the liner has failed, can you get the proper sized liner in? If not, either reduce the input rate/ size of equipment, or use alternatives such as power venting.

    If a customer balks at these measures, you should clearly state the hazard, the consequences for failure to mitigate or correct and the sequelae for those issues. For instance: a chimney is unlined. You state an unlined chimney does not comply with code and is, therefore, a hazard that must be corrected. Failure to correct it may result in venting failure, carbon monoxide exposure, respiratory irritants and aerosols being inhaled, erosion and destruction of the chimney, weak draft, poor combustion and reduced efficiency. These can result in death, health issues, fire, chimney collapse, collateral building damage and increased costs to operate.

    Unfortunately, that is the level you must notify someone of hazards or else it could be construed as a 'failure to warn'. This is the hottest legal concept in tort law because it plays on sentiment and not just empirical facts. You knew there was a hazard yet neglected to inform the owner in writing. You become the bad guy. When you find an unlined flue, I would give a complete written warning having them sign and date receipt of a copy. If they refuse to sign, they get a certified letter return receipt. If I observe blatantly hazardous conditions, such as my personal CO alarm alerting yet they blow it off, certified letter. If they thank me and ask for a quote, no certified letter. If I give them a quote and the express their derision and scoff at the hazard, certified letters to everyone.

    You do what you want. I do consulting in such cases. I provided litigation support to a major mfr. for years working daily with corporate attorneys, insurance companies, fire investigators, code officials, etc. I also sit on the NFPA 211 cmte. and the UL Standards Technical Panels 103 for venting and 127 for hearth appliances so I'm familiar with the code process. I suggest these strong measures not to be a hard-****. I suggest them based upon actual cases. We teach this extensively in the hearth industry. We have whole courses on how to diagnose and document conditions, report writing, and solutions. Maybe some Wet Heads should consider delving into it a little more.
    barnumandbaileyCorktown
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,247
    Thank you, Bob Harper for sharing this. Your experience and insight is valued here.
    Larry Weingarten
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,406
    When in doubt...lock em out. If there is ANY chance people will die, I will do the right thing for all humans. I'd never forgive myself if I didn't. Its a black and white issue to me when it comes to Life Safety. Good catch Johnny.   Mad Dog 
    Bob Harper
  • BobC
    BobC Member Posts: 5,491
    Sometimes the ones with the most money squeak the loudest.

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • ChrisJ
    ChrisJ Member Posts: 16,146
    edited February 2023
    Mad Dog_2 said:
    When in doubt...lock em out. If there is ANY chance people will die, I will do the right thing for all humans. I'd never forgive myself if I didn't. Its a black and white issue to me when it comes to Life Safety. Good catch Johnny.   Mad Dog 
    I have to admit judging by the quality of work I've seen from many contractors, including in my own house I have a problem with this.

    Is it wrong in the situation being discussed?  Probably not but I can see it being wrong in many situations.  It also comes across as "pay me or you suffer"


    I think how @JohnNY handled it was great.




    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    KC_JonesJohnNYLong Beach Ed