main vents on my steam boiler
mmc239
Member Posts: 81
Where do I install main vents on my steam boiler?
0
Comments
-
Not on or near the boiler, in one pipe steam systems. Main vents should be placed at or near the end of the steam mains.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Sometimes the end of the steam main is near the boiler
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
True. But in terms of the way the steam moves, it isn't... I can't tell from the photos if that system has that arrangement.ethicalpaul said:Sometimes the end of the steam main is near the boiler
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Is there a better angle I can take the pictures from?0
-
If you start at the boiler and follow each steam pipe to it's end.
If it simply goes up a radiator then that is not a main, just a run out.
If it goes to the end of the house and then turns and comes back to the boiler, that would be a steam main with a return going back to the boiler, usually dropping down to the floor and then into the boiler.
A vent should go after the last steam take off/run out. Could be right at the boiler up high as possible.
You should look for any fittings with plugs, these could have been steam main air vents.0 -
-
Does the lower smaller pipe run back to the boiler with no other connections?
If so it is most likely where a vent used to be and could have been moved to get the ceiling installed.
Show the other end of that pipe at the boiler, you might consider adding venting at that point.
Otherwise some ceiling surgery is needed.
Floor to ceiling shot of the piping at the boiler please.0 -
Looks plausible anyway -- but you're going to have a clearance problem. The vent should go on top of that reducing T -- but ideally should be a few inches above it on a nipple. Don't think you have the clearance for that, not even sure you have enough clearance for any kind of vent... where does the small pipe underneath go?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Smaller pipe goes back into boiler room towards the boiler.0
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 420 Carbon Monoxide Awareness
- 80 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 891 Plumbing
- 5.9K Radiant Heating
- 378 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements