My Utica MAC 205 Boiler Sounds like the Horn of Gondor
That being said, ever since (or at least fairly close to that time) the boiler had been taken apart and put back together several times, it periodically sounds like the Horn of Gundor when the flame kicks on. Now, when I hear the word horn, I think air, but again, we cannot find any leaks. Also, it does not happen every time the boiler kicks on. It is bizarre. It does seem to happen frequently when the unit switches between heating domestic water and radiant floor water, but not every time and that is not the only time it happens. It also often happen when a new zone kicks on, but again, not every time. My best guess scenario at this point is that when cool water hits the hot resevoir, it is causing the unit to resonate, and it does also kind of sound like that as well, but that is only a guess.
No one seems to be able to give me a definitive answer on this and Utica won't talk to me because I am not an HVAC person. And, where I live, getting an HVAC person, or any other professional to show up at your house, is literally almost impossible.
So, I am at a loss. Do you think there is any relation between the disassembly and reassembly of the unit with the sound, or is that just a coincidence? Do you guys have any ideas or troubleshooting steps you think I should try? The manual does not say anything about this issue in the troubleshooting section. Any help you could provide would be awesome!
Comments
-
Since the undersized gas line was the first thing that should have been checked, not the last (gas pressure when firing), I don't have much confidence in the folks you are working with.
That said, how is the gas connected to the boiler? There have been a number of problems with boilers connected with flexible (CSST) gas lines which are similar to yours. I've not personally investigated them, but some kind of resonance between the change in gas flow and the line losses seems to cause a flame instability which sounds like a horn.
So -- how is yours connected?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Interesting. Mine is indeed hooked up with flexible line. I will provide pics when I get home. I also should add that, rather than running a new, larger line, to fix the undersized line issue, a 2lb regulator was put on the house. Then, right before the boiler, there is another regulator to kick the pressure down to where it should be per boiler spec. Again, I will provide pics when I get home.Jamie Hall said:Since the undersized gas line was the first thing that should have been checked, not the last (gas pressure when firing), I don't have much confidence in the folks you are working with.
That said, how is the gas connected to the boiler? There have been a number of problems with boilers connected with flexible (CSST) gas lines which are similar to yours. I've not personally investigated them, but some kind of resonance between the change in gas flow and the line losses seems to cause a flame instability which sounds like a horn.
So -- how is yours connected?0 -
I had a situation years ago where a Utica LP Gas boiler was in service for many years and this occurred. Not sure if it is the same model as yours. Nothing had changed about the home.
Checked the chimney, draft, room air supply, all good. The flame was burning within the tubes causing resonation.
After checking, the inlet pressure was too high, the Gas Provider replaced the regulator. Then set manifold pressure to spec., nothing changed.
Called Utica Tech support. Their answer was a superseded burner tube(s) for that boiler, which they sent. Replaced, set parameters to spec., still to no avail.
I left the company and did not find the answer.
Best to call Utica Tech support for help.0 -
The CSST is your issue.
https://forum.heatinghelp.com/discussion/164856/csst-the-cause-of-harmonic-fog-horn-noise#latest
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
So if I go with 1" CSST that would fix it? Otherwise, I would need to just go with black rigid pipe and that shoudl fix it?Ironman said:0 -
That is not encouraging lolKickstand55 said:I had a situation years ago where a Utica LP Gas boiler was in service for many years and this occurred. Not sure if it is the same model as yours. Nothing had changed about the home.
Checked the chimney, draft, room air supply, all good. The flame was burning within the tubes causing resonation.
After checking, the inlet pressure was too high, the Gas Provider replaced the regulator. Then set manifold pressure to spec., nothing changed.
Called Utica Tech support. Their answer was a superseded burner tube(s) for that boiler, which they sent. Replaced, set parameters to spec., still to no avail.
I left the company and did not find the answer.
Best to call Utica Tech support for help.0 -
Prevch said:
The CSST is your issue.
So if I go with 1" CSST that would fix it? Otherwise, I would need to just go with black rigid pipe and that shoudl fix it?
https://forum.heatinghelp.com/discussion/164856/csst-the-cause-of-harmonic-fog-horn-noise#latest
Gas line sizing must be done according to code using approved charts and calculations for the specific application.
There’s no “one size fits all” method.
What I am trying to point out is that the CSST is the cause of the fog-horning.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
That is not encouraging lolKickstand55 said:I had a situation years ago where a Utica LP Gas boiler was in service for many years and this occurred. Not sure if it is the same model as yours. Nothing had changed about the home.
Checked the chimney, draft, room air supply, all good. The flame was burning within the tubes causing resonation.
After checking, the inlet pressure was too high, the Gas Provider replaced the regulator. Then set manifold pressure to spec., nothing changed.
Called Utica Tech support. Their answer was a superseded burner tube(s) for that boiler, which they sent. Replaced, set parameters to spec., still to no avail.
I left the company and did not find the answer.
Best to call Utica Tech support for help.
I can’t guarantee that because I don’t know the particulars of you house.Ironman said:
Gas line sizing must be done according to code using approved charts and calculations for the specific application.
There’s no “one size fits all” method.
What I am trying to point out is that the CSST is the cause of the fog-horning.
Got it. Thanks0 -
I’ve never dealt with a fog-horning situation where the CSST was on the supply side of the regulator, so I’m not sure if the harmonics will transfer through the regulator.
I have seen where it can happen when the regulator is too close to the appliance, like you have it.
It’s recommended to have at least 10’ of hard pipe between the regulator and the boiler or fog-horning can occur.
P.S.
I do remember a situation like yours from about 15 years ago where the gas contractor did the same thing and it fog-horned. I don’t think the owner ever made him correct it.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.2 -
@Prevch
This might not have anything to do with the horn of gondor (lmao) but the length of pipe from that second stage regulator to the boiler is most likely going to cause you issues in the future. I had 1 manufacturer tell me no less than 6 feet of 3/4" pipe (we were locking out on failed ignition) but In my experience we needed more, that was for a 155,000 BTU boiler. In addition to being able to deliver the proper amount of fuel, you also need to guarantee the initial volume of fuel at ignition to prove flame. It won't always be an issue, but if you start locking out on failed ignition, that would be the most likely reason in my opinion.
edit: I see @ironman already suggested this, pretty smart guy!0 -
@GGross @Ironman Interestingly, the Horn of Gondor started sounding long before that second regulator was put in. It started happening after we found the propane leak from the boiler being taken apart. The 2lb regular outside and regular you see in the pics above weren't installed until probably a year after that.
So, if it was you, what would you do? Bear in mind that calling a professional is pretty much not an option. Maybe I just run 1" black pipe from the 2lb regulator to the regulator inside and create some extra space between the inside regulator and the boiler?
Or perhaps I should try knocking the pressure down a 1 or 2? I can't remember off the top of my head, but I think my boiler is rated for 8-12, and it is currently at 12, so perhaps ease off to say 10?
Any other ideas?0 -
if, as you say calling a professional not an option then you'd best purchase a $1000 combustion analyzer and spend another grand on training, take a minimum of two years HVAC training so you can dial in the fuel/air mixture to stop this. CSST is not the only cause. sorry0
-
ch4man said:if, as you say calling a professional not an option then you'd best purchase a $1000 combustion analyzer and spend another grand on training, take a minimum of two years HVAC training so you can dial in the fuel/air mixture to stop this. CSST is not the only cause. sorry0
-
I would have someone come out and do a combustion test. Improper combustion will cause the foghorn noise your talking about. Happens when the gas pressure is to low in low fire after modulating down. Should always do a combustion test when adjusting gas pressures.0
-
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 97 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 929 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements